Currently reading:
Star delta fan wiring help please

Discuss Star delta fan wiring help please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

G

Goldygoldy

Hello there

have been asked to fault find on a clients 3 phase star delta fain in a grain store.

the client purchased the fan second hand and I have power across the contractors but no power on the out going side.

no wiring diagrams either.

Can anybody give me some in what to check for and a website for a wiring diagram would be great (already googled it)

thanks in advance
 

Attachments

  • image.jpg
    172.7 KB · Views: 65
  • image.jpg
    165.2 KB · Views: 58
  • image.jpg
    185.6 KB · Views: 53
Hello there

have been asked to fault find on a clients 3 phase star delta fain in a grain store.

the client purchased the fan second hand and I have power across the contractors but no power on the out going side.

no wiring diagrams either.

Can anybody give me some in what to check for and a website for a wiring diagram would be great (already googled it)

thanks in advance
obvious question first, have you checked the fuses
 
I didn't check them no, there's been some cables just cut at the bottom
RHS of the control box (t5) like I said there is power at contractors.

just strange why some cables have been cut
 
Hello there

have been asked to fault find on a clients 3 phase star delta fain in a grain store.

the client purchased the fan second hand and I have power across the contractors but no power on the out going side.

no wiring diagrams either.

Can anybody give me some in what to check for and a website for a wiring diagram would be great (already googled it)

thanks in advance
Have you inspected the start stop system to se if there is a wire loose or a line fuse blown, or a stop button pressed in?
 
Hi Goldy - welcome to the forum :)

A few questions first :-

- Have you any experience with motors and control systems?
- If your self employed have you expressed to your insurance you are working on such equipment otherwise you may only be insured for single phase installs.
- can you take a photo front on so we can see the cut wires and where they are connected to or where they might have gone.
- what happened to the previous fan - the issue that led to its failure may be present still.

Be very careful here unless you are competent in such systems you shouldn't really get involved with them without supervision, a simple mistake with such a sized fan can have costly results, its sometimes better to be honest than get involved with equipment you have no knowledge of :thinking:
 
Hi Goldy - welcome to the forum :)

A few questions first :-

- Have you any experience with motors and control systems?
- If your self employed have you expressed to your insurance you are working on such equipment otherwise you may only be insured for single phase installs.
- can you take a photo front on so we can see the cut wires and where they are connected to or where they might have gone.
- what happened to the previous fan - the issue that led to its failure may be present still.

Be very careful here unless you are competent in such systems you shouldn't really get involved with them without supervision, a simple mistake with such a sized fan can have costly results, its sometimes better to be honest than get involved with equipment you have no knowledge of :thinking:



Thanks for the reply...
i do have experience although along time ago I used to maintain air handling units for sainsburys
im also insured for three phase working

i have left the site now however the cut wires look as if they was in terminals 97 and 98 just below the first contractor.

the previous fans shaft went on it so they replaced it with this new one.
The new fan already came with the control box
 
Thanks for the reply...
i do have experience although along time ago I used to maintain air handling units for sainsburys
im also insured for three phase working

i have left the site now however the cut wires look as if they was in terminals 97 and 98 just below the first contractor.

the previous fans shaft went on it so they replaced it with this new one.
The new fan already came with the control box

That's fine.. just checking we haven't got a domestic brigade stepping into areas he shouldn't be in ...

Thats sorted now - the wires that may have been in 97 an 98 are usually signal wires to operate maybe a trip lamp, buzzer, relay etc anything that may have operated if the overload tripped basically.

Now back to the starter, do you get any operation of the star/deta contactor when you press the start button?
cf1 and cf2 are your fuses for the 400v control circuit are these both good, if not then you need to figure out why one or both have blown - you could follow the control cables through the start/stop button etc and just check for flash marks or damaged/loose wires.

Ask the customer the history behind having to buy a new fan, it may be the case it was mis-diagnosed and in fact the controls were faulty.
 
Last edited:
Hi Goldy , could you post more detailed photo's ?
At the moment I would guess that they are part of a remote start setup , but a guess is all it is without more detailed photo's .

And Darkwood is not scaremongering with his advise about it getting costly , it looks like you have a Brooke Cromton 18kw stand alone starter there . Those contactors are now obsoleat , and a replacement unit will be around £400 +vat
 

Reply to Star delta fan wiring help please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock