Hi all.

I'm currently renovating a house and have one particular requirement I'd like, if possible, sme suggestions.

One of the things I would like to do is put in stair edge lighting. I have found some nice ULV LED spots that I want to put into the stringer on the wall side. Now this is only 15mm deep, so, they have to be very low profile.

If this was the total requirement I would have no problems, but... You all knew a but was coming!

What I want to do is have them switched at the top and bottom by PIR's at floor level. this has a couple of problems. So, suggestions welcome.

- I have very little depth so was looking at using something like these:

ABB 6811 EB-500 - http://new.abb.com/products/ABB.DEBJE6800-0-2517

PDFMMINIL - 360° Flush Mount Linkable Mini PIR Sensor | Timeguard - http://www.timeguard.com/products/light/pir-presence-detectors/360-flush-mount-linkable-mini-pir-sensor

But they are too deep.

The actual requirements are:

- They need an ambient light sensor, so, only activate below 50-70 lux, and, have a timer set to about 1 min.

- I'm worried about strobing with the top and bottom triggering when someone walks up the stairs.

- To prevent the sensons conflicting I was thinking of actually using the PIR's to trigger a timer such as the below.

Time Switches Timers - http://www.hager.co.uk/product-catalogue/energy-distribution/modular-devices/timers/time-switches/38549.htm

Electronic Time Delay Switch IP20 - https://www.toolstation.com/shop/Electrical/d190/Wired+Timers/sd2660/Electronic+Time+Delay+Switch+IP20/p17352

This would just then re-trigger the timeswitch / relay component and prevent the strobing.

Open to any opinions on the viability or method. Ideally I'd like to do everything at ULV, but, appreciate this may not be possible.

Many thanks for any help, and, time.

Regards

Dave
 
Hi all.

I'm currently renovating a house and have one particular requirement I'd like, if possible, sme suggestions.

One of the things I would like to do is put in stair edge lighting. I have found some nice ULV LED spots that I want to put into the stringer on the wall side. Now this is only 15mm deep, so, they have to be very low profile.

If this was the total requirement I would have no problems, but... You all knew a but was coming!

What I want to do is have them switched at the top and bottom by PIR's at floor level. this has a couple of problems. So, suggestions welcome.

- I have very little depth so was looking at using something like these:

ABB 6811 EB-500 - http://new.abb.com/products/ABB.DEBJE6800-0-2517

PDFMMINIL - 360° Flush Mount Linkable Mini PIR Sensor | Timeguard - http://www.timeguard.com/products/light/pir-presence-detectors/360-flush-mount-linkable-mini-pir-sensor

But they are too deep.

The actual requirements are:

- They need an ambient light sensor, so, only activate below 50-70 lux, and, have a timer set to about 1 min.

- I'm worried about strobing with the top and bottom triggering when someone walks up the stairs.

- To prevent the sensons conflicting I was thinking of actually using the PIR's to trigger a timer such as the below.

Time Switches Timers - http://www.hager.co.uk/product-catalogue/energy-distribution/modular-devices/timers/time-switches/38549.htm

Electronic Time Delay Switch IP20 - https://www.toolstation.com/shop/Electrical/d190/Wired+Timers/sd2660/Electronic+Time+Delay+Switch+IP20/p17352

This would just then re-trigger the timeswitch / relay component and prevent the strobing.

Open to any opinions on the viability or method. Ideally I'd like to do everything at ULV, but, appreciate this may not be possible.

Many thanks for any help, and, time.

Regards

Dave
ULV do you mean ELV, SELV
 
Something like this?
Screen Shot 2017-07-13 at 11.19.08.jpg
 
Look at deck light kits for the lights.

I dont know why you think you will get strobing or timing issues from using 2x pirs?

And if depth of the pir is a problem why not put it in the step so theres a void?
 
I’ve never seen a door with 4 hinges - that’ll be the strongest bit then!
That your old gaff SWD?
Thats was a property that I owned then redeveloped and sold this year. Also double Banham locks and a decent door frame.

You must have seen the photos as I have had the pee pee taken out of me.........
 
Ive only seen the one of the kitchen/diner the size of a football pitch - this time I'm genuinely interested! It a good picture of the stairs and door (like the colour too) I'm full of compliments today!
Thats was a property that I owned then redeveloped and sold this year. Also double Banham locks and a decent door frame.

You must have seen the photos as I have had the pee pee taken out of me.........
 
If you go the pir route the timeguard one above with a slave module will be fine, we have fitted a few of these with no problems.
 
Fit small microwave sensors under the stairs, they should detect through the timber work without any issues, you can put one at the bottom step facing outwards and one under the top step facing upwards
 
Thanks.

Been a busy weekend. SWA for the garden as it was nice.

The top photo is exactly what I was looking for as an end result. I assume the wiring in under the stairs themselves? I have a U shaped half landing that may be problematical, but, everything has a solution.

I'll have a look at both the PIR and microwave routes. Does anyone have a link to the microwave switches?

Also, as said above, love the colours and stairs in the photo.

Thanks everyone for the help.

Regards

DaveA
 
My fittings where supplied by Mr Resistor, as it was a full refurb the cabling went in through the wall partitions as I don't think the neighbour would have been pleased with wiring in her flat down below.
 

Reply to Stair Lighting unusual switching in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Driven by the recent colossal hikes in the cost of electricity I hit upon the wizard wheeze of replacing some of the existing LED bulbs in our own...
Replies
2
Views
930
I have searched online, have a few ideas, but I'm getting old... Basically, I have a bin store which has light on the ceiling...you can use the...
Replies
10
Views
2K
currently I have LED tape inside a duffuser running up the length of my stairs controlled by two standalone PIR sensors (one top, one bottom) I...
Replies
4
Views
1K
I have a ceiling PIR motion sensor fitted in my cloakroom that sometimes causes my kitchen lights to turn off when the sensor is triggered...
Replies
16
Views
3K
Hi, I had my home entirely rewired 5 years ago had some outside lights added to the front of the house. I’d now like to add these into my...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock