Discuss Street lighting causing RCD to trip? in the Australia area at ElectriciansForums.net

P

Ponty Massive

Evening all,

Had a call today from a customer I did a job for a few months back. I went in to install a socket for them, only to find that the circuit had been put on the non-rcd side of the board (16th board). Asked the woman if she had a copy of the certificate when she had the board changed, which she did.

The guy who installed is a part P spark. She had the board changed because she had a new bathroom with jucuzzi. After having the board changed, the RCD would trip now and again for no reason. The original spark came back and just moved the mcb (which was also powering the jacuzzi) to the non-rcd side and like magic the problem went!!

I fitted the socket and moved the mcb back to the protected side and asked them to keep an eye on it, and let me know if it goes again.

Had a call today saying it has tripped about 3 times in the last 2 weeks, but they seem to think it is happening when the street lights come on. They assured me they were just sat in the room watching TV and when the street lights came on it tripped?

Has anyone else come across this problem before?
 
Upstream tranisants/noise can trip down stream rcds, difficult to say if this is your problem.

Dno may monitor supply if this is what you think may be the case.
 
Thanks Chris, did think of that, but why would it stop tripping when the other spark moved the MCB. I think it must be that specific circuit, but they assured me nothing had been operating, only the street light switched on??
 
It could be a needle in a haystack situation mate. Possibly something they are plugging in at that time? 3 times is really intermittent.
 
I've heard of ballasted street lights causing nuisance tripping but I haven't heard of a solution. I'm not sure if it would be a harmonics issue with the lighting switchgear. I know some RCD's are more prone to this type of nuisance tripping than others.

I've attached a pdf that might give you some ideas.

View attachment DemystifyingRCDs.pdf
 
Thanks all, Yeah I'll start by changing the RCD and see where we go from there. With it being so intermittant, it could take some time.

Cheers all !!
 
I know this may sound daft but have you checked the connections where the bus bar fits into the MCB's , ive come across this situation and found that the grip terminal for the mcb had missed the bus bar and was resting against it it tripped the RCD about 20 mins after the heating came on , i know its a daft one but may be worth checking also is the Ze ok i have had this caused by the neutral going down on the supply which caused the RCD to trip
 
They are on holiday at the moment, should be back next week. I'll have a look and try all your suggestions, Nickblake it's normally the daft idea's that turn out trumps !! Ta all.
 
My also be worth while seeing if they have a security light with a photo cel if it trips at the same time as the street lights kick in on their own photo cel. Just a thought.
 
I would have a go a putting a RCBO in for that circuit on the unprotected side to stop any major inconveniance to the customer in the short term.

It could be that the main RCD is at its limits with the leakage on that bussbar on something going on is enough to trip it adding up the leakage.

Might be worth ramping the RCD and sticking a clamp meter on to see what the mA drain is.

Mind you agree with all the above ideas and like nickblake says its normally a daft idea that gets it fix.

Photo cell is a good sugesstion as well Paul.

Good luck.
 
Last edited:
I would have a go a putting a RCBO in for that circuit on the unprotected side to stop any major inconveniance to the customer in the short term.

It could be that the main RCD is at its limits with the leakage on that bussbar on something going on is enough to trip it adding up the leakage.

Might be worth ramping the RCD and sticking a clamp meter on to see what the mA drain is.

Mind you agree with all the above ideas and like nickblake says its normally a daft idea that gets it fix.

Photo cell is a good sugesstion as well Paul.

Good luck.

My thoughts as well, it may not be one item off equipment but a number of items which are not always on together but when they are they cause the the RCD to trip.
 

Reply to Street lighting causing RCD to trip? in the Australia area at ElectriciansForums.net

Similar Threads

I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
581
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
343
Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
478
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock