Discuss Spur at point of origin in the UK Electrical Forum area at ElectriciansForums.net

P

pyrosym

Just a quick question, I know you can spur a ring at the C.U. but can you do the same with a radial?

I have not seen it done that way on a 20A A3 radial.

It is only for a test rig I am putting together to train students testing so its not that important any thoughts?
 
To be honest I have never been quite sure what is meant by a "spur" of off a radial circuit. I guess on a 4mm socket radial there could be a call for it, cost wise if you wanted to extend it and decrease the cost of cable down to 2.5mm

As for a 20amp 2.5mm socket radial, well unless you wanted to take say a light off of it, there is very little point in creating a "spur" and that is why in appendix 15 there is no mention of spurring at the CU, as there is no mention of spurring anywhere full stop.

As for what you plan there is nothing wrong with it. In essence your using the MCB/Fuse in the CU as a JB. It is still just one circuit, and as long as you utilize the correct size cable for the PD it is fine
 
The way I see it, if you 'spur' off a 20a 2.5mm radial at the CU or anywhere else, it is not actually a spur, it is just a branch of that circuit. As malcolm points out, a 2.5mm branch off a 4mm 32a radial would in fact be a spur (hence can only serve one double socket)!
 
Sorry Malcolm but if you look at page 426 in the BGB, it does actually state: "An unfused spur may be connected to the origin of the circuit in the distribution board".
 
That is mentioned on the 4mm 32amp radial Spin, I was referring to the 20amp 2.5mm (A3) one mate, that doesn't mention mention spurs at all.
Oh yes I see what you mean.
If you notice, there is no mention of the two spurs on the 20A diagram.
That's because the spurs use the same CSA conductors.
Just as with the 30/32A diagram, ther is no mention of the 4mm² spur.
I guess they didn't consider it worth a mention, if the spur uses the same CSA as the rest of the circuit, as the CPD will provide protection.
Only fused and unfused spurs are mentioned because the CPD won't provide overload protection.
 
You can't really have what I'd call an unfused spur off a 20a radial.....it's just a branch! An unfused spur would have to be run in 1.5mm², and we obviously wouldn't do that! If you see what I mean lol.
 
You can't really have what I'd call an unfused spur off a 20a radial.....it's just a branch! An unfused spur would have to be run in 1.5mm², and we obviously wouldn't do that! If you see what I mean lol.
I wouldn't know about that.
I'm thinking bell transformers, smokes and door entry systems.
Often spured off in 0.75mm² or even smaller.
 
Thank you all,
It seems like it will create debate among my students so I'm going to do it and see what they come up with on their EICR sheets. I'm going to spur off the breaker with a double socket and built in RCD just to make them scratch their heads a bit more as its already a sub.

kind regards all
 

Reply to Spur at point of origin in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
465
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
631
Evening all, Been to a job on Fri where the customer had a condition report completed. Two of the remedial identified was that there were too...
Replies
7
Views
1K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
863

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock