Currently reading:
Sub Board fed from a plug top, EICR Coding

Discuss Sub Board fed from a plug top, EICR Coding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Just to keep you all updated.

We had our NICEIC inspection the other day and we pulled this issue up with the inspector.

They basically called it out as we’ve been debating here. Technically it’s part of the fixed wiring, and being on a plug top is prone to overloading/heating. But it being on the plug top could also exclude it from the EICR entirely (I don’t necessarily agree with this ruling as a conservatory isn’t leaving anytime soon).

We left it up to the discretion of the client, and told them if they wanted it included on the EICR we would run a new sub main down for the additional fuseboard, otherwise we would exclude it and highlight why we think it isn’t up to scratch.

With a little persuasion the client is going to have the sub main done, which I think is the optimal outcome for all parties.
 
2.8 Installing fixed electrical equipment is within the scope of Part P, even if the final connection is by a standard 13A plug and socket, but is notifiable only if it involves work set out in regulation 12(6A)

2.9 Installing prefabricated, modular wiring (for example for kitchen lighting systems) linked by plug and socket connectors is also within the scope of Part P

Quoted from Part P of the Building Regulations 2013. Just to show that there are instances where equipment that is fed from a standard plug and socket need to be given consideration.
This might be useful info.
 

Reply to Sub Board fed from a plug top, EICR Coding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top