Discuss Solar iboost not working in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Reaction score
1
We have a solar iboost which was working fine then suddenly stopped. If you turn it off at the mains and then on again, it says low voltage and heats via solar initially with a high reading then this drops until zero and it states heating off. Amy ideas on what the problem could be? Thanks
 
Dear Mary12345: I cannot find a message which says 'low voltage' but I did find one 'Sender battery low'; perhaps this is what you meant. If it was 'Sender battery low' then you need to replace the two AA batteries in the sender; do not use rechargeable batteries - only use normal alkaline as you buy in the shops.

The sender is this device which connects via a lead to the clamp around a cable near the meter:

Solar iBoost+ Sender - Marlec - https://www.marlec.co.uk/product/solar-iboost-sender/
 
Dear Mary12345: I cannot find a message which says 'low voltage' but I did find one 'Sender battery low'; perhaps this is what you meant. If it was 'Sender battery low' then you need to replace the two AA batteries in the sender; do not use rechargeable batteries - only use normal alkaline as you buy in the shops.

The sender is this device which connects via a lead to the clamp around a cable near the meter:

Solar iBoost+ Sender - Marlec - https://www.marlec.co.uk/product/solar-iboost-sender/

We have changed the batteries in the sender and no difference. The light on the sender is flashing intermittently and the little Wi-fi signal is also flashing on the iboost itself. The low voltage message appears briefly as you switch the mains switch back on on the iboost, the. It is replaced with the version/model details briefly then goes to normal display and the blue light comes on and heats via solar initially at a level expected for the weather but this then slowly drops/decreases until the display reads heating off. You can then turn the iboost off again via the mains and on again and the whole process is repeated but obviously can’t do this all the time.....
 
Mary12345: Good morning Madam. To submit a query I need to know the following information:

1. Press display and please tell me the savings made today, yesterday, last seven days, last 28 days etc.

2. Is it the Iboost or Iboost plus?

3. Do you know when it was installed and by whom?

4. Do you have battery storage for your PV system?

5. Does the green light on the sender flash?

6. Does the radio symbol (top right) on the iBoost display flash? It looks like a Christmas tree with waves.

7. Are you still able to heat the water using the electric immersion element?

Thank you.

:)
 
Mary12345: Good morning Madam. To submit a query I need to know the following information:

1. Press display and please tell me the savings made today, yesterday, last seven days, last 28 days etc.

2. Is it the Iboost or Iboost plus?

3. Do you know when it was installed and by whom?

4. Do you have battery storage for your PV system?

5. Does the green light on the sender flash?

6. Does the radio symbol (top right) on the iBoost display flash? It looks like a Christmas tree with waves.

7. Are you still able to heat the water using the electric immersion element?

Thank you.

:)
1 - today 0; yesterday 0; last 7 0.36 (me turning it on and off otherwise would be 0); last 28 days 95.99; total 5198.00

2- iboost

3- can’t find any paperwork apart from the manual - think we had it installed just after the solar panels in 2016 ish

4- no

5- yes

6- yes

7- yes; kicks in when press boost, haven’t left on to see if heats water to full temperature over time as is expensive and we have an oil boiler to heat water

Thank you
 
I have submitted a query into Marlec the manufacturer. If I were to hazard a guess on what is wrong I think the iBoost's internal 'keep alive' battery is flat.
 
Mary12345: Eventually my telephone call to MARLEC went through to a recorded message: 'blah, blah, blah, covid, difficult time, blah, etcetera'. The advice in it is to do what I have done for you already - complete an on-line query and wait for a response. We will have to be patient.
 

Reply to Solar iboost not working in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a 6kw PV with a 6kw Growatt battery and invertor. I have a solar iboost going to the hotwater tank. Recently I had a Ohme Home Pro...
Replies
2
Views
2K
hi there, I have purchased a house with a Solar iBoost. Been working fine for 2 years, went on holiday and switched it off as it had a time...
Replies
10
Views
2K
4
Can someone tell me what the resistance should be for a Solar iboost Clamp? My clamp is regestering zero ohms and I want to confirm this is the...
Replies
0
Views
874
4Dave C
4
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
2K
Is it possible for all or at least most electricians to be trained up in the wiring of solar PV installations, particularly the iBoost or Eddy or...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock