Discuss Smeg cooker tripping randomly in the UK Electrical Forum area at ElectriciansForums.net

Neilacker

DIY
Reaction score
0
Hi
Hope someone could help, I have a Smeg induction range cooker that randomly trips the switch to all the plug sockets in the house but never trips the switch the cooker is on, we have had an electrician check the wire from the cooker to the mains and all came back OK and a specialist smeg repair man look at it and no one can find fault.
It will randomly trip doesn't matter whether its the oven being used or just the induction hob, it could trip 3 times per hour then go days without problem a
The model number is tr93ix si 08.

Hope someone could help
Thanks
 
a Picture of the consumer unit (fuse board etc) would help us here.
 

Attachments

  • 20211011_175203.jpg
    188.3 KB · Views: 18
Any pattern in how much of the cooker you have turned on when it trips? Woulda thought 32a wouldn't be sufficient with all of it going at once but i've not whipped out the calculator so someone else will correct me if wrong.
 
Any pattern in how much of the cooker you have turned on when it trips? Woulda thought 32a wouldn't be sufficient with all of it going at once but i've not whipped out the calculator so someone else will correct me if wrong.
Hi
There's no pattern it could go days no problem and then a few times per hour sometimes even when not in use.
It got to the point that I made a chart for what was being used on the cooker and other electrical items even had a section for it was raining haha
Its connected to a 40a switch
Thanks
 
I'm assuming it's the RCD switch in the middle that is tripping.
It would be an interesting experiment, though no doubt inconvenient, to turn off the MCB's for the garage, upstairs and downstairs sockets, and the unlabelled one in between, to see if the cooker still trips it!

Is it a recently acquired Smeg range, or have you had it a while and its just started doing this?
 
I'm assuming it's the RCD switch in the middle that is tripping.
It would be an interesting experiment, though no doubt inconvenient, to turn off the MCB's for the garage, upstairs and downstairs sockets, and the unlabelled one in between, to see if the cooker still trips it!

Is it a recently acquired Smeg range, or have you had it a while and its just started doing this?
Yes its the RCD that trips, I've already tried with them all off and still tripped.
The unlabelled one is the cooker, the one saying cooker is to an outside socket
Thanks
 
Yes its the RCD that trips, I've already tried with them all off and still tripped.
The unlabelled one is the cooker, the one saying cooker is to an outside socket
Thanks
So when everything else on the RCD side is switched off at their MCB's, but the cooker MCB is on, the RCD still trips.
Taken at face value, that implies the problem is with the cooker.
One final test might be to repeat that experiment with the cooker isolator in the kitchen switched off (to check the tripping stops) though you say an electrician has already checked the cooker circuit.

The reason I asked if the cooker was new, is that sometimes if a new oven has been stored in a warehouse for a while, the heating element can absorb a little moisture and develop a leakage current that can trip an RCD. After it dries out the problem goes away. Probably not the issue here if you've already used the oven a bit.

Does the cooker ever trip the RCD when you are not using it at all, ie nothing working on either the hob or the oven?
 
Last edited:
So when everything else on the RCD side is switched off at their MCB's, but the cooker MCB is on, the RCD still trips.
Taken at face value, that implies the problem is with the cooker.
One final test might be to repeat that experiment with the cooker isolator in the kitchen switched off (to check the tripping stops) though you say an electrician has already checked the cooker circuit.

The reason I asked if the cooker was new, is that sometimes if a new oven has been stored in a warehouse for a while, the heating element can absorb a little moisture and develop a leakage current that can trip an RCD. After it dries out the problem goes away. Probably not the issue here if you've already used the oven a bit.

Does the cooker ever trip the RCD when you are not using it at all, ie nothing working on either the hob or the oven?
Yes thats correct everything else off and it still tripped, the cooker isolator switch was switched off each night so the electricity would still be on over night.
The problems started about a week after the warranty ran out so Smeg wouldn't look at it ?

Yes the cooker has tripped when not in use but isolator on
Thanks
 
Yes thats correct everything else off and it still tripped, the cooker isolator switch was switched off each night so the electricity would still be on over night.
The problems started about a week after the warranty ran out so Smeg wouldn't look at it ?

Yes the cooker has tripped when not in use but isolator on
Thanks
I think you should persist with Smeg - fitness for purpose/ merchantable quality and all that. Shouldn't be failing with a safety related fault so soon!
 
He put some sort of tester on it I remember him telling me the equipment he was using was more accurate than a multi meter
Thanks
Sounds good.

Coming from a French background i wonder if any of the experts in here (since i'm not one) think it's a reasonable suggestion that the AC RCD could be the problem? I've had a look at the cooker there doesn't seem to be much electronics on it so maybe this suggestion is bunk but i just noticed the AC RCD and it sprung to mind.
 

Reply to Smeg cooker tripping randomly in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm not an electrician. I clean cookers and today arrived to a rangemaster range cooker. Got started, and as part of my routine, I turn on ovens...
Replies
1
Views
807
I hope this is the correct thread. I have to replace the main oven selector switch in a Smeg A4-5 cooker. I can't find a proper service manual...
Replies
0
Views
480
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
820
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
580
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
729

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock