Hi all

I have an issue with a spa installation we had a few months ago.
Just as a bit of background info, I am a TV engineer and run a TV engineers forum, I have also completed many of my own electrical installations at home before things got a tricky without the relevant qualifications etc.

The install consisted of splitting the tails, installing a new metal clad fuse box with appropriate fuse and RCD and running the larger of the applicable sizes of armoured cable around the house to a 32a rotary isolator, then there is a length of armoured cable into the spa.
This was completed by a qualified electrician prior to the spa arriving.

The was fitted and has been OK.

Last night I decided to check the chemicals in the spa before getting in, this is highly unusual for me, checks are usually performed earlier.
I was barefoot on an outside block paved patio, I dipped the test meter in the water and got a good tingle through a few days old cut in one finger.

Put a non injured finger in and you feel nothing, put my shoes on and put the cut finger in and you feel nothing.

I have read through any posts referencing spa shocks on this forum but the solution isn't entirely clear to me. As I recall the armoured cable was three core and I can't remember what the electrician said or did about the earth conductor and the armoured outer, are they joined together????

Anyway, I have contacted the spa installer and they are coming out tomorrow.
I asked the following question, which probably didn't go down well.

Can you tell me what qualifications your installer has please?

The answer was "years of experience, knows hot tubs inside out etc etc" & "was approved as competent by the NICEIC"

It seems strange that a qualified electrician must install everything but someone with proof of nothing can be left to make the final connections to the spa given the current legislation as I understand it.

Can anyone tell me what the situation is regarding who can or can't make the final connections and should any tests have been completed on the installation before or after the installation of the spa. Should a record of installation have been left for us?

Considering the longish run of armoured cable around the house was there a more appropriate method to install it, I read a lot about rods being driven in the ground near spa's in the other threads.

Thanks for any advice offered. This is a little different to what my forum members normally deal with.

regards
Trevor
 
You probably have a tncs/pme earthing arrangement and the tingle you are feeling is the potential difference between true earth and the earth of the electrical installation. An earth electrode connected to the MET with a very low impedance could be used negate the potential difference.
 
Last edited:
Hi
Many thanks for the quick reply, I was hoping that's what the issue was. It was suggested by a member on my forum as well.

So that connection must be to the MET and not at the spa end where it would be easier to to get deep into the clay soil.

Is there a requirement regarding the maximum length of cable from the rod to the MET and gauge of wire to be used?

And I assume that doing that work would require a part P qualified person rather than a competent person?

Thanks again.

Don't know how you guys on here cope, I have read the rule books and they seem wide open to be interpreted differently each time I read them.......
shocking.gif
 
Out of interest TrevorM did you receive an electrical installation certificate for the new circuit? If you did, under the section of supply characteristics it should have a tick next to what earthing arrangement you have.
 
Last edited:
Why don't you call the installer of the circuit back and get him to retest the circuit and compare the results with the certificate he gave you?
 
Lee, what's your preference when it comes to hot tubs? I have connected a few, not many, and I normally connect it back to the supply earth as it's going to be better than any rod, however these were all sitting on decking limiting the risk. I know sticking rods in would be nice and cut off the supply earth but it's never going to compete.

however, I suppose you could always put a rod in local to the tub and connect it back to the met, gives you redundancy in the event of fault.
 
Thanks for the replies guys.

Yes, after researching this issue tonight and the help from this forum, I suspect all is OK and the potential difference is the issue.
Unfortunately I seem particularly sensitive to 50Hz and any AC voltages.

As I frequently work on live equipment I am especially careful and was probably a bit unfair to the spa installer over the phone.
Of course this on mostly isolated supplies but a hefty wallop can still be administered.
I shall grovel a little bit tomorrow and offer tea and cake :icon12:

And thanks for the offer.

regards
Trevor
 
Why don't you call the installer of the circuit back and get him to retest the circuit and compare the results with the certificate he gave you?

Thats not a bad idea, I know if someone called me to say that about my install I'd be round there like a shot as I would hate for something bad to happen and get the blame!
 
Hi
The electrician is customer of mine and did the work for me one weekend so I do not have a certificate.
I am going to call him for a chat but only got the answer phone tonight.

Yes, I am absolutely sure it is a shock, the cut provides a lower resistance to the rest of the skin.
I even popped my Fluke probes in the water and onto my skin and get a 2-3 VAC depending on pump speed.
And it doesn't happen with shoes on.

It might be interesting to try the same thing with bare feet and the metal kitchen sink.
 
So you wouldn't expect the spa fitter to have a Fluke or Kewtech to make certain everything was OK before making the connections?

regards
Trevor
 
Lee, what's your preference when it comes to hot tubs? I have connected a few, not many, and I normally connect it back to the supply earth as it's going to be better than any rod, however these were all sitting on decking limiting the risk. I know sticking rods in would be nice and cut off the supply earth but it's never going to compete.

however, I suppose you could always put a rod in local to the tub and connect it back to the met, gives you redundancy in the event of fault.

Have you ever considered extending the equipotential zone as well as rodding, this would give the best of both worlds, excellent low earth resistance with local equalised true earth to provided earth.
 
Lee, what's your preference when it comes to hot tubs? I have connected a few, not many, and I normally connect it back to the supply earth as it's going to be better than any rod, however these were all sitting on decking limiting the risk. I know sticking rods in would be nice and cut off the supply earth but it's never going to compete.

however, I suppose you could always put a rod in local to the tub and connect it back to the met, gives you redundancy in the event of fault.

It depends really..using the suppliers earth or making the hot tub TT both have there pros and cons Imo. When using the suppliers earth pme/tncs you could have a healthy installation but experience "tingles" like the OP suggests but this isn't going to do wonders for the relationship between you and the customer so to speak. When Making the hot tub TT 99/100 you are going to be relying on an RCD for earth fault protection. In an ideal world I suppose you would use the suppliers earth with a rod/s connected to the MET with a very low Ra and have the hot tub either sat on or have wooden/composite decking built around it where you are likely to be in contact with the tub and ground at the same time
 
Hi
The electrician is customer of mine and did the work for me one weekend so I do not have a certificate.
I am going to call him for a chat but only got the answer phone tonight.

Yes, I am absolutely sure it is a shock, the cut provides a lower resistance to the rest of the skin.
I even popped my Fluke probes in the water and onto my skin and get a 2-3 VAC depending on pump speed.
And it doesn't happen with shoes on.

It might be interesting to try the same thing with bare feet and the metal kitchen sink.
Is weekend work exempt from certification then?
 
Op not sure if you've have the search facility on this forum. If you have, you'll find a lot of posts on this subject. No expert myself in this area, but the advice you've been given by Lee appears spot on from what I've researched. Putting on shoes increases your resistance, thus prevents you receiving a 'shock', in your described scenario. In addition to what Lee suggested (if it proves to be the case), I would also consider putting down some materials, to prevent you stepping on bare earth or ground, when getting in and out of your tub. Stuff I've read about outside spa baths etc, I wouldn't be using one as you have installed (the tub, not necessary the electrical installation). Composite decking might be an idea?
 
Last edited:

Reply to Spa shock issue and competence to install in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
642
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock