I have recently moved into a flat. One the single sockets shows LN reverse on the socket tester that I bought today Why could this be ?

I have checked the earth connection which is all good.
 
Thanks for your replies to my comment. I think I have found the problem! One of the double sockets in the living room the earth cable had fallen out.

I’ve attached a photo. Why would the earth cable go into a connector in the block and then into the back of the socket connector? Can I run the earth cable straight into the socket ?

E256DEF0-FD7C-440B-BE3B-9CC99DDA84AB.jpeg 3A2A06A5-9780-49FC-99EB-16DBE44668C3.png
 
It looks like one earth is connected to the socket and the other to the earthing terminal in the backbox. while this is not correct practice,when the socket is screwed back both earths will be joined, so I would doubt this is your issue. From your original post it would appear that the L and N are simply in the wrong terminals in the socket, have you checked that?
 
In all living room sockets the earth cable was out. I’ve put the earths back in but I’m getting the following voltage readings on one of the double sockets

between live and neutral 243volts

live and earth 141volts

neutral and earth 103 volts

all cables are in the correct connection slots on all sockets
 

Reply to Socket shows LN Reverse on socket tester in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Why my polarity tester is showing earth is leaking after replacing earth leakage which was tripping and there is no power in the sockets. Please help
Replies
0
Views
445
Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
706
Today I was doing an EICR and went around a couple sockets with a Megger MST220 socket tester just to see if there was anything obvious, all three...
Replies
20
Views
787
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
886
just had a new meter fitted,tells me most sockets are faulty and not to use,all sockets apart from two show live neutral reverse. going to egypt...
Replies
9
Views
960

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock