loser123

hi

when i am generating 3kwh via the solar panels and only using to 2kwh the red light on the meter (electric company bill) comes on which means it has stopped..

but if i am generating 1.5kwh and using 2.00kwh will my meter which the electric company bill me for only going up 0.5kwh or 2.00kwh as no red light on the meter is visible in this scenario


i hope this makes sense :yes:
 
It should only go up 0.5 kWh. The electricity generated by your PV in this scenario never goes through that meter. It goes straight from your inverter to whatever is using it.
 
Assuming we are talking about an installtion in the UK, uner the FiT schem, then so long as it has been wired in correctly TedM is spot on.

Though of course we should actually be talking Power (kW) not energy (kWh) here. you billing is dependant upon the time of use. (Power x Time = Energy)

If you generate 3kWh (Energy) during the day and use 2kWh (Energy) at night them you will be billed for 2 kWh and (assuming you are on FiT scheme for <30kW) you be paid for generating 3kWh and additionally paid for exporting 1.5kWh (as they don't measure it)

IF you are generating 3kW (power) and at the same time using 2kW (power) in lighting etc, and it generates consistently at that level for an hour, and your consumption doesn't change during that period (no extra cups of tea :) ) then DURING THAT HOUR your import (DNO / Electric Company ) meter should not change

IF you are generating 1.5kW (power) and at the same time using 2kW (power) in lighting etc, and it generates consistently at that levvel for an hour, and your consumption doesn't change during that period (no extra cups of tea :) ) then DURING THAT HOUR your import (DNO / Electric Company ) meter should only increment by 0.5kWh - [0.5 kW (Power) for an hour = 0.5kWh [Energy])

In this graph, the only time that the electric company meter would be increasing is when the RED line is above the GREEN line (and hence the only time you would be charged)

1-chart.jpg

The RED line (consumption) as been optimised to match the GREEN line (Generation) in this real life installtion by the installtion of an ImmerSun unit that closely tracks the generation and consumption and diverts excess generated power to an electric hot water immersion heater. The large peaks include lunchtime when the kettle went on :) , breakfast and supper time.
 

Reply to solar pv question on meters in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Greetings, everyone, After dedicating over a month to researching Solar PV systems, I'm nearly ready to make a decision. I owe my progress to...
Replies
1
Views
925
Hello fellow professionals, I'm currently facing a challenging scenario that involves the integration of solar photovoltaic (PV) systems on roofs...
Replies
1
Views
288
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
1K
I currently have a 3Kwh solar PV system which was installed over 12 years ago and getting a very good FIT payment and I don't want to lose it! I'm...
Replies
0
Views
4K
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
423

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock