Jimmyb

Im I missing something ?

been checking 2 x ring finals yesterday and found the following results :-


R1 Rn R2 R1+R2

0.36 0.36 0.45 0.18 for length of est circuit r1&rn values seem about right

0.47 0.47 1.38 0.35 cant check length with this but most be loose cpc somewhere

I thought well ill check for loose connection on both and found nothing, well I checked all accessible one/what I could find

anyone else got thoughts on this please there is only loose damaged connection
 
You're 95% correct. I always have an issue with the term loose connection. It's poor connection to me.

It doesn't necessarily mean theres a 'loose connection' anywhere - as you've pointed out you can't find it. You could literally open every single socket and find everything tight.

It could mean that the insulation of the cable is nicked instead of the copper at one of the connections somewhere on the ring.

It could also mean theres a socket that you haven't found that has a 'loose connection' or even a damaged cable end thats just about hanging on in there at the terminal.

But yes you're correct, it's a 'loose connection' as you put it somewhere.
 
Sounds like more than a loose connection looking at that R1+R2 figure on the first RFC. Daz
 
Is this a new installation or old. Have you checked R1 + R2 at terminal connections at back of sockets as opposed to socket outlet fronts, as results can vary considerably due to tarnishing and wear ?.
 
The R2 value can't be 'better' if it's incorrect though can it. Daz
 
I would suggest that ring 2 may have a poor connection in an inaccessible joint box, or the cable type being older may have a smaller cpc than you expect.
 
Have not read all of the post but firstly id be looking for any noticable alterations and starting there. It will more than likely be a poor connection in a junction box under floor boards or connections made of behind a kitchen unit for example. Or try following a logical route using "long lead" method and notin any considerable rises in test values to pin point the location of the fault
 
try following a logical route using "long lead" method and noting any considerable rises in test values to pin point the location of the fault
Follow a logical route, hmm... this is not always the case; I was doing this and going from socket to socket and got the rise in resistance logically between two sockets on the same wall 2 m apart, could not find the fault, then eventually took up the floor and found the ring went from one socket off to the end of the house, round the kitchen, upstairs, into the loft, back to the kitchen opposite wall through three more sockets and eventually back down to the other socket!
Obvious really when you (fail to) think about it.
 
Follow a logical route, hmm... this is not always the case; I was doing this and going from socket to socket and got the rise in resistance logically between two sockets on the same wall 2 m apart, could not find the fault, then eventually took up the floor and found the ring went from one socket off to the end of the house, round the kitchen, upstairs, into the loft, back to the kitchen opposite wall through three more sockets and eventually back down to the other socket!
Obvious really when you (fail to) think about it.

Upon finding nothing you should of thought 'maybe thats not the cable route' and followed the "non-logical" route :)
 
Follow this lack of logic!
Illogical ring.jpg
 

Reply to Strange loop values in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
933
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
Replies
13
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock