Cool .. Thank you.

Could we do the entire system with the 2 CT's + controller and without using a microcontroller ? any comparator circuits using LM series ?
 
Cool .. Thank you.

Could we do the entire system with the 2 CT's + controller and without using a microcontroller ? any comparator circuits using LM series ?
not that I know of I think the only way to calculate real power and control the proportional controller is to use software.
 
ok. Are you using this setup to heat the water? Does the controller heats up during working ? Also, How do you fine tune it ?

Thanks for the great help
 
Hi,
This is a fine solution if you don't mind building it yourself as a commercial version is not yet available for several reasons:
1. Phase angle controls can generate EMC problems which would have to be filtered out at some cost;
2. A commercial controller would need to be tested for CE marking at some cost;
3. Getting a reliable source of mains power used is very difficult with modern installations, just measuring current will give false import and export readings as there is no sign from a standard CT, e.g. 8A generated and 5A on grid, could be export of 5A or import of 5A to meet 13A load.

TT.
 
I wouldn't buy the £168 + £8 p&p ebay one as there's a good chance it will be running your immersion heater off the grid. If you pay 3p/kW for gas and 15p/kW for electric then running this off the mains at a 1:5 ratio or for 10 mins per hour will negate any savings made. Anything more than 10 mins for hour of greater than 500W baseload at your property (kettles, TVs etc on-top of fridges/freezers) will start actually costing you money!

I'm amazed it's sold so many, especially as you could do the same by simply flicking the switch on your immersion heater when your solar meter is saying 1.5kW or greater. You'd probably be better off with a timer from Argos which you only turn on during peak hours and turn it off when the weather forecast is bad.

Anyways... I've been looking into this and you will need a 1kW immersion heater ideally rather than the 3kW most people have. I've looked into stepping a 3kW down to 1kW via 220 to 110V, but it's not cost-efficient.

I'm looking to make one of these for myself, which will automatically turn on the immersion heater when the solar is exporting 1kW or more. It will automatically turn off at below 1kW export, so will never take electricity from the grid. If anyone, would like me to try and make one for them, please PM me. I'll probably need some pics of your install (consumer unit, gen meter etc) and details of what exactly you want. My install is going to be quite simple but I don't mind making it a bit more complicated for your needs if I can.

Bear in mind... I will be doing this as a hobby not a business!!! So please be kind!!!
 
I wouldn't buy the £168 + £8 p&p ebay one as there's a good chance it will be running your immersion heater off the grid. If you pay 3p/kW for gas and 15p/kW for electric then running this off the mains at a 1:5 ratio or for 10 mins per hour will negate any savings made. Anything more than 10 mins for hour of greater than 500W baseload at your property (kettles, TVs etc on-top of fridges/freezers) will start actually costing you money!

I'm amazed it's sold so many, especially as you could do the same by simply flicking the switch on your immersion heater when your solar meter is saying 1.5kW or greater. You'd probably be better off with a timer from Argos which you only turn on during peak hours and turn it off when the weather forecast is bad.

Anyways... I've been looking into this and you will need a 1kW immersion heater ideally rather than the 3kW most people have. I've looked into stepping a 3kW down to 1kW via 220 to 110V, but it's not cost-efficient.

I'm looking to make one of these for myself, which will automatically turn on the immersion heater when the solar is exporting 1kW or more. It will automatically turn off at below 1kW export, so will never take electricity from the grid. If anyone, would like me to try and make one for them, please PM me. I'll probably need some pics of your install (consumer unit, gen meter etc) and details of what exactly you want. My install is going to be quite simple but I don't mind making it a bit more complicated for your needs if I can.

Bear in mind... I will be doing this as a hobby not a business!!! So please be kind!!!


you do not need a 1kw immersion heater you can still use your 3kw immersion with the correct solar controller.
my unit uses spare power right down to 400w so on a cloudy day it will still give you a tank of warm water. On a sunny day I get a tank of hot water. It is usable all through the winter.
using a 3kw immersion will still give you a tank of hot water with say 1.5kw spare power, it will just take longer to heat up.
 
Thanks for the replies guys. A site transformer would make it a lot easier but I'm going to have to do some calcs to see whether 700W immersion is going to be sufficient for different size PVs. A solar controller would be ideal but I'm not sure the cost will payback... more sums for me to do.

I'll spend some time on PVOutput and see what difference in benefit there is for each solution.

I'm hoping to have my own one up and running within a few weeks... will keep you all updated!
 
I have often wondered why people will spend so much time and money trying to come up with a system to heat their domestic hot water.
Firstly, let's try and work out how much we actually use; Washing machine, cold fill, dishwasher, cold fill, so what else do we use it for? Baths/showers and hand washing, and that is it.
A modern hot water cylinder will hold it's temperature for around 24hrs, so minimal losses there.
So what is the true cost in £'s to heat the hot water from conventional methods? Well due to the amount we use it has to be very little.
What if you have no spare PV, how would you heat your water from cold? Most would just switch on the immersion heater to heat it up quickly, as the kids need a bath before bedtime.
If it were used as a way to add some free heat to a heatstore, then I feel it may be worth it.
Just my thoughts.
 
I think the benefits will probably be small... between £50 and £100 per year for gas, bit more for economy 7, probably double or triple for electric / oil / lpg. Once I figure it all out I'll post what I think and hopefully people can correct my inevitable mistakes.

I've got gas, so will get the least payback, and I want to make the payback within a few years, so alot better than Solar PV itself. If energy prices rise then you are protected even more. I'm thinking if it warms up the water during the day, the gas boiler won't be needed, so for at least 3 months of the year I won't need to pay to heat the boiler up for showers, baths, washing up etc.

If everyone just made one for themselves then yes it would be alot of effort for little benefit, but I'm quite interested in getting different ones working, so for me it's a bit of fun too. I've got a kit-car, I could've bought it cheaper already made... but where's the fun in that?

Appreciate your thoughts... constructive criticism will stop me spending way too long on this or making mistakes so please keep them coming!

Thanks
 
Hi everyone

Seems this subject still has a long way to go.

I built my own automated Solar Dumper late last December 2011 using a 3.3kWA isolation transformer because I wanted to maximize the surplus solar from my new 3.76kWh PV system. I automatically switch between the 55 volt winding and the 110 volt winding to give 160W and 660W loads using a single 3kW immersion. However, because I also have a 3kW boost, I am able to switch through a combination of loads 160W, 320W, 660W, 820W and finally 1,320W all automatically using a £20.00 microprocessor called an Arduino andtwo Efergy current sensors and a hand full of relays.

Drawbacks of using a transformer are current inrush requiring a type C breaker and a thermistor with an additional relay. Also I have found if on all day it gets quite warm even with no load so I fitted a cooling fan too.

Total cost about £250.00 for all the electrics as I used quality components and £130.00 for the 3.3kVA transformer as I wanted a wall mounted version that had a continuous 1.65kVA rating. During the last four months of operation I have managed to dump 250kWh or 24% of all generation into the hot water tank that was surplus after house load. I expect about one MW hours each year to be diverted in this way.

I am currently working on a transformer-less version that still uses the Arduino for control, two efergy ct's, but instead of the transformer I will be using eight relays that act as a low volt – high volt interface to switch a resistance network that drives a 3,800W dimmer circuit to control the voltage in stages to the 3kW immersion.
I have a working prototype and I plan to switch the following loads as solar is available 100W, 200W,300W, 400W, 500W, 600W 750W 1,000W. From my experience it is better to use small loads, as even in winter up to 500W is readily available and heat transfer is better at lower wattages as you get less insulating bubbles forming around the heating element.

The beauty of this system is all the parts are readily available Arduino and sensors £40, eight relays onPCB for Arduino £10 (Hong Kong), 3,800W dimmer PCB £8 (UK or HongKong) the most expensive item is a 5V DIN rail power supply but you could use a cheaper 9V 1A mains adaptor if you wish. I mount all my components in a ABB 12 way consumer unit as it give me flexibility and looks professional. It also allows me to fit a DIN rail Wattmeter so I know exactly how many kWh I have diverted. Total cost around £100 excluding meter.

I also have a third system in the pipeline with no relays as the 3,800W dimmer can be driven directly by the Arduino. However, the Arduino is not able to monitor the current and trigger the triac at the same time, so I would have use two Arduino's. It also requires additional electronics for opto-isolation and zero cross sensing. All of the components parts I have working separately, but not sure I want to go down that route,as it seems overly complicated when I already have a working system and the eight relay system upgrade is so cheap and less complex.

All three systems use stepped loads to try and match the spare solar output a bit like digital sampling of an analog waveform used in the music industry.

My system is also compatible with off peak systems, as the Arduino can switch a change over relay as soon as spare power is available. The Arduino needs a interface to the current transformers so you will need soldering skills see linkhttp://openenergymonitor.org/emon/buildingblocks/ct-sensors-interface you will also need a lot of patience.

It took me two weeks of trying to write an Arduino sketch for current calculation and triac triggering only to conclude it can't be done with one Arduino.

Regards, trader9.
 
Last edited:
has anyone used this Solar PV switch for hot water. I can see lots of posts of people developping their own pro type but none actually saying whether they have used it. I know it does not compare to actual consumption, but if it does as it says will sweitch on 1kw heater when panels generate more than 1.5 KW.

Thanks
 
I think the benefits will probably be small... between £50 and £100 per year for gas, bit more for economy 7, probably double or triple for electric / oil / lpg. Once I figure it all out I'll post what I think and hopefully people can correct my inevitable mistakes.

I've got gas, so will get the least payback, and I want to make the payback within a few years, so alot better than Solar PV itself. If energy prices rise then you are protected even more. I'm thinking if it warms up the water during the day, the gas boiler won't be needed, so for at least 3 months of the year I won't need to pay to heat the boiler up for showers, baths, washing up etc.

If everyone just made one for themselves then yes it would be alot of effort for little benefit, but I'm quite interested in getting different ones working, so for me it's a bit of fun too. I've got a kit-car, I could've bought it cheaper already made... but where's the fun in that?

Appreciate your thoughts... constructive criticism will stop me spending way too long on this or making mistakes so please keep them coming!

Thanks

Just been looking at a website called solardivert and from them they say it is about £170 a year in savings. Although oil will be a lot more expensive. They also have a product that looks fairly good as it takes into account consumption of electricity in the house and not just the electric generated from the solar panels. Not sure how much it is but they say it's low cost.

Thanks
 
I would definitely recommend a fully proportional power diverter rather than a stepped type. I have built a Crydom based diverter based on a circuit supplied by a member of this forum.
If this last weeks production is anything to go by the proportional system will really come into it's own in the winter.For example this week my 4kW WSW system has only produced around 4 to 6 kWh per day but the diverter has sent 2.5 kWh of the 4 kWh and 4.6kWh of the 6kWh to the immersion. This is everything not being used for other things like base load, dishwasher, washing machine etc. and about 40- 60W export. On poor days like these the power going to the immersion from the proportional diverter can be as low as 10 or 20W and up to a maximum of say 300W yet the tank can still be up to a good temperature by tea time. A stepped system might not kick in until say 500 or 1000W and so would not provide any heat on days like these. On medium to good days my immersion thermostat will kick in by about 11am at this time of year but then that shouldn't be much different on a stepped system depending on the tank size etc.
The only drawback of a proportional system is the cost. The cost of parts to build mine was £170 but compared to a plumbed solar hot water system even the £300+ of a ready built proportional system seems cheap.
 
Last edited:
I would definitely recommend a fully proportional power diverter rather than a stepped type. I have built a Crydom based diverter based on a circuit supplied by a member of this forum.
If this last weeks production is anything to go by the proportional system will really come into it's own in the winter.For example this week my 4kW WSW system has only produced around 4 to 6 kWh per day but the diverter has sent 2.5 kWh of the 4 kWh and 4.6kWh of the 6kWh to the immersion. This is everything not being used for other things like base load, dishwasher, washing machine etc. and about 40- 60W export. On poor days like these the power going to the immersion from the proportional diverter can be as low as 10 or 20W and up to a maximum of say 300W yet the tank can still be up to a good temperature by tea time. A stepped system might not kick in until say 500 or 1000W and so would not provide any heat on days like these. On medium to good days my immersion thermostat will kick in by about 11am at this time of year but then that shouldn't be much different on a stepped system depending on the tank size etc.
The only drawback of a proportional system is the cost. The cost of parts to build mine was £170 but compared to a plumbed solar hot water system even the £300+ of a ready built proportional system seems cheap.

Hi Digon

Thanks for your update, I am glad you have a good working system. I have been thinking of a fully proportional system but have only found a schematic without any other information on type of current transformers (CT's) set up etc.

Can you list all the parts you used please, so anyone else interested can also build one. And any useful information on the build process would be helpful

My problem is I can't get my head round the fully proportional concept. If you have two CT's measuring solar and house load, then as soon as you have more solar than house load you start to divert surplus to the immersion heater, but as soon as you do, the house load rises and you no longer have any surplus to detect. So how do you then maintain power to the immersion when both CT's are reading the same power levels?

My stepped system is easy, because as soon as there is 200W surplus I add a 160W load and then when this increases to 200W again I add an extra 160W load etc.

I currently have a microprocessor based five step system working using relays which cuts in at 160W then steps through 320W, 660W, 820W and finally 1320W.

My whole concept was to develop something cheap and simple for other people to copy. If I am successful my next system will require only basic components and should be well below £100.

Using a Arduino microprocessor interfaced via a opto-coupler to a 25A variable solid state relay SSRI could have as many steps as I want or if I understood the fully proportional concept I could maybe incorporate that instead.

The new system should be cheap, as the25A control SSR is only £8.52 mounted on a heatsink, Arduino £20,optocoupler less than £2, two efergy CT's with interface components £30, box and 9V mains adaptor £20. That's just £81 and the whole thing could more or less just be connected together with a screwdriver and no printed circuits to build.

Regards Trader9.
 

Reply to Solar Panel immersion heater automatic switch. in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Help please, this is my first post on this subject regarding solar panel / battery installation into house with 3 phase supply. I am a DIY level...
Replies
0
Views
1K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
782
Hi, I'm after some help please. I have a 21 panel 8.5kw system with 5kw export allowance and a Sunsynk 8kw inverter. The inverter has a smart...
Replies
0
Views
3K
I need a 3 phase immersion heater with a DN32/42 mm thread for a commercial pasteuriser. The only ones that I've found so far are not inexpensive...
Replies
0
Views
580
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock