Looks like the ssr is connected to the relay output
it should be connected to the ssr output terminals.
however, it May not be as simple as moving them from one set of terminals to another.
you need to look at the instructions for the temperature controller to see the correct way to wire the ssr to the controller
I based on how the previous Eliwell EWTQ905 thermoregulator was connected, the previous thermoregulator had an internal relay which drives an SSR, but the SSR cannot be connected directly to numbers 11 and 12 otherwise the oven does not work and the thermoregulator would go crazy. The oven is designed to be connected in this way.
 
The temperature controller is designed to drive the ssr direct from its ssr output.
I really think you are going to need someone who has the knowledge to come and fix this for you.
 
The D2425 requires a direct current control voltage signal. From where is this voltage signal currently obtained which is at the moment routed via the normally open no volt contacts in the controller to the ssr? The D in D2425 indicates direct current control whereas an A as in A2425 would mean alternating current control signal.
 
Last edited:
The D2425 requires a direct current control voltage signal. From where is this voltage signal currently obtained which is at the moment routed via the normally open no volt contacts in the controller to the ssr? The D in D2425 indicates direct current control whereas an A as in A2425 would mean alternating current control signal.
There is a Fagor B40 C5000 / 3300 rectifier bridge which has been replaced with a new one just to exclude it from the possible cause of the problem that does not make the oven work.
 

Attachments

  • fagor.jpg
    106.2 KB · Views: 18
if You are determined to use the relay output, have you reprogrammed the relay output to be heat instead of an alarm of some type?
 
The direct current wires come out of the respective polarities of the rectifier bridge and go straight into the input of the SSR relay.

Instead the alternating current wires of which I am attaching the photos are connected to several wires.

As for the alternating current instead (measuring with the tester at the output it says 228 v):

The white wire coming out of the SSR at the top taped together with a black wire goes to the resistance, the black wire instead goes to the panel light which turns on when the heating is in progress. The other wire that comes out of the light arrives in the blue connector present in the power supply of the thermoregulator, they are two wires in the same connector.

The blue wire that starts from the SSR relay ends up in the terminal block next to the rectifier bridge, it is taped together with another wire which goes into the first double connector on the power button at the top, the other part of the double connector goes to the timer and the other wire coming out of the timer goes into the first red power connector on the thermoregulator.

Instead, the last black wire on the right in the terminal board ends up in connector 4 of the thermoregulator.
 

Attachments

  • foto32.jpg
    97.6 KB · Views: 22
  • foto34.jpg
    133.5 KB · Views: 16
  • foto33.jpg
    67.3 KB · Views: 15
  • foto35.jpg
    348.2 KB · Views: 19
These are my latest thoughts on why your oven is not working. The D2425 is a 'zero crossing' device. It will only turn on when the mains cycle crosses the zero Volts axis. The condition for it turning is a trigger voltage greater than 3Vdc and a mains voltage less than the maximum allowable voltage for turn on at zero crossing. I show these in my attached diagram.

The trigger voltage is currently derived from the mains 240V cycle via a step down transformer to 24V ish (I cannot remember exact value). The stepped down 24 ac waveform is in synchronism with the mains cycle as I show in the diagram. Thus both the 240V ac waveform and the 24V waveform are in phase and cross over at 0V at the same times. The slope of the 240V ac waveform is greater than the slope of the 24 V ac waveform.

The 24V ac waveform is passed through a full wave rectifier to produce the green waveform . This is a unidirectional voltage but not constant, drops to zero volts and for a short period at crossover is not greater than the minimum 3V dc to trigger the D2425.

I think that the ssr is not triggering reliably. Sometimes the trigger voltage is greater than 3V dc before the mains cycle exceeds the maximum crossover start conduction voltage - the ssr turns on and powers the element.

But at other times (and maybe temperature dependent) the mains cycle exceeds the maximum crossover start conduction voltage before the trigger voltage exceeds 3V dc - so the ssr does not turn on.

The ssr requires a constant unidirectional voltage signal or at least a voltage which switches between 0V and greater than 3 V dc for reliably triggering into conduction. I attempt to show this bottom right.

What to do?

Place an electrolytic high temperature capacitor - say 1000 microFarads 63Vdc electrolytic - across the terminals 3 and 4 of the ssr - ensure polarity of capacitor. Or use the controller's dedicated ssr output which has a voltage waveform suited to signal the D2425 to start conduction at crossover because it instantly exceeds 3V ie: it does not follow the mains cycle waveform.

If you try the capacitor solution buy a few of these:

RS PRO 1000μF Electrolytic Capacitor 63V dc, Through Hole | RS Components - https://uk.rs-online.com/web/p/aluminium-capacitors/7076666
 

Attachments

  • E94770CC-1218-49D6-8F26-5B20A43B3FBB.jpeg
    239.9 KB · Views: 20
Last edited:
These are my latest thoughts on why your oven is not working. The D2425 is a 'zero crossing' device. It will only turn on when the mains cycle crosses the zero Volts axis. The condition for it turning is a trigger voltage greater than 3Vdc and a mains voltage less than the maximum allowable voltage for turn on at zero crossing. I show these in my attached diagram.

The trigger voltage is currently derived from the mains 240V cycle via a step down transformer to 24V ish (I cannot remember exact value). The stepped down 24 ac waveform is in synchronism with the mains cycle as I show in the diagram. Thus both the 240V ac waveform and the 24V waveform are in phase and cross over at 0V at the same times. The slope of the 240V ac waveform is greater than the slope of the 24 V ac waveform.

The 24V ac waveform is passed through a full wave rectifier to produce the green waveform . This is a unidirectional voltage but not constant, drops to zero volts and for a short period at crossover is not greater than the minimum 3V dc to trigger the D2425.

I think that the ssr is not triggering reliably. Sometimes the trigger voltage is greater than 3V dc before the mains cycle exceeds the maximum crossover start conduction voltage - the ssr turns on and powers the element.

But at other times (and maybe temperature dependent) the mains cycle exceeds the maximum crossover start conduction voltage before the trigger voltage exceeds 3V dc - so the ssr does not turn on.

The ssr requires a constant unidirectional voltage signal or at least a voltage which switches between 0V and greater than 3 V dc for reliably triggering into conduction. I attempt to show this bottom right.

What to do?

Place an electrolytic high temperature capacitor - say 1000 microFarads 63Vdc electrolytic - across the terminals 3 and 4 of the ssr - ensure polarity of capacitor. Or use the controller's dedicated ssr output which has a voltage waveform suited to signal the D2425 to start conduction at crossover because it instantly exceeds 3V ie: it does not follow the mains cycle waveform.

If you try the capacitor solution buy a few of these:
In the input of the relay and at the output of the rectifier bridge the measured direct current is 22.6 volts. When the heating process is on, the DC current measured at the SSR input is 22.3-22.4v instead when the heating process is off, it is approximately 22.6-22.8v.
 

Attachments

  • ssrinput.jpg
    345.1 KB · Views: 7
In the input of the relay and at the output of the rectifier bridge the measured direct current is 22.6 volts. When the heating process is on, the DC current measured at the SSR input is 22.3-22.4v instead when the heating process is off, it is approximately 22.6-22.8v.



So to be clear - the voltage across the ssr terminals 3 and 4 is always in the range 22.3 - 22.8 V? It never drops to zero Volts even when the heating process is Off? This is surprising and not what one would expect.

Why will you not connect the SSR to the controller's SSR output? This output is designed to switch the SSR on and off.

Could you draw a diagram of how items are connected please?
 
So to be clear - the voltage across the ssr terminals 3 and 4 is always in the range 22.3 - 22.8 V? It never drops to zero Volts even when the heating process is Off? This is surprising and not what one would expect.

Why will you not connect the SSR to the controller's SSR output? This output is designed to switch the SSR on and off.

Could you draw a diagram of how items are connected please?
Yes, it is always in that range even when the heating is not on.
I can't fully understand how the oven works.
 
So to be clear - the voltage across the ssr terminals 3 and 4 is always in the range 22.3 - 22.8 V? It never drops to zero Volts even when the heating process is Off? This is surprising and not what one would expect.

Why will you not connect the SSR to the controller's SSR output? This output is designed to switch the SSR on and off.

Could you draw a diagram of how items are connected please?
What if I directly connected the SSR relay to the thermoregulator using terminals 11 and 12 (currently not used since the SSR is driven by the thermoregulator through the internal relay function of the thermoregulator) of the thermoregulator?

If I disconnect all the wires of the input and output of the SSR and to the input of the SSR 3+ and 4, I connect some wires that I am going to connect to terminal 11 and 12 of the thermoregulator, while in the output of the SSR I connect directly only the wires of the resistance? It might work?

I measured the direct current at the output of terminals 11 and 12 of the thermoregulator, it corresponds to 11.9 volts. Could it be fine for the relay as there is currently 22.6 volt current in use?
 

Attachments

  • foto25_.jpg
    121.1 KB · Views: 13
I still say you are beyond your abilities here. No shame in that.

Without a wiring diagram I feel we shall get nowhere.
 
What if I directly connected the SSR relay to the thermoregulator using terminals 11 and 12 (currently not used since the SSR is driven by the thermoregulator through the internal relay function of the thermoregulator) of the thermoregulator?

If I disconnect all the wires of the input and output of the SSR and to the input of the SSR 3+ and 4, I connect some wires that I am going to connect to terminal 11 and 12 of the thermoregulator, while in the output of the SSR I connect directly only the wires of the resistance? It might work?

I measured the direct current at the output of terminals 11 and 12 of the thermoregulator, it corresponds to 11.9 volts. Could it be fine for the relay as there is currently 22.6 volt current in use?
Yes. Ensure correct polarity, The minimum voltage is 3V and across 11 and 12 there is 12V. ssr input has to be greater than 3 and no more than 32V.
 
I have attached a picture showing you how to connect the ssr to the controller. MAke sure the SSR and controller are connected with + to + and - to -.
 

Attachments

  • PIDCONTROLLERROME.jpg
    298.3 KB · Views: 11
I have attached a picture showing you how to connect the ssr to the controller. MAke sure the SSR and controller are connected with + to + and - to -.
I solved the problem by directly connecting the thermoregulator to the SSR relay as you told me, now it works fine. Perhaps it was the rectifier bridge transformer circuit that failed, by directly connecting SSR and thermoregulator the transformer was bypassed. What do you think caused the failure? Before doing all this I also disconnected the thermoregulator from feeding the transformer through terminal 4, although the problem persisted, this shows that the thermoregulator works well. I also put some terminals on the connectors that I no longer use and I wrote the corresponding number on them, in case of a possible future use by fixing the transformer problem. The only thing is that it gets to 790 degrees in 2 hours and 20 minutes. I would need it to get to that temperature in 2 hours. If I put a fan on top of the SSR would I be able to reduce the time? When the oven was open and reached 500 degrees, the relay by touching it above had a temperature slightly above that of the environment. Then I had to close the panel and turn the oven to test it up to 790 degrees.
 

Attachments

  • photo_2022-07-04_20-50-37.jpg
    96.7 KB · Views: 4
  • photo_2022-07-04_20-50-37 (2).jpg
    129.8 KB · Views: 6
Installing a fan will not help. Why do you have to reach 800C in 2 hours? What difference does 20 minutes more have?
 
Installing a fan will not help. Why do you have to reach 800C in 2 hours? What difference does 20 minutes more have?
For a matter of saving time in the long cooking process of the flasks and the goldsmith casting. There are heat losses from the opening door and the hole where the oven exhaust pipe is, perhaps trying to contain them using ceramic fiber or other heat resistant materials I could reduce the time.
 
For a matter of saving time in the long cooking process of the flasks and the goldsmith casting. There are heat losses from the opening door and the hole where the oven exhaust pipe is, perhaps trying to contain them using ceramic fiber or other heat resistant materials I could reduce the time.
Please don't ignore the PID tuning advice.
You need to find out if the longer heating time is due to the controller "slowing down" the heating as set temp approaches.
or it may be that it's just the time it takes because of the thermal mass of the oven and the power of the heating element.

The controller has to be set to balance power "= speed of heating" vs overshoot. If you don't want to exceed 800 deg, it will take longer to heat the oven than if it doesn't matter about overshoot. See illustration below. Have you looked into these settings?
There's plenty on the web about this if you haven't investigated it already.
5CC6C99E-49CE-4DE7-80A2-DCB2023BB650.png
 

Here is a youtube clip which explains how to set up the controller initially and then to select auto tune (AT) to optimise how the oven heats up and then regulates its temperature. It is the same controller as the one you have although it has a different name.

Here is leaflet on your controller but I recommend you use the YouTube clip first.

https://images-na.ssl-images-amazon.com/images/I/91cH5fgtECL.pdf
 
Also, remember it could take 2 to 3 hours to tune if your set point is really high.
 
The computer inside the controller is making small changes to the P, I and D values and then seeing how the oven performs in terms of oven temperature PV and its error when compared with the desired or set temperature SV all over time. Iteratively it will be homing in on the P, I and D values which give the best oven temperature PV time performance. When it has arrived at these values any changes away from them will make the performance worse each time which is how the controller knows when to stop auto tune.
 
I should have said that in order for the auto tune to work you will need to cycle your oven from cold to hot to cold, a number of times for the AT function to work and the light to stop flashing, before you use the oven for business.

I also need you to confirm you have turned the derivative or d function on.
 
Good you have been looking at the controller's settings. Would you go through the steps as in the youtube video and report to me the settings you find? I can then tell you what to change or keep the same.

More immediately please me tell if you have set up 'InP' value as 'k' ( see at 5m57s) to tell the device you are using a thermocouple - and then tell me if the 'd' function is set to on or off (see at 6m57s).
 
AL1 and AL2 are over- and under- temperature limits to alert you if the oven goes to far above or below the set temperature. Would this be useful to you?
 
Good you have been looking at the controller's settings. Would you go through the steps as in the youtube video and report to me the settings you find? I can then tell you what to change or keep the same.

More immediately please me tell if you have set up 'InP' value as 'k' ( see at 5m57s) to tell the device you are using a thermocouple - and then tell me if the 'd' function is set to on or off (see at 6m57s).
The input signal is set to the type K thermocouple, which is the one actually present and which has been replaced. The variable "d" corresponding to the derivation time is set with the default value "30", in the manual it is written that if it were set to "0" the derivation would be closed. The variable AL1, on the other hand, is set to the default value "10". The AL2 variable is not present. SLL (setting of minimum set value) and SLH (setting of maximum set value) are the variables that, if set, put a minimum and maximum limit on the temperature that can be manually set on the thermoregulator display, I wonder: what is the difference between these variables and AL1? I never understood what AL1 was really for, is it perhaps an audible alarm that sounds when the temperature is reached?
 
I am wondering now whether your controller is not exactly the same as the one shown in the youtube clip but similar in many respects.

How long does the oven take now to reach 800C?

Please set d to 200 and let me know how the oven performs.

I did ask for all the controller settings in my earlier post.

I will have another search for the manual for your controller. All I could find before was a leaflet with brief details.

Are you using the oven now to melt gold?
 
Last edited:
I am wondering now whether your controller is not exactly the same as the one shown in the youtube clip but similar in many respects.

How long does the oven take now to reach 800C?

Please set d to 200 and let me know how the oven performs.

I did ask for all the controller settings in my earlier post.

I will have another search for the manual for your controller. All I could find before was a leaflet with brief details.

Are you using the oven now to melt gold?
I have not yet done the test of setting the variable 'd' to 200, however the auto tuning is still in operation, to get to 800 degrees the oven takes 2 hours and 27 minutes setting the temperature to 1000 degrees in order to make it rise continuously without being slowed down by the overshooting system. An anomalous thing I noticed is that if it reaches for example the temperature of 790 degrees and I set the temperature variable to be reached from 1000 to 790 to keep the temperature stable for ten minutes, I noticed a drastic drop, in 10 minutes it dropped to 736 degrees. The temperature maintenance system did not work, same thing happened to me when I dropped the temperature to 540 degrees and I set the temperature to be reached at 550 degrees, the temperature did not rise, I had to set 600 degrees to make it rise.
 
Thank you. I will study the manual and have a think. It really would help to know the settings which have been input since these determine the way the controller responds. :cool:
 
I have not yet done the test of setting the variable 'd' to 200, however the auto tuning is still in operation, to get to 800 degrees the oven takes 2 hours and 27 minutes setting the temperature to 1000 degrees in order to make it rise continuously without being slowed down by the overshooting system. An anomalous thing I noticed is that if it reaches for example the temperature of 790 degrees and I set the temperature variable to be reached from 1000 to 790 to keep the temperature stable for ten minutes, I noticed a drastic drop, in 10 minutes it dropped to 736 degrees. The temperature maintenance system did not work, same thing happened to me when I dropped the temperature to 540 degrees and I set the temperature to be reached at 550 degrees, the temperature did not rise, I had to set 600 degrees to make it rise.
I might be able to comment on what you have written if only I had the PID controller's current settings ...................

I have some ideas on how to proceed once I have the settings in front of me.

Are you writing and reading here in your first language?
 
Last edited:
I might be able to comment on what you have written if only I had the PID controller's current settings ...................

I have some ideas on how to proceed once I have the settings in front of me.

Are you writing and reading here in your first language?
Some variables in the manual are not present in the menu of my temperature controller. I list below the variables related to the PID that are present in the menu:

At, Al1, SC, P, I, d, t, rSt, LCy are present.
The variable 'At' is still set to Yes since I have activated auto tuning.
The variable 'P' is set to 20.0 instead of 30.0 as it would be by default.
All other variables are set with factory default values. You can see these values in the central 'Factory Defaults' column of the manual.

Al2, oH, rE, bUFF are not present.

English is not my primary language. I really appreciate your interest and thank you for your help.
 
Thank you. Armed with this information I will be back in touch. Meanwhile could you do a trial for me please? Please set the Control Period 't' value to 2 seconds suitable for an SSR - at the moment it is set to 20s required for a relay. Then disable the Derivative D function by setting it to 0. Because the oven has a high thermal capacity and hence is slow to change in temperature the D function will not be that useful for temperature regulation. How does the oven perform now when the set Value SV is 800C? eg time to first reach 800C, overshoot and undershoot temperatures, time to 'stay at' 800C. Is it 'better' than when D is selected with a value of 20? Keep the AT selected.

The Control Period Value t being set to 20 is wrong because you are using an SSR which can switch more frequently than a relay without damage. I am pondering that your oven only needs PI control not PID. The reason the AT may be taking a long time or even not succeeding is that it assumes the controller has dual action ie it can raise the temperature and also lower the temperature by adding or removing energy. Of course the element can only add energy not remove it. For the oven to cool it needs heat energy to be removed and this must rely on it flowing out of the oven which I assume has reasonably well insulated walls so it is going to take more time to reduce the temperature by say 50C than to raise it by 50C - the controller does nothing but wait with a zero output and element off when the actual temperature PV has to decrease.

I am finding this problem interesting and a nice revision of the control engineering I learned/forgot decades ago. :)
 
Last edited:
Thank you. Armed with this information I will be back in touch. Meanwhile could you do a trial for me please? Please set the Control Period 't' value to 2 seconds suitable for an SSR - at the moment it is set to 20s required for a relay. Then disable the Derivative D function by setting it to 0. Because the oven has a high thermal capacity and hence is slow to change in temperature the D function will not be that useful for temperature regulation. How does the oven perform now when the set Value SV is 800C? eg time to first reach 800C, overshoot and undershoot temperatures, time to 'stay at' 800C. Is it 'better' than when D is selected with a value of 20? Keep the AT selected.

The Control Period Value t being set to 20 is wrong because you are using an SSR which can switch more frequently than a relay without damage. I am pondering that your oven only needs PI control not PID. The reason the AT may be taking a long time or even not succeeding is that it assumes the controller has dual action ie it can raise the temperature and also lower the temperature by adding or removing energy. Of course the element can only add energy not remove it. For the oven to cool it needs heat energy to be removed and this must rely on it flowing out of the oven which I assume has reasonably well insulated walls so it is going to take more time to reduce the temperature by say 50C than to raise it by 50C - the controller does nothing but wait with a zero output and element off when the actual temperature PV has to decrease.

I am finding this problem interesting and a nice revision of the control engineering I learned/forgot decades ago. :)
I did the test with the configuration you suggested, what I noticed is that after 2 hours the temperature was at 750 degrees instead of 764 as in the other measurement with the setting at 1000 degrees and without the configuration you suggested. I don't understand why there is this 14 degrees difference. I don't think it could be the resistance that has degraded considering that it has been changed by a specialized technician a couple of months ago. I didn't always watch the oven continuously so I don't know if the heating stopped sometime, but when I took the measurement it was on.

The second thing I noticed was that at 760 degrees the heating turned off, after which it dropped to 753 degrees and stopped there; after a few minutes it began to rise. Then it reached 764 and switched off again, after that the temperature dropped and after a while it started again reaching 763 degrees, then it did the same thing stopping at 766. In 2 hours and 28 minutes it was at 766 degrees, instead in the measurement made days ago (with the temperature set at 1000 degrees) reached 800 degrees in 2 hours and 27 minutes. Since it seemed impossible that the temperature would rise more, I decided to finish the test.
 
Thank you. Tuning the controller is I regret to say largely 'trial and error'.

Next let us reduce the I value from 210 to 180. Reducing this time increases the integral action I and helps to reduce the error quicker as the temperature PV gets closer to the set value SV, but it can also increase oscillations so some more trial and error with this value. The integral action makes up for the reducing drive from the P proportional action since P depends on the error and the error is decreasing.

Please use 800C as the set value from the moment you turn on the oven. We are attempting to tune the system to achieve 800C 'quickly' not 1000C. If you set SV at 1000C the controller does not use proportionate control until close to 1000C and the temperature enters the proportional control band centered around 1000C. We want proportionate control to kick in as the oven nears 800C. The SV value determines the midpoint of the proportional band.

1658134261022.png


Please understand the oven and controller has two 'behaviours' working at the same time. From cold to set value temperature the oven is operating in its transient mode since there is the biggest change in temperature. As the oven temperature reaches the set value the transient behaviour should reduce and the oven enters its steady state behaviour only making small changes to keep the temperature near to 800C.

Transient response - Wikipedia - https://en.wikipedia.org/wiki/Transient_response#:~:text=In%20electrical%20engineering%20and%20mechanical,the%20equilibrium%20of%20the%20system.
 
Last edited:
Thank you. Tuning the controller is I regret to say largely 'trial and error'.

Next let us reduce the I value from 210 to 180. Reducing this time increases the integral action I and helps to reduce the error quicker as the temperature PV gets closer to the set value SV, but it can also increase oscillations so some more trial and error with this value. The integral action makes up for the reducing drive from the P proportional action since P depends on the error and the error is decreasing.

Please use 800C as the set value from the moment you turn on the oven. We are attempting to tune the system to achieve 800C 'quickly' not 1000C. If you set SV at 1000C the controller does not use proportionate control until close to 1000C and the temperature enters the proportional control band centered around 1000C. We want proportionate control to kick in as the oven nears 800C. The SV value determines the midpoint of the proportional band.

View attachment 99614

Please understand the oven and controller has two 'behaviours' working at the same time. From cold to set value temperature the oven is operating in its transient mode since there is the biggest change in temperature. As the oven temperature reaches the set value the transient behaviour should reduce and the oven enters its steady state behaviour only making small changes to keep the temperature near to 800C.

Transient response - Wikipedia - https://en.wikipedia.org/wiki/Transient_response#:~:text=In%20electrical%20engineering%20and%20mechanical,the%20equilibrium%20of%20the%20system.
Should I leave the other variables "d = 0", "t = 2" and "AT = yes" unchanged and change only the variable "I" from 210 to 180?

Could I do the test by entering a lower temperature like 500 degrees or does it always need to set 800 degrees? Putting 500 degrees in an hour I would have the response and I could do the test faster, otherwise like the previous test I will proceed by setting SV to 800.
 
Should I leave the other variables "d = 0", "t = 2" and "AT = yes" unchanged and change only the variable "I" from 210 to 180?

Could I do the test by entering a lower temperature like 500 degrees or does it always need to set 800 degrees? Putting 500 degrees in an hour I would have the response and I could do the test faster, otherwise like the previous test I will proceed by setting SV to 800.
Yes leave those variables unchanged. Only change I. You can use 500C for the test.
 
Tried skipping through quickly so sorry if already mentioned, the colour coding on your thermocouple wires could be from a different global zone thus identified incorrectly, assuming the controller has been configured for the therm' type it is monitoring, not doing so will give the wrong feedback voltages and the wrong temperatures. Type K And J are commonly used but must be correctly input into the PID controller fir it to Interpret what the thermocouple resistance feeds back is.
 
Last edited:
Thermocouple Cable Colour Codes and Tolerances - TC Ltd - https://www.tc.co.uk/thermocouple-information/thermocouple-colour-code.html

The k type thermocouple has red and green wires which would indicate it is using the German colour code red for plus and green for minus. This is how it is connected to the controller. See #49.

mdkmdk - could you send me details of the thermocouple please? Is it made in Germany. Do the red and green wires go all the way to the thermocouple or have you joined the thermocouple wires to the red and green wires which go to the controller?

If you have a small permanent magnet and hold it near the red wire and then the green wire the wire which is most magnetic is the negative lead.
 
Last edited:
Yes leave those variables unchanged. Only change I. You can use 500C for the test.

I did the test you suggested by changing the variable 'I' and setting it to '180':
The oven reached the temperature of 475 degrees and the heating turned off.
It dropped to 486 degrees while the heating was off.
The temperature dropped, and at 474 degrees it started again.
The temperature dropped to 466 degrees, and the heating turned on again.
The heating turned off at 477 degrees.
Then I finished the test as it never seemed to reach 500 degrees.

Thermocouple Cable Colour Codes and Tolerances - TC Ltd - https://www.tc.co.uk/thermocouple-information/thermocouple-colour-code.html

The k type thermocouple has red and green wires which would indicate it is using the German colour code red for plus and green for minus. This is how it is connected to the controller. See #49.

mdkmdk - could you send me details of the thermocouple please? Is it made in Germany. Do the red and green wires go all the way to the thermocouple or have you joined the thermocouple wires to the red and green wires which go to the controller?

If you have a small permanent magnet and hold it near the red wire and then the green wire the wire which is most magnetic is the negative lead.
Tried skipping through quickly so sorry if already mentioned, the colour coding on your thermocouple wires could be from a different global zone thus identified incorrectly, assuming the controller has been configured for the therm' type it is monitoring, not doing so will give the wrong feedback voltages and the wrong temperatures. Type K And J are commonly used but must be correctly input into the PID controller fir it to Interpret what the thermocouple resistance feeds back.

A few months ago I also changed the thermocouple. Before replacing it I did the test with the magnet and it showed that it was a type K thermocouple. Later I replaced it with a new one of the same type, obviously K. I remember that before changing it I inquired about the colors of the wires and it emerged that they probably refer to the German colour code.
 
Last edited:
First it seems to me the controller is working and that 25C or so away from 500C seems to me quite good after the initial period of heat up. Would you please leave for longer and find out how close the oven temperature settles to 500C?

Jogged by Westward10's post I am thinking about the error in measuring the oven temperature PV introduced by the connection of the thermocouple's red and green leads to the metal terminals on the back of the controller. These two connections are the other half of the thermocouple circuit. A thermoelectric circuit has a hot sensing end thermocouple and a cold reference end thermocouple. The combined circuit produces a voltage/current proportional to the difference between the temperatures of each end. See:

Thermocouple Cold (Reference) Junction Compensation - https://blog.beamex.com/thermocouple-cold-junction-compensation

The reference thermocouple made by the terminal connections will reduce the voltage produced by the hot end. Thus temperature measurements by the hot end thermocouple will be seen by the controller as lower than they actually are. The controller has a an SC value for correcting sensor measurement errors so I will come back to you later about entering a value other than 0.

The problem is that the reference temperature 'cold junction' is actually getting warmer and warmer as the oven does because the terminals are enclosed in a space near the oven and ssr.

How accurate does the temperature need to be for your purpose?
 
First it seems to me the controller is working and that 25C or so away from 500C seems to me quite good after the initial period of heat up. Would you please leave for longer and find out how close the oven temperature settles to 500C?

Jogged by Westward10's post I am thinking about the error in measuring the oven temperature PV introduced by the connection of the thermocouple's red and green leads to the metal terminals on the back of the controller. These two connections are the other half of the thermocouple circuit. A thermoelectric circuit has a hot sensing end thermocouple and a cold reference end thermocouple. The combined circuit produces a voltage/current proportional to the difference between the temperatures of each end. See:

Thermocouple Cold (Reference) Junction Compensation - https://blog.beamex.com/thermocouple-cold-junction-compensation

The reference thermocouple made by the terminal connections will reduce the voltage produced by the hot end. Thus temperature measurements by the hot end thermocouple will be seen by the controller as lower than they actually are. The controller has a an SC value for correcting sensor measurement errors so I will come back to you later about entering a value other than 0.

The problem is that the reference temperature 'cold junction' is actually getting warmer and warmer as the oven does because the terminals are enclosed in a space near the oven and ssr.

How accurate does the temperature need to be for your purpose?
From 475 to 500 degrees it would take a long time since the heating stops constantly.

I completely redone the panel when the resistance was changed and I made the preparation for the new thermocouple since it did not have a bolt on which to stand. I soldered it at a slight angle to prevent the thermocouple wires from getting close to the resistor wires and the oven exhaust pipe.

It is important for me that the temperature is accurate and real and that it reaches 800 degrees as soon as possible.
 

Attachments

  • photo_2022-06-16_23-12-35.jpg
    120.1 KB · Views: 16
  • photo_2022-07-19_19-08-15.jpg
    118.2 KB · Views: 14
Last edited:

Reply to SSR relay problem solution in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I’m not an electrician and I have a question in relation to Dimplex Duo300n. Some background information: a couple of months ago I have...
Replies
34
Views
7K
Hi, I have been trying to solve this problem for months now. I work as an Electrical Engineer in a tunnel project, we will use TBM machine to...
Replies
13
Views
2K
My view on life, in any field, is not to produce more but to consume less. Everybody told me this is a very eccentric weird mentality. Perhaps...
Replies
12
Views
2K
S
Hi everybody. I am here asking for your help as I am not able to come up with a solution. My system is done this way: I have the main house power...
Replies
9
Views
3K
sampei
S
Please take some time to read through this. It is written by Widdler's father. I found it on a governement website.. It certainly speaks my mind...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock