Discuss Spark gone missing after EICR and no report in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
88
I've been called by a client to fix a problem exposed by EICR.
Spark put new light and fan in shower, also moved shower switch above bathroom door. Customer wanted EICR, but spark got his mate to do as he can't do EICR. So I'm suspicious he's not part of CPS, below might make you think the same.
Anyway, second spark come round and did stuff, I'm not sure what. 1st Spark never forwarded EICR and just mentioned a short on ring. After a few months customer got fed up chasing and called me.
While I was there I had a quick look, I can see 118 ohms across live and neutral. Turns out boiler is run off kitchen ring in fused spur and this was reason for reading. After post on plumbers forum apparently this is normal.

Anyway, while I was there I observed a shower switch above ground floor bathroom door. I also observed a shower pull switch in the 1st Floor bathroom. So nothing suspicious there...……..
Customer asked if I could remove pull switch in 1st Floor as not used. Stuck my head in and has electric shower. Sorry no I says, you need this it must be in use. No says customer switch for 1st Floor bathroom is above Ground Floor bathroom. Turns out Ground Floor shower is mains fed, no electric.
Seems mad as this is a new switch down stairs. I've suggested I move switch back upstairs which is very quick job. Customer agrees.
However, whilst this seems like a crazy place to put a shower switch, in reality it's not unsafe. But I assume there is a reg that says switch must be in close proximity to shower?

This is as much I want to get it off my chest as a question.
 
I've been called by a client to fix a problem exposed by EICR.
Spark put new light and fan in shower, also moved shower switch above bathroom door. Customer wanted EICR, but spark got his mate to do as he can't do EICR. So I'm suspicious he's not part of CPS, below might make you think the same.
Anyway, second spark come round and did stuff, I'm not sure what. 1st Spark never forwarded EICR and just mentioned a short on ring. After a few months customer got fed up chasing and called me.
While I was there I had a quick look, I can see 118 ohms across live and neutral. Turns out boiler is run off kitchen ring in fused spur and this was reason for reading. After post on plumbers forum apparently this is normal.

Anyway, while I was there I observed a shower switch above ground floor bathroom door. I also observed a shower pull switch in the 1st Floor bathroom. So nothing suspicious there...……..
Customer asked if I could remove pull switch in 1st Floor as not used. Stuck my head in and has electric shower. Sorry no I says, you need this it must be in use. No says customer switch for 1st Floor bathroom is above Ground Floor bathroom. Turns out Ground Floor shower is mains fed, no electric.
Seems mad as this is a new switch down stairs. I've suggested I move switch back upstairs which is very quick job. Customer agrees.
However, whilst this seems like a crazy place to put a shower switch, in reality it's not unsafe. But I assume there is a reg that says switch must be in close proximity to shower?

This is as much I want to get it off my chest as a question.
Looks like this client of yours has had his pants pulled down by Matey the " Electrician"
 
Have you carried out many eicrs? Why would you test L-L on a ring final? L&N -earth (with cpc connected to earth bar) is only required IR test imo on eicr.
No isolator atall on shower is a c2 for me its cowboyish, provides no local isolation & doesnt comply with MI.
 
[QUOTE="Michaelwgroves, post: 1454180, member: 68265"

But I assume there is a reg that says switch must be in close proximity to shower?

[/QUOTE]
Sorry to be blunt but EICR's require a considerable level of experience and knowledge, you do not seem to me to have the required knowledge to be advising the client on such matters. Seems to be a case of the blind leading the blind.
 
The OP wasn’t conducting an EICR.
He was rectifying faults found on an EICR.
If I were to have an Isoltor for a shower, I think I would prefer it to be outside the shower it corresponds with, rather than outside a different shower.
 
There’s no Regs stating showers or other household appliances should have local isolation.
However where local isolation is desired, it’s not much use if it’s not local.
 
MIs are guidance only, and don't have to be followed, especially when they are wrong.

So you think MI are wrong stating there should be a local douple pole isolator? Do you not fit isolators adjacent to showers, cookers, heaters boilers ect..
The regs are a minimum guidance, nothing stopping you going a step further to better the install.
Madness not to have one imo.
 
So you think MI are wrong stating there should be a local douple pole isolator? Do you not fit isolators adjacent to showers, cookers, heaters boilers ect..
The regs are a minimum guidance, nothing stopping you going a step further to better the install.
Madness not to have one imo.
It’s not so much that they are wrong (though sometimes they clearly are), as whether non-compliance with an MI is a non-compliance with the Regs. or is dangerous.
 

Reply to Spark gone missing after EICR and no report in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

This could possible have been a poll, but really just opening up for suggestions and feedback on where folks think an isolation switch for an...
Replies
12
Views
3K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
671
Hi Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired...
Replies
8
Views
1K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
838
Hi Absolutely 0 knowledge of this so excuse language / terms / explanation. Electric only ground floor 2 bed flat ( 3 external walls) On peak...
Replies
59
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock