Discuss Solar Panel Array to charge 24v batterys in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

D

Dougy

Solar panel details

Hello everyone
Im a new member to the forum, i have done a course on industrial electronics so im no expert on solar panel arrays etc,

Im thinking now of making up a solar panel array (off grid) to charge 24v batteries(2x12v) and use them with 24v to 240v true sine wave inverters for different ring main circuits around the house

I Have a 30amp solar charge controller with a load disconnect at 22.2v and load reconnect at 25.20v. float voltage at 27.2v
my Question now is i have solar panels with these specs below

Max power (Pmax) 245W

Max. power voltage (vpm) 29.75V

Max. current voltage (Ipm) 8.24A

open circuit voltage (Voc) 36.6V

Short circuit current (Isc) 8.90A

Max. system voltage 1000V

Max. fuse rating 14A

size 1637 x 992 x 50mm

if i used 3 of these panels in parallel (Max. power voltage(vpm) 29.75V giving a total of (Max. current voltage (Ipm) 24.72A would that be sufficient to charge the batteries or would 4 be better 32.96A on those not so sunny days

thx for you help everyone
 
Last edited by a moderator:
I am not an expert on this, but one will come along shortly, and there are some good one's on here.

But I will try and help a little, panels are tested under STC (standard test conditions) so on a cool day with clear sunshine (I can not wait for that) they can and do produce more than stated, also on a hot day they will produce less.

From the little I know on this subject 2x12v through an inverter will not power much at all, and certainly not for long.

There was a thread on here recenctly about this very thing, try doing a search using different "key words"

I hope this helps a little for now.
 
I am not an expert on this, but one will come along shortly, and there are some good one's on here.

But I will try and help a little, panels are tested under STC (standard test conditions) so on a cool day with clear sunshine (I can not wait for that) they can and do produce more than stated, also on a hot day they will produce less.

From the little I know on this subject 2x12v through an inverter will not power much at all, and certainly not for long.

There was a thread on here recenctly about this very thing, try doing a search using different "key words"

I hope this helps a little for now.

thx for your reply Earthstore i do understand that i will need a few more battery's i just need to work out the setup later for the circuits etc, i do have a 2500w invertor with 2 12v in series at 75amp each batteries, ive been running the house lights top and bottom circuits, all 11watt energy bulbs and a small 50W portable TV which i have been running not continually but for 2 days at present all still going well, il let you know when it gets dark lol.:cool4:
i will be getting more invertors and batteries for each different curcuit etc.

this is just in the early stages yet

its just the charging and setup side from the array im not 100% on
 
Last edited by a moderator:

Reply to Solar Panel Array to charge 24v batterys in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello, My current 2.5kW Solar pv array is in a less than favourable position, but there is plenty of space to expand the array. I have an...
Replies
2
Views
1K
Hi, So I'm replacing a small old off grid with a new 7.5kw off grid, & being poor seek best value for my mppt, after long searches I find this...
Replies
1
Views
676
Good morning all. Before I start I am not an electrician and am relatively new to this topic. Current set up Axpert 5.5 Kw inverter, 7 x 420...
Replies
4
Views
2K
Greetings, everyone, After dedicating over a month to researching Solar PV systems, I'm nearly ready to make a decision. I owe my progress to...
Replies
1
Views
943
I currently have solar array and was going to purchase Shelly EM to monitor Grid in/out and solar production. So far so good. But I also plan in...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock