Discuss Steel framed workshop. in the UK Electrical Forum area at ElectriciansForums.net

bigspark17

-
Arms
Reaction score
718
hi have a large workshop to price, standard stuff, but i noticed that the steels 4 of which are not bolted together so in a sense offer 4 earth fault paths, i would plan to export suitable earth/cpc conductor from house to bond the frame but should i bond each steel back to consumer unit(in workshop) or link them together or just bond 1.?
Usually in buildings like this i see that steels are connected together with other steels but on this occasion its timber between.
If i havent explained well i appoligise, but intrested to hear thoughts.

Bigspark17
 
test each section of the steel to see if it's extraneous i.e. IR test to your MET. if the reading is <22k Ohms, bond them.
 
I'm assuming the steels are frames concreted into the ground and hence almost certainly extraneous.....but then again maybe just RSJ's???....confirm please Bigspark.
 
I'm really interested to see what the guru's say about this one, because I'm struggling to even visualise it.
Would have been nice to see a picture.

Im sorry my post is not clear but i thought it might not lol. Its about 20M long with 4 x steel A frames but the A frames are segregated, usually i would see cross sections bolted together inbetween A frames thus making them one large extraneous part and only require 1 bond.

You will have to link the steels together with a continuous bond. Don't forget the cpc in the sub to the MET at the intake will need to be at least of the minimum size required for bonding or a separate bond will need to be installed

Yes the sub will be a 16mm 3c, 100A DNO in house so cpc adequate for bonding conductor & cpc house>workshop.

My gut is to link all with an unbroken bonding conductor (10mm) from workshop cu through each steel, just feel is slightly overkill as cant be much Earth fault path resistance from one steel to next.

test each section of the steel to see if it's extraneous i.e. IR test to your MET. if the reading is <22k Ohms, bond them.

Yes the huge steel frame buried deep in the ground is extraneous...
 
Just a thought,but what type of structure,are these A frames?
If they are made up of bolted or riveted sections,you may find you are not bonding all parts,dependant on where you stick your eye terminal.

An assessment of the merits of your bonding,may be needed :)

Older lattice type steelwork,used in buildings,bridges,over-head cranes,etc is notorious for it's continuity mood-swings.
 
Just a thought,but what type of structure,are these A frames?
If they are made up of bolted or riveted sections,you may find you are not bonding all parts,dependant on where you stick your eye terminal.

An assessment of the merits of your bonding,may be needed :)

Older lattice type steelwork,used in buildings,bridges,over-head cranes,etc is notorious for it's continuity mood-swings.

Bolted brand new A frames, yes they will give full continuity.

What do you mean an assesment of my bonding merits may be needed? If they are extraneous which they are then they need bonding, but my original thought was if you main bonded one wouldnt that be enough?

Im not bonding a bridge or a crane its a steel frames workshop!
 
Bolted brand new A frames, yes they will give full continuity.

What do you mean an assesment of my bonding merits may be needed? If they are extraneous which they are then they need bonding, but my original thought was if you main bonded one wouldnt that be enough?

Im not bonding a bridge or a crane its a steel frames workshop!

Hi,your first line is the answer,then.

My reference to bridges and cranes,was in regard of the type of construction,of steel sections in older pre-fabs,Romney buildings,etc.

I have seen similar structures,with additional supplementary bonding,fitted correctly,frame to frame,stud welded eye terminals,no breaks... but varying or poor readings,as you test along and away,from the bonding.

So,in effect,bonded,but not effectively. It would be a situation such as this,that may require a bonding merit assessment :)
 
i just got back from specsavers, got new glasses, steel frames. should i use 6.0mm or 10.0mm bonding cable to my pacemaker?
 
i just got back from specsavers, got new glasses, steel frames. should i use 6.0mm or 10.0mm bonding cable to my pacemaker?

Now,you,more than anybody,knows that the correct thing to do,is to find out if those frames are required to be bonded,or just a pair of spectacles.....get your IR tester,and...
 
Now,you,more than anybody,knows that the correct thing to do,is to find out if those frames are required to be bonded,or just a pair of spectacles.....get your IR tester,and...
is that tested in the box, or on me yed?
 

Reply to Steel framed workshop. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Some friends are setting up a metal workshop inside a shipping container, on site at a commercial building that rents out studios, workshop space...
Replies
9
Views
2K
Hi customer had installed a 10m awning that is secured to a very substantial 6” box steel frame, concreted in either end - large goal post if you...
Replies
7
Views
2K
Was wondering if the gurus can critique and/or provide recommendations on my plan to install two sub-panels in a (50'x100') 5,000 sq ft steel...
Replies
2
Views
1K
Hello All, I am working on a kitchen extension which has 3 Universal Beams bolted together which sit on block-work. There is no direct connection...
Replies
12
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock