Discuss Spilt concentric cable duel use in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
8
Morning all, started a job yesterday fit a bathroom fan etc.
When I took off consumer unit cover to do dead test I came across a split concentric cable supplying an outbuilding/shed in another Mcb. It was the type with the single insulated neutral and separate earth. What threw me was that some of the neutral cores had been separated and used as two way switch for an outside light. Theswitch was located next to fuseboard and the other next to the c/unit it’s in shed. All the cables had been sleeved for identification etc
Not having much experience of this cable I immediately thought this is not right, you cannot do that.
just wondered if anyone could shed some light on it, or is it fine but just something I have not seen before
 
Can we get a photo?

Concentric is usually a live central core, with neutral as strands around that, and earth as strands around that on the outside.

There is also one with the neutral and earth strands in the same layer, but the neutrals are insulated.

Concentric isn’t normally used as installation wiring…. Just supplies for DNOs.
(someone may correct me there)
 
Can we get a photo?

Concentric is usually a live central core, with neutral as strands around that, and earth as strands around that on the outside.

There is also one with the neutral and earth strands in the same layer, but the neutrals are insulated.

Concentric isn’t normally used as installation wiring…. Just supplies for DNOs.
(someone may correct me there)
Not the best picture, but you can see the neutral cores go into to of main switch then the 3 terminals they have separated for the 2 way. The person who lives here previously worked for Dno so might explain why this cable was used as probably got it for free
6DFD1325-6D70-4F7B-A484-05AF8BC86B2A.jpeg
 
It’s not really a multi core cable.

the number of neutral strands will give an equivelant CSA of the line conductor, so taking 3 out will reduce that.

C2 on EICR if I was feeling generous. C1 if that type of cable shouldn’t be used in that situation in the first place.
(I’m on holiday, regs book at home, so can’t check)
 
Interesting!
My first thought is the reduced csa of the neutral - it's unlikely to be an issue but I'd want to check - I'd measure one of the cores with micrometer and work it out. My guess is you have at least 10mm^2 there. Whatever it is, you'd have to consider the csa of the Live to be too, and check the upstream OCPD is adequate.
(the connections in the terminal block look poor, middle one biting insulation?)
 
@littlespark cross-post, and we agree on that bit!
But as long as cable is adequately sized, marked accordingly and appropriate for the conditions I'm struggling to immediately see why it's a C2.
Just because it's not common (understatement!) doesn't instantly make it dangerous in my view.
 
The biggest size the cable can be with seven neutral cores is 16.0 and assuming it is 16.0 each neutral core is 1.70.
There is no issue with the neutral cores being used as a line conductor as the cable is rated at 600/1000v meaning 600v between live conductors and earth, 1000v between live conductors.
The question here is the reduced csa and whether it is installed to manufacturers requirements.
 
1000V between live conductors, yes, but the neutrals would be classified as a whole, not as individual conductors. There's a plastic spacer core separating the neutrals from the earth and the much thicker and robust insulation surrounding the live central conductor separating the live and neutrals.
 
It is 16mm as It had 1x16/16/16 on cable sheath. If you were doing an eicr what code would you give? I looked in regs last night but didn’t help as could not find anything to help make a decision if I was going to give c2 or c3.
thankfully only had to fit a fan but defo an interesting one
 

Reply to Spilt concentric cable duel use in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
Had UKPN come out to a property recently to upgrade the main fuse from 60A to 100A but when they arrived they said that the supply cable which he...
Replies
9
Views
2K
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
579
Hi Everyone, Last year arranged for my mother's and my consumer units to be changed by the same electrician who is NICEIC registered. Both jobs...
Replies
20
Views
2K
Looking for some cabling advice for my garden project. I’ve put together this diagram below, which hopefully explains what I’m trying to achieve...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock