Discuss Sub main advice please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

537.1.4 A main linked switch or linked circuit-breaker shall be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation.

A main switch intended for operation by ordinary persons, e.g. of a household or similar installation, shall interrupt both live conductors of a single-phase supply.

BYB page 154

Which is open to interpretation ... A main switch per fuseboard and per switch fuse could serve to provide the necessary isolation.

If not hundreds of thousands of properties could be deemed dangerous
 
Which is open to interpretation ... A main switch per fuseboard and per switch fuse could serve to provide the necessary isolation.

If not hundreds of thousands of properties could be deemed dangerous

I don't think it would mean properties would be dangerous, just poorly designed.

Would you have the same opinion if you went into the mains room of a large factory and had to shut off the power in an emergency, and instead of having a single main isolation switch, you had a series of 15 randomly placed switch fuses and fuse boards? BS 7671 applies to all setups after all.
 
Not quite the same thing though is it. Two consumer units next to each other do not really create an isolation problem. Certainly not one which means it is essential to install a separate isolator next to them anyway.
 
MDJ - thanks for your reply. To clarify intent. Split incoming mains and install a CU house side that will feed 16mm to outbuilding. CU in outbuildings supplying one RFC one lighting circuit and 15m2 of UFH and two electric Velux. The reason for T&E into SWA was picked up in a post - for aesthetics as conduit into box outside looks better than trying to get 16mm SWA out and down a wall. Does this answer Qs or have i missed something? Thanks so far all. I was going to install a mains isolated while i was there as currently not one
 
I picked an example at the other end of the spectrum on purpose to be honest. The regulation doesn't say how many fuse board there needs to be before you need an isolator to turn it all off, it just says that every installation needs one at the origin.
 
537.1.4 A main linked switch or linked circuit-breaker shall be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation.

A main switch intended for operation by ordinary persons, e.g. of a household or similar installation, shall interrupt both live conductors of a single-phase supply.

BYB page 154

In such a case where there are 2 boards or more, you could argue that 537.1.6 would then apply ................... (BYB p 154)
 
In such a case where there are 2 boards or more, you could argue that 537.1.6 would then apply ................... (BYB p 154)
Can you believe they've deleted 537.1.6 from BBB. I think we will have the same label at 514.15.1 and perhaps 537.2.7 (new) which says isolators to be clearly identified.
 

Reply to Sub main advice please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
837
hi thank you for help in advance have a potential pv installation for a garage roof that is some 60m from the main house (main incomer in the...
Replies
9
Views
2K
Hi, I’m new to the forum and am seeking some advice please. I’ve picked up a job that another electrician has abandoned, the job is to...
Replies
17
Views
2K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
881

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock