Discuss Strange voltage and power factor values and installation issues in the UK Electrical Forum area at ElectriciansForums.net

kasemu

DIY
Reaction score
3
Hi,
We have installed 2 meters (each meter is a 3 phase meter) for sub-metering in a residential house (1 phase installation per apartment). One of the meters, after correcting installation, works fine now. The other one, in my opinion measures strange voltage values. We had since the begining connectivity problems with this meter (it uses NB-IoT technology). Please see the graphs of the various parameters the meter is measuring.

The electrician insists that there is nothing wrong with the installation of the second meter. However, I found discrepance between what the Ferraris meter measures (utility) and the smart meter measures. This discrepance together with some strange dashboard values makes me suspect there is something wrong. With the Ferraris meter we get 17 kWh for a few days time period and with the smart meter we get 21 kWh for exactly the same period of time.

The company that sold us the meter told me the electrician should check installation again and this is quite problematic as he was already several times there. They say "the problem with the installation is not on the part of the connection on the meter, the connections on the meter are correct. The problem is if the phase that is connected on PIN 1 is the same as CT 1 is measuring.
That is why we need to know if the CT 1 that measures Load 1 has the same reference voltage connected in Pin 1- (Phase 1)".

Since I am not in the electricity field, I am not sure what he means with "reference voltage". Does he mean the electrician needs to check that the voltage of Load 1 that measures CT1 is the same as the voltage connected in Pin1?

Thanks in advance
 

Attachments

  • Screenshot (129).png
    203.9 KB · Views: 19
  • Screenshot (130).png
    146.1 KB · Views: 16
  • image (8).png
    2.1 MB · Views: 21
I think it is simply referring to the same problem as you had with the other meter, i.e. that the voltage input was measuring one phase while the current transformer was measuring another. I don't think that applies here as the readings are not so outlandish.
 
I think it is simply referring to the same problem as you had with the other meter, i.e. that the voltage input was measuring one phase while the current transformer was measuring another. I don't think that applies here as the readings are not so outlandish.
I agree. The point is that the electrician insisted saying that his installation is correct. I will have to contact him again and say that it does not really look correct and he should double check.

Could you kindly explain what do you mean by "I don't think that applies here as the readings are not so outlandish." Thank you - I am not english native speaker.
 
I do not think that the current and voltage measurements are out of phase in this particular installation, because that usually causes the readings to be complete nonsense as they were on the other meter, not just of poor accuracy. I don't have time now to look more closely at the plots.
 
Please would you send photos so I can see what is in the blue circles?

Are the two apartments connected to the same phase L1; or to L1 and L2.

The meter outputs look fine to me apart from the voltage plot. It seems odd that the three voltage plots (red, blue and green) are identical - superimposed on each other. One would expect some variation between them at the scale of this plot. This would indicate that the L1, L2 and L3 voltage references for the meter are provided from one of the three phases.

One can see a periodic load turning on and off - is there a fridge or freezer? The low power factor is when most of the apartment loads are off or in standby so not consuming real power - the background reactive power is 'consumed' by any transformers inside electrical items eg: door bell or small motors in say time clocks which remain constantly energised. When real power is consumes it so much greater than the background reactive power that the power factor improves. ( Power Factor = Real Power/Apparent Power)
 

Attachments

  • Inkedimage (8)_LI.jpg
    1 MB · Views: 11
Please would you send photos so I can see what is in the blue circles?

Are the two apartments connected to the same phase L1; or to L1 and L2.

The meter outputs look fine to me apart from the voltage plot. It seems odd that the three voltage plots (red, blue and green) are identical - superimposed on each other. One would expect some variation between them at the scale of this plot. This would indicate that the L1, L2 and L3 voltage references for the meter are provided from one of the three phases.

One can see a periodic load turning on and off - is there a fridge or freezer? The low power factor is when most of the apartment loads are off or in standby so not consuming real power - the background reactive power is 'consumed' by any transformers inside electrical items eg: door bell or small motors in say time clocks which remain constantly energised. When real power is consumes it so much greater than the background reactive power that the power factor improves. ( Power Factor = Real Power/Apparent Power)
Thanks a lot for the detailed feedback!
I will not be able to send other photos soon, but I am asking directly the electrician about the connections in the blue circles as well as the phases connected to the apartments. I shoud also be able to provide more feedback on the voltages - you are right that is odd!
 
I do not think that the current and voltage measurements are out of phase in this particular installation, because that usually causes the readings to be complete nonsense as they were on the other meter, not just of poor accuracy. I don't have time now to look more closely at the plots.
Allright - thanks.
 

Reply to Strange voltage and power factor values and installation issues in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am working at a site with around 100 of these meters installed on various loads. Doing an audit, we found that most of the meters were recording...
Replies
2
Views
813
Hi All, I've installed a Lorex doorbell recently, but it is not turning on. I did some tests using a multimeter and this is what I found...
Replies
5
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi everyone, I need some help with an electrical issue I'm experiencing. I recently created a new circuit for an electric oven at my friend's...
Replies
7
Views
2K
Hi. Not sure if it's the right place to ask, so won't be upset if it gets removed. Apologies if the terminology (PEN/PME/etc) is used...
Replies
44
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock