Discuss Stripping Wires With Side Cutters in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
4
Hi guys

Have some trouble here.

So I'm doing terminations at work and using side cutters, usually on 1.5mm or 2.5mm. Seems to happen more with stranded.

I'm squeezing the cutters a bit and turning the side cutters around the wire and often the insulation bags up against the side cutters and just turns with the cutters as I turn them around the cable, without cutting all the way around the insulation, so I can't pull it off easily.

If I go gentler, I have to turn the cutters several times more than my colleagues in order to get the insulation thin enough to pull it off and it just feels like they're rubbing the insulation at all.

Its slowing me down and it's got to the point where I'm concerned it's one of two things.

The cutters I'm using are my first pair and are knipex vde side cutters, the usual short ones.

Either the side cutters I've bought aren't sharp enough or my technique is just wrong. I've heard that recent knipex side cutters aren't what they used to be, people moaning they aren't sharp, I ignored that and bought a pair anyway, but now I'm starting to think they might be too blunt from my own personal experience, but because I've not tried a load of types out, I can't be sure. But I'm also aware I've not got years of experience to back it up and I'm still on my first pair of cutters so I'm probably just inexperienced and I'm sure that's playing a part.

Any tips and any ideas on what you think the problem might be? My colleagues are all using CK side cutters that seem to have a sharper angle on the blades and they do one twist and pull the insulation off with very little force. I'm doing several twists and pulling way harder and not getting it off and sometimes I open the cutters to see they've simply just pressed in to the insulation, gripped it and have twisted it around the conductor. As a side note, I'm a fairly strong lad so this isn't a lack of minerals.

If I'm patient and do more twists and spend more time, I get through the insulation and I can feel the sheath give so I stop there and it pings off fine, but it's taking longer than it should.

If you think it's my technique, I'd appreciate some tips on what you do.

The way I see it, things like this can add up to big time savings as I obviously can't compromise on quality, just trying to be the best I can so helpful answers are appreciated.

Note: I'm not damaging the conductor. All the testing of my circuits have been fine and the sparks checking my work are happy with it, I'm just frustrated with the time and obvious difference in effectiveness when stripping the ends of cables for termination.
 
My personal view... the clue is in the name :)

Side cutters are for cutting... I know people use them for cable stripping but they aren't really designed for it. If you work primarily with 1.5 and 2.5, then might I recommend the Knipex installation pliers. Nice sharp shear for cutting cables (I've cut 25mm tails with mine) and some dedicated strippers for cable sizes up to 1.5 and 2.5. If you work a lot with flex they also have a crimper for attaching bootlace ferrules.

Edit:- Cutters with dedicated stripping sections... they are designed for stripping and so may work well for you, but straight up side cutters aren't meant for stripping cable.
 
My personal view... the clue is in the name :)

Side cutters are for cutting... I know people use them for cable stripping but they aren't really designed for it. If you work primarily with 1.5 and 2.5, then might I recommend the Knipex installation pliers. Nice sharp shear for cutting cables (I've cut 25mm tails with mine) and some dedicated strippers for cable sizes up to 1.5 and 2.5. If you work a lot with flex they also have a crimper for attaching bootlace ferrules.

Edit:- Cutters with dedicated stripping sections... they are designed for stripping and so may work well for you, but straight up side cutters aren't meant for stripping cable.
Its weird because college taught me to use side cutters that have no notches and everyone I've met on the tools all uses side cutters, albeit most have notches for stripping, I've only seen people advise using dedicated strippers or installation pliers on forums or YouTube. Is it really that rare to find people who use them?

Do you think that more recent knipex side cutters are even less suitable than other side cutters to carry out this duty...being aware that many cutters arent notched for stripping or are just all 'basic side cutters with no notches' just a hindrance in this duty?

Thank you for your reply.
 
I used to use side cutters a lot for stripping wire for electronics but they were substantially smaller than the Knipex ones I have now. I have used my Knipex ones for stripping the odd cable but just find them clunky compared to tools with a proper wire stripping facility.

I watch some sparks on YouTube and some seem to use side cutters (with and without the stripping notches).

Like many things to do with tooling, it's probably personal preference. My two most used pliers are my Knipex side cutters and my installation pliers. I cut and trim with the cutters and do nearly everything else with the installation pliers. That's just how I've ended up working and it suits me.

There are alternatives such as automatic wirestrippers. Maybe look into some of them?
 
Remember, just because a cable tests OK, it doesn't mean you haven't damaged the core. It is, after all, a very small amount of insulation being stripped and partial damage would make very little difference to continuity test readings. Under load condition, things could be very different. I've seen 'time saving' cost more than a few minutes.
I was taught using a knife and still use one. I also like the 'notched' stripper cutters, in some instances' but precision is vital. I've used all sorts of methods....it all comes via practise and ability to adapt to what you're using.
 
Last edited:
I used to use side cutters a lot for stripping wire for electronics but they were substantially smaller than the Knipex ones I have now. I have used my Knipex ones for stripping the odd cable but just find them clunky compared to tools with a proper wire stripping facility.

I watch some sparks on YouTube and some seem to use side cutters (with and without the stripping notches).

Like many things to do with tooling, it's probably personal preference. My two most used pliers are my Knipex side cutters and my installation pliers. I cut and trim with the cutters and do nearly everything else with the installation pliers. That's just how I've ended up working and it suits me.

There are alternatives such as automatic wirestrippers. Maybe look into some of them?
I can see why you'd use those two.

I've seen people using shears to do work on 1.5 and 2.5mm, what are your thoughts on using them? They look like they cut more than they crush, but I'm not sure if that's just a bad idea or not.
[automerge]1575335054[/automerge]
Remember, just because a cable tests OK, it doesn't mean you haven't damaged the core. It is, after all, a very small amount of insulation being stripped and partial damage would make very little difference to continuity test readings. Under load condition, things could be very different. I've seen 'time saving' cost more than a few minutes.
I was taught using a knife and still use one. I also like the 'notched' stripper cutters, in some instances' but precision is vital. I've used all sorts of methods....it all comes via practise and ability to adapt to what you're using.

Thanks for your reply.

I've not had any issues yet, but that's not to say there might not be one in the future, sort of why I'm here in the first place, to see what other people with more experience do.

I've considered a pair of notched cutters and SparkyChick has even pointed out a pair of installation pliers.

Ideally I'm looking to carry as few extra tools as possible, so perhaps the notched cutters or notched shears if they exist... Not sure if shears are just asking for it and will keep damaging the conductor.

I'm going to avoid using a knife where I can for now, perhaps look at that down the line when I'm on a project where I can often not see what I'm doing. The work I'm doing is in very difficult positions with not a lot of slack so I need to be sure I'm playing as safe as I can be.
 
Last edited:
Pro tip... The pliers should never leave your hand...… use it to cut, strip, crimp and hammer.

why are you twisting? score the side with the cutter blade, score the top and gently pull, sheath slides off. With the right amount of pressure you will not touch the copper.
Always buy good quality pliers and you wont regret it. You will never use side cutters again.
 
I was taught at college to use proper adjustable wire strippers.... 2 v notched ends and an adjusting screw so you couldn’t close them too far and damage the copper.

Afterwards, I just got used to using combination pliers... but sometimes you got a tough piece of insulation that needed a knife.
After the pliers have cut through a live cable, it has the perfect sized notch:eek:

I now use an automatic wire stripper. But I’m finding sometimes the waste I’m pulling off gets stuck on the blade, and it doesn’t work on the next cable until I clear it.
 
It is unlikley to be that your cutters are not sharp enough, I presume they are new or nearly new.

Over time you will develop your own techniques and get “the feel” for your own set of cutters.
After some time they will eventually feel like an extension of your hand and act almost intuitively.
Even picking up another sparks “identical” pair of cutters will feel wrong as soon as you use them.

Stick with it, practice makes perfect.
 
I was taught at college to use proper adjustable wire strippers.
This might be sound advice if you work for a boss that pays you hourly rate, but terrible advice in general. If you are working as a contractor or want to be a good leco, you don't have time to grab different tools just to connect a piece of wire. The job needs to be done professionally and in a timely manner, otherwise you wont make money. It is not hard to use pliers when you use them all day. After a while they become an extension of your body and you will start to feel when you have the right pressure to score the cable enough to strip the sheath. If you continue to use different tools you will never become "one" with your pliers.


but sometimes you got a tough piece of insulation that needed a knife.
Woah, knives are too sharp, you will cut too deep and nick the copper.
 
Hi guys

Have some trouble here.

So I'm doing terminations at work and using side cutters, usually on 1.5mm or 2.5mm. Seems to happen more with stranded.

I'm squeezing the cutters a bit and turning the side cutters around the wire and often the insulation bags up against the side cutters and just turns with the cutters as I turn them around the cable, without cutting all the way around the insulation, so I can't pull it off easily.

If I go gentler, I have to turn the cutters several times more than my colleagues in order to get the insulation thin enough to pull it off and it just feels like they're rubbing the insulation at all.

Its slowing me down and it's got to the point where I'm concerned it's one of two things.

The cutters I'm using are my first pair and are knipex vde side cutters, the usual short ones.

Either the side cutters I've bought aren't sharp enough or my technique is just wrong. I've heard that recent knipex side cutters aren't what they used to be, people moaning they aren't sharp, I ignored that and bought a pair anyway, but now I'm starting to think they might be too blunt from my own personal experience, but because I've not tried a load of types out, I can't be sure. But I'm also aware I've not got years of experience to back it up and I'm still on my first pair of cutters so I'm probably just inexperienced and I'm sure that's playing a part.

Any tips and any ideas on what you think the problem might be? My colleagues are all using CK side cutters that seem to have a sharper angle on the blades and they do one twist and pull the insulation off with very little force. I'm doing several twists and pulling way harder and not getting it off and sometimes I open the cutters to see they've simply just pressed in to the insulation, gripped it and have twisted it around the conductor. As a side note, I'm a fairly strong lad so this isn't a lack of minerals.

If I'm patient and do more twists and spend more time, I get through the insulation and I can feel the sheath give so I stop there and it pings off fine, but it's taking longer than it should.

If you think it's my technique, I'd appreciate some tips on what you do.

The way I see it, things like this can add up to big time savings as I obviously can't compromise on quality, just trying to be the best I can so helpful answers are appreciated.

Note: I'm not damaging the conductor. All the testing of my circuits have been fine and the sparks checking my work are happy with it, I'm just frustrated with the time and obvious difference in effectiveness when stripping the ends of cables for termination.
Use dedicated stripping tools, ignore the fact that you said that you haven't damaged the conductors, no amount of electrical testing will prove this, there will be damage to the conductors, especially stranded conductors, that you wont be able to see with a cursory check, unless you actually find that you have less strands than you should have, even solid cable, if you stuck any of these terminations under a magnifying lenses, and seen the results of using the wrong tool, you would soon change your opinion, use the right tool for the job Mate, you know it makes sense. Is the work you are involved in mainly new builds, where speed counts? these other Sparks that check your work, how skilled are they?
 
Last edited:
I use knipex and they stay sharp for years, but any cutters should be sharp and keen as new so won't be that.
As SC says, they can strip but are not made for it. That said, it's an easy enough task with side cutters, I can only assume it's practice you need.

I personally use Jokari FKZ for small twin cable stripping nowadays. Faster and neater than cutters and less thumb strain for me. I was starting to suffer with permanent strain injury.
 
As Pete says, the damage to a conductor caused by using the wrong tool may be difficult to see with the naked eye, yet it can be weakened .and stressed so that it snaps off later when flexed.

A good spark should be able to make a sound connection with any tool, but will favour the correct one i.e. an appropriate stripper or stripping section of electricians' pliers.
 
Just because everyone doesn't mean it's the right way.

Also sometimes was right for others isn't right for you. Don't be scared about trying different techniques and tools to see what work for you. Within reason of course.
 
Get yourself a pair of decent knipex ones. Stripping cable will come with experience. There is no right way to do it just whatever you are comfortable with.
 
I've used side cutters for years for stripping wires, admittedly I didn't do a very good job to start with, and this was before dedicated wires strippers were easily available. Bit like on here where some say torque screwdrivers are a waste of time.

Nowdays I use side Combi cutters for your 1-2.5mm cables, as its just plain quicker. I also somehow acquired those strippers that @littlespark mentioned, dream to use I must say.

@MeggerHertz_NW I would recommend carry on training stripping small cables with side cutters, its a basic skill you should have. But eventually, you'll find using a dedicated stripper just less complicated.
 
Auto wire strippers for small cables and T&E sheath. Notched cutters if doing 1.2/2.5 and shears for bigger stranded cables.
 
I am also a trainee. (3rd year) I also had a problem stripping to begin with.

my personal view is you should persevere with using the side cutters or pliers. You are currently learning your trade and you should take full advantage that your not on a price.

yes wire stripping tools is a quick and easy fix and could make you quicker short term. however in the long term learning to do it with one tool will eventually make you a better spark
 
Wire in left hand, cutters in right. Grip insulation with cutters but not enough to cut into copper. Use thumb of left hand to push cutters away from end of cable while maintaining the same gentle grip with the right hand. Insulation comes off with no effort and no scratching, or scoring of the copper below.

If the conductor needs folding over I always use pointy pliers.
 
Yes, if I'm going to use cutters, that's how I do it. Depending on the cable type I'll sonetimes give a quick pinch, then move 90 degrees around the cable before the main squeeze. Works best for mid size cables.
 
Last edited:
Hi guys

Have some trouble here.

So I'm doing terminations at work and using side cutters, usually on 1.5mm or 2.5mm. Seems to happen more with stranded.

I'm squeezing the cutters a bit and turning the side cutters around the wire and often the insulation bags up against the side cutters and just turns with the cutters as I turn them around the cable, without cutting all the way around the insulation, so I can't pull it off easily.

If I go gentler, I have to turn the cutters several times more than my colleagues in order to get the insulation thin enough to pull it off and it just feels like they're rubbing the insulation at all.

Its slowing me down and it's got to the point where I'm concerned it's one of two things.

The cutters I'm using are my first pair and are knipex vde side cutters, the usual short ones.

Either the side cutters I've bought aren't sharp enough or my technique is just wrong. I've heard that recent knipex side cutters aren't what they used to be, people moaning they aren't sharp, I ignored that and bought a pair anyway, but now I'm starting to think they might be too blunt from my own personal experience, but because I've not tried a load of types out, I can't be sure. But I'm also aware I've not got years of experience to back it up and I'm still on my first pair of cutters so I'm probably just inexperienced and I'm sure that's playing a part.

Any tips and any ideas on what you think the problem might be? My colleagues are all using CK side cutters that seem to have a sharper angle on the blades and they do one twist and pull the insulation off with very little force. I'm doing several twists and pulling way harder and not getting it off and sometimes I open the cutters to see they've simply just pressed in to the insulation, gripped it and have twisted it around the conductor. As a side note, I'm a fairly strong lad so this isn't a lack of minerals.

If I'm patient and do more twists and spend more time, I get through the insulation and I can feel the sheath give so I stop there and it pings off fine, but it's taking longer than it should.

If you think it's my technique, I'd appreciate some tips on what you do.

The way I see it, things like this can add up to big time savings as I obviously can't compromise on quality, just trying to be the best I can so helpful answers are appreciated.

Note: I'm not damaging the conductor. All the testing of my circuits have been fine and the sparks checking my work are happy with it, I'm just frustrated with the time and obvious difference in effectiveness when stripping the ends of cables for termination.
Klein side cutters and practice practice practice
 
In the OP you say you don't know if it's you or your side cutters that are the problem

Use another pair borrowed from a colleague and get him to try yours

If you still can't strip the cable more efficiently than with yours it's your technique

Your Electrician mate will tell you if your cutters are blunt

I used to work with T+E and found it was the technique wasn't right by trial and error
I did have side cutters of all common makes and found some were sharper than others of the same brand

I ended up scoring with a knife pulling the cpc and snapping of neatly
I work in controls now and still use the knife but I do use US style wire strippers for the cores
 
Hi guys, just an update on this.

On the advice of others:
I asked to try out my colleagues cutters and asked them to try mine.
I also looked in to getting some Strippers, but they were £20 a dance so I borrowed some installation pliers and they weren't quite as much fun, but they did the job.

So I tried some colleagues cutters:
  • Knipex X-cut
  • Another pair of knipex diagonal cutters the same as mine.
  • CK sidecutters
  • CK combicutters
  • Knipex Installation snips

Outcome of conversation and comparison:

When I asked, they asked me what was up and I told them straight. 2 immediately lit up and agreed with me and pulled out their Knipex cutters they'd replaced due to the same issue. One being a fully qualified approved electrician and another being an experienced improver who is nearly ready for his AM2.

It turns out we all found the same issue with the Knipex diagonal cutters and knipex x cut that didn't exist in the other cutters.

The X-cut and second pair of knipex diagonal cutters were owned by electricians who had stopped using them because they weren't doing the job properly and have them as spares.

They described their problem as the same, it was squeezing the insulation not scoring it and it meant they had to press harder than they wanted to, it slowed them down, compressed the conductor and they didn't like that.

I tried the C.K. cutters, they were way sharper and it was effortless to score the insulation and strip it.

Another spark has a pair of C.K. cutters that are normal cutters, but have 2 notches for 1.5 and 2.5mm, an anvil for bending and have pattress screw cutters built in behind the pivot point.

The C.K. cutters of both types did the job in my hands twice as fast, more reliably and without having to put as much effort in, in spite of their age. They also cut with far less force as well so when I'm grabbing a few cores to cut them down roughly, I can get through the entire lot with ease.

Now we were all talking and whipped our cutters out in front of each other and were comparing size, angle, sharpness, how we hold them, hahaha!

Anyway, the Knipex cutters we were frustrated with, even my newer pair, simply weren't cut at as sharp an angle as the installation pliers (which have shears) or the C.K. cutters/combicutters which have a sharper cut and also a more open face for clearing discarded sheaths from and we could all feel the force and estimated it as requiring double the effort to cut anything significant and a lot longer to strip anything.

I now own a new pair of C.K.'s the boss gifted me (he weighed in and disliked the snips I had as well and offered to sort me out) as his own personal recommendation which are absolutely fantastic. They've got 1.5mm and 2.5mm strippers in and cut whatever I want like butter. The only thing I miss is the handles on the Knipex, which are marginally chunkier, but were a less comfortable shape.

Thanks for giving me the tips ladies and gents, in part, I'm sure I'd have got faster with the knipex anyway but they were slowing my work and that isn't on. Ultimately, they were a significant part of the problem and I'll continue to train and learn but with the new C.K.'s in hand as a significant improvement and I'll save my knipex as spare. I asked a couple of the older ones to look at my technique and show me theirs and they said it was fine and told me my cutters were garbage...which suprised me.

Merry christmas guys and girls, any follow up questions on my findings, let me know and again, thank you all for the tips.
 
I use these as my go-to


These are my others for when I need long nose

Draper 05048 220mm Expert Ergo Plus Fully Insulated High Leverage VDE Long Nose Pliers View: https://smile.amazon.co.uk/dp/B005DMVSHY/ref=cm_sw_r_cp_apa_i_5397DbCZVMTPA
 
I use these as my go-to


These are my others for when I need long nose

Draper 05048 220mm Expert Ergo Plus Fully Insulated High Leverage VDE Long Nose Pliers View: https://smile.amazon.co.uk/dp/B005DMVSHY/ref=cm_sw_r_cp_apa_i_5397DbCZVMTPA
They are extremely similar to the C.K. ones I'm now using
 
After hearing so much about the Knipex installation pliers before, I finally got some in my hand at the wholesalers the other day. They went straight back behind the counter...the handles were tiny !
 
I use these as my go-to


These are my others for when I need long nose

Draper 05048 220mm Expert Ergo Plus Fully Insulated High Leverage VDE Long Nose Pliers View: https://smile.amazon.co.uk/dp/B005DMVSHY/ref=cm_sw_r_cp_apa_i_5397DbCZVMTPA
One does wonder what the world of Electrics is coming to.
 
I use these. I'm not a fan of compact cutters. The Armeg ones are sharp and have sharp pointed tips, something missing from a lot of other models of cutters.
 
I use the ck combi cutters, got them in both sizes, wont use anything else and can just about manage the screw cutter part, I don't use the anvil as often, I use knippex pliers to fold and form the end, sometimes the with CK combi cutters you may, if working in a confined space, nick another cable as you use the anvil, if theres bags of space to work in, then I use the anvil, it can speed up work.

The Ck cable cutters quite good, goes through tails easily and score the insulation if careful, however, treat them with care.

The worst cutters I have used are Irwin vice grip, I was gifted a set, cutting edge is pretty poor, the only use they have now is pulling nails out, utter garbage.

At the end of the day, its a trial and error with tools, eventually you will have your favourites that your used to using. This is what I hate about the lack of decent tool shops where you can go and try stuff out, ya know, a real tool shop where us tool fanatics can spend a day in :)
 
The Snap On and Mac tool vans still come to my mate's garage.
I have to deliberately miss them.
If I happen to arrive when they are there it is a struggle of wills.

Snap On are worse than sky cold callers or those twits that mug you in supermarkets, I can deal with them easily but Snap On I had to muster all my will power and say no, then slope off sulking because Mrs Tux made it clear we are not re-mortgage the house.
 
It's just personal preference but I think it's good to try all options too. I have the knipex installation pliers and they work for me. Many tasks can be performed with them. However some people hate them.

I settled on these after trying all options. I still use the automatic strippers if I'm doing lots of cable stripping. Iv used side cutters and had similar issues to what you describe. Iv tried cable cutters, adjustable insulation cutters etc etc.

It really helped working with them all because on my recent AM2 exam I only had side cutters. Good job I knew how to actually use them, even if I dont on a daily basis.
 
It's just personal preference but I think it's good to try all options too. I have the knipex installation pliers and they work for me. Many tasks can be performed with them. However some people hate them.

I settled on these after trying all options. I still use the automatic strippers if I'm doing lots of cable stripping. Iv used side cutters and had similar issues to what you describe. Iv tried cable cutters, adjustable insulation cutters etc etc.

It really helped working with them all because on my recent AM2 exam I only had side cutters. Good job I knew how to actually use them, even if I dont on a daily basis.
So on the exam that's all you're allowed?
 
There's many ways to skin a cat (not that I'd ever skin a cat. I love mine).

There's many different approaches to sripping. Evetually, you develop a bit of a "muscle memory" for it, and it's different for everyone.

I like to use CK redline cutters with the notch in for t&e. But i also know chaps who use cable loppers and side cutters.

Simialrily, I like to use a knife for circling around round flex outer insulation (many will gasp, but i've done it this way for years and my hands have done it that many times, I just know "the right feel" to stop it going too deep - plus I still always check each inner core individually for nicks even after all these years)

In short, you won't get a solid answer. Just try a few tools, try on lots of scrap cable and in time, you'll get a system that works for you wthat you won't struggle with.
 

Reply to Stripping Wires With Side Cutters in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm new to this forum and trade as DF Electrics - Small Job Specialist based in Ellastone, near Ashbourne, Derbyshire. I'm now back on the...
Replies
10
Views
834
First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
350
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
747
Hi, I'm looking to get the lionshare of a small shed wired before a friendly electrician does the needful. I'm a confident DIYer, but I would...
Replies
25
Views
1K
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock