Discuss Spurs.... Not the football type! in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
31
Hi Guys
Need the experts advice again please .

Recently added a new double socket in a kitchen off of the existing ring final.

At last minutes notice I was asked to see if I can add an outside light by the back door. (Which is right next to the new socket that's just ben added)

The question being, if I were to add a 3A FCU from the spur I've just added to then feed the outside light, this would be classed as spurring a spur right?
So would a better option be to add a 13A FCU before the new spur and then have the outside light feed off of the double socket?
Realistically I can't take the feed for the light from anywhere else but don't want to disappoint and turn down the request.

As always, your help is very much appreciated .
 
Thanks Guys .
Very informative as always. I've read the Regs and as above have seen that u u need the FCU to be prior to the new socket if I'm to add the outside light as well.

My second question is, purely out of curiosity is, can I wire both the new socket AND the outside light coming from the FCU or will the load blow the fuse (13A) or only the double socket from the FCU and then have the outside light coming from the socket?

Thanks .
 
It doesn't matter where you connect the external light from providing the spur protects both. What is currently connected from the socket and I assume rcd protection is provided.
 
Ok. It would be easier for to run the light straight from the FCU. I just wasn't sure if I could have the wiring for the light and the socket in the FCU.
That's ok to do is it?

RCD wise. It's a very old build so no RCD on the ring at the CU. Would making the FCU an RCD protected FCU be sufficient?
 
Are you electrically qualified because the socket you added would have required additional rcd protection.
 
Via the FCU or at the Board?
Long story short, qualified as a domestic installer last year, was working as an apprentice with an electrician, he left unduly so I've been asked to do two small jobs in his absence.
This being one of them.

So because I've added a spur to an existing ring, I need to upgrade the whole board so it's RCD protected?
 
So at present are you working with no guidance because it is a bit worrying you have installed a socket without additional rcd protection. Assuming this is a domestic site the new light fitting also requires additional rcd protection.
 
At present yes until the new spark arrives. I was under the impression that an additional socket was something the home owner could do?
So an FCU prior to the new socket wouldn't be enough?
I'd have to upgrade the entire board?
 
At present yes until the new spark arrives. I was under the impression that an additional socket was something the home owner could do?
So an FCU prior to the new socket wouldn't be enough?
I'd have to upgrade the entire board?
Not necessarily.
 
Thanks for confirming.
The work you do will need to be RCD protected but not necessarily the whole consumer unit. Obviously depending on the circumstances then different methods of achieving this may be considered, including RCD protection of the whole circuit.
 
@DPG I can test and inspect but the likelihood is we will get someone in to do so.

@Pete999 I thought an addition to an existing installation wouldn't require a new board. Would it be necessary to do so in this instance!?
You could fit a RCD Fused spur unit before you install the new socket
 
home owner can do anything up to new circuits or wiring in locations containing a bath or shower without notifying the local authority. And even those if they agree with the local authority about getting it certified. However regardless of all that the whole electrical installation is a controlled service under building regs so th ehomeowner still must comply with part P which in practice means BS7671 (for all the design, testing, installation and certification but good luck finding a DIY who did all that)
Otherwise you're saying that work done by the homeowner can be less safe, which makes no sense.
So if BS7671 requires RCD protection for all new socket outlets (and concealed cables) then that must be complied with to comply with building regulation. The only things that need updating on an existing consumer unit would the fundamentals e.g. bonding and disconnection times. The RCD protection can go elsewhere.
 

Reply to Spurs.... Not the football type! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
714
Hi all, Thank you in advance... So I had an electrician put in some FCUs on spurs to a couple of outside lights.. this one was in readiness to...
Replies
17
Views
627
Hi, apologies for the basic question In a radial circuit, is it permissable to spur off the supply side of an existing fused connection unit...
Replies
1
Views
390
Evening everyone… I’ve attached pictures for your leisure.. so basically the customer does not have any RCD protection.. 3036 fuseboard is in...
Replies
9
Views
362
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
711

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock