Discuss socket outlets in commerical premisis in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

zone77

-
Reaction score
0
what code would i give on PIR for skt oulets in commerical property with no rcd protection?
all skts Zs are under max values and only intended for staff:confused:
 
If they're under the supervision of a skilled or instructed person such as a handyman (not just anyone who happens to work there) then they're fine.
If not then they're just not to the current regs, code 4.
 
As long as they do not supply equipment outdoors. 411.3.3 (ii), there is no exception to this rule and it also appeared in the 16th ed a code 2 if this situation exists IMO.
 
No code unless they are used for mobile equipment outdoors, or intended for general use by ordinary persons
EAWR requires that workers meet the definitions of skilled or instructed persons when using socket-outlets for work.
 

Reply to socket outlets in commerical premisis in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
1K
Evening all, If a socket circuit is not RCD protected via an RCD/RCBO and there isn't the option of fitting an additional RCD enclosure or...
Replies
20
Views
6K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
707
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock