Hello again
Thanks to those who answered my question on PIR/occupancy sensors for my downstairs toilet.
I have some questions regarding a flat I'm renovating. The flat is an ex-council property; imperial steel conduit, wired in singles, Wylex skeleton board in a Mantel cupboard, solid concrete floors and ceilings.
The Kitchen is very short of sockets. There at two single sockets at low level. The L-shaped worktop has one double socket at the far end of L. The only other socket is on the Cooker Control unit and serves the part of the worktop at the corner of the L and that's it!
I'd like to add some more sockets and am intending to get a local contractor to come and change the Wylex fuseboard for a Wylex FAL Consumer unit (2 RCDs), and give then this job. I just want to be clear what I should be asking for.
The Cooker circuit is wired in 6mm currently has a 32a MCB protecting it. The cooker has three elements (main oven 2.7kw, small oven 1.7kw, grill 2kw. total of 6.7kw or 27Aif no diversity applies). There is no RCD the current fuse board. I believe it would be possible to continue the 6mm cooker circuit (in 6mm) to a FCU with ?A fuse to feed a couple of double sockets. I appreciate there's not a lot of capacity on the circuit unless some diversity applies but I think I need to do something to increase the number of sockets and don't want a lot if making good to do. Neither am I a fan of mini-trunking.
The Cooker Control Unit is set into the top line of tiles. (There are just three rows of tiles above the work top.) I believe it would be a relatively simple job for the contractor to pop off this top line of tiles, and sink some 6mm T+E into the plaster to run to the FCU and continue in 2.5mm to a couple of flush double backboxes. (Approx 1m of 6mm & 1m of 2.5mm.)
My questions:
1. Can any diversity be applied to the cooker load to give me more than 5A for any additional sockets?
2. If some additional sockets can be added, would you feed them from the supply side of the FCU or from the Load side? (I was surprised to find that the switch for the socket on the CCU is in series with the cooker switch. It struck me that it might be more logical if the cooker switch isolated all the sockets fed from the CCU not just the one on the front.)
Thanks all
Thanks to those who answered my question on PIR/occupancy sensors for my downstairs toilet.
I have some questions regarding a flat I'm renovating. The flat is an ex-council property; imperial steel conduit, wired in singles, Wylex skeleton board in a Mantel cupboard, solid concrete floors and ceilings.
The Kitchen is very short of sockets. There at two single sockets at low level. The L-shaped worktop has one double socket at the far end of L. The only other socket is on the Cooker Control unit and serves the part of the worktop at the corner of the L and that's it!
I'd like to add some more sockets and am intending to get a local contractor to come and change the Wylex fuseboard for a Wylex FAL Consumer unit (2 RCDs), and give then this job. I just want to be clear what I should be asking for.
The Cooker circuit is wired in 6mm currently has a 32a MCB protecting it. The cooker has three elements (main oven 2.7kw, small oven 1.7kw, grill 2kw. total of 6.7kw or 27Aif no diversity applies). There is no RCD the current fuse board. I believe it would be possible to continue the 6mm cooker circuit (in 6mm) to a FCU with ?A fuse to feed a couple of double sockets. I appreciate there's not a lot of capacity on the circuit unless some diversity applies but I think I need to do something to increase the number of sockets and don't want a lot if making good to do. Neither am I a fan of mini-trunking.
The Cooker Control Unit is set into the top line of tiles. (There are just three rows of tiles above the work top.) I believe it would be a relatively simple job for the contractor to pop off this top line of tiles, and sink some 6mm T+E into the plaster to run to the FCU and continue in 2.5mm to a couple of flush double backboxes. (Approx 1m of 6mm & 1m of 2.5mm.)
My questions:
1. Can any diversity be applied to the cooker load to give me more than 5A for any additional sockets?
2. If some additional sockets can be added, would you feed them from the supply side of the FCU or from the Load side? (I was surprised to find that the switch for the socket on the CCU is in series with the cooker switch. It struck me that it might be more logical if the cooker switch isolated all the sockets fed from the CCU not just the one on the front.)
Thanks all