I have one single socket on its own from a consumer unit. (10A) (no ring) Can I swap this to a double and then spur off another double from it? It means there will be an equal number of spurs than there are sockets which I have been told is a no no. Is this true?

Thanks in advance
 
they're not spurs as it not a ring circuit. you will have a radial socket with 2 double outlets.
 
Only a 10amp MCB on that circuit? Does it only have small cable supplying the socket?

It sounds like its a radial put there for a low-current purpose (intruder alrm, boiler, etc). Even a modest load on those two sockets will trip the MCB. What did you plan to run off those (potentially) 4 sockets?
 
Does the CU or circuit you are adding the socket to have a RCD?

How are you intending to install the extra socket?
 
Last edited:
I have one single socket on its own from a consumer unit. (10A) (no ring) Can I swap this to a double and then spur off another double from it? It means there will be an equal number of spurs than there are sockets which I have been told is a no no. Is this true?

Thanks in advance
Deanomc, ask the mods for access to the trainee section, to go back to your question, what size cable has the one socket been wired in? if its 2.5 you could turn the circuit into a 20Amp radial, take a look at Appendix 15 in your copy of BS 7671.
 
Deanomc, ask the mods for access to the trainee section, to go back to your question, what size cable has the one socket been wired in? if its 2.5 you could turn the circuit into a 20Amp radial, take a look at Appendix 15 in your copy of BS 7671.

Never realised I was in the wring section. I'll email the the moderator. As for the wire, it is a 2.5 T&E. Thanks for the help
 
The current single socket is in the living room. I believe a tv, skybox, wifi box and hifi will run from them. So I need to upgrade it to a 20Amp on the RCD. Does this seem reasonable .
 
The current single socket is in the living room. I believe a tv, skybox, wifi box and hifi will run from them. So I need to upgrade it to a 20Amp on the RCD. Does this seem reasonable .

2.5 turn it into a 20 Amp radial with a 20 Amp OCPD (MCB) + a 30ma RCD
 

Reply to Spuring off one socket in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
654
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
715
Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
567
Double wall socket switch won't switch off. It just flips back to on. The left side one is fine. It used to do this 3 years ago then was working...
Replies
1
Views
440
Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
751

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock