Discuss SPD for TPN 100a sub mains in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi Guys,

Looking for some options to provide surge protection to a 100a TPN sub main to be wired 60m from the origin

Im currently looking at installing a 4 way TPN mccb panel board with spd at the origin but it looks as if its going to cost the best part of a grand

This is obviously a far greater cost than installing a TPN 100a switch fuse but don’t really see many alternatives

Any one any ideas to keep the cost down?
 
Is there already some board at the source?

If it is simply a sub-main from supply point to the existing DB then just put in a switch-fuse for cable fault protection (assuming not TT!) at the source and then have the SPD at the end DB.

MCCB panels are expensive, and unless you get the fancy and expensive electronic MCCB (maybe with EL trip) they have a lower and harder to meet Zs requirement compared to the good old fuse.

If you absolutely have to have the SPD at the source then you could use a switch-fuse for the 100A over-current protection and then have a small DIN box for the SPD and a few Henley block to join it up, or some DIN terminals that can accept the size of incoming and outgoing wires as well as the link to SPD, or some line-taps in the DIN box, etc. Just keep the cables from block to SPD short (less then 25cm).
 

Reply to SPD for TPN 100a sub mains in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I am a homeowner and have a solar project coming up. I intend to install a 9kw solar system but I am not sure if I have to upgrade my main...
Replies
2
Views
962
Struggling a touch at the minute with customers getting work done by “someone they know” and citing our quotations being too expensive as the...
Replies
7
Views
722
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
737
Hi We are looking to get an EV charger installed, and I asked for an SPD to be on the new CU that will be required for that. The electrician has...
Replies
11
Views
5K
hi thank you for help in advance have a potential pv installation for a garage roof that is some 60m from the main house (main incomer in the...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock