Hi All.

I'm finally getting to start the installation that i'd asked advice on in October. However there have been some changes i've had to make i may or may not be on the right track.

The plan was to put in an 8 way cu (sub main) with 6 RCBOs' to divide up a computer suite, 25 PCs', data projector, printer, e.t.c, all radials (high integ earthing).
The 8 way being fed by the original radial circuit from a Federal DB in a riser about 50m away (cable run). The plan being to replace the 30A Federal RCBO with a 40A Federal MCB, those of you with much more experience than myself have just seen the flaw in my plan, Federal boards are now obsolete and i'm a little uncomfortable with using secondhand MCBs' (ebay).
So i decided to let sleeping dogs lie and not touch the Fedral except for the folowing.

So plan B from the riser a 2 way cu sub main with a 40A MCB (63A pole switch) to the computer suite in 10mm T&E to the 8 way cu.

My question concerns the tails from the 2 way cu:-
Where do i connect them, on the incoming or bus bar side of the Federal board (each phase protected by a 100A fuse)?
Or directly to the incoming supply bus bar box?
Can i use the 10mm T&E?
Or does it need to be larger that 10mm?

The total length not being longer than 2 meters.

Your thoughts would be appreciated.
 
I'm a bit confused by the sub-main supply end connection also. If there is a busbar chamber, you could supply directly from this with a suitably rated switchfuse to protect the sub-main. If there is a change in CSA, the switchfuse will need to be within 3M of the chamber.

WRT the actual sub-main being 10mm T&E, an issue that immediately springs to mind is the size of the CPC and the possibility of high earth leakage currents from all the IT equipment.
 
Lenny
Effectively the 2 way with 40A MCB is what i was trying to achieve being similar to a switch fuse you suggested and it is well within the 3m distance so i'll wire it directly into the bus bar chamber.

However i didn't give the CPC any thought. I'm not sure but i think that the CPC in 10mm T&E is 4mm so does this mean that i'll have to run an additional 6mm CPC.
As the installation stands when all pc's are on, i've measured up to 60ma for short periods, 2-3 seconds, however from time to time it stays there for long enough to trip the RCBO. As a result i've disconnected 6 PCs' as an interim fix. It was the story "this looks like a good room to turn into a PC suite" not looking at all if the supply will support it.
 
I did a internet cafe some years ago now and it was designed with no more than six pc's per circuit for that reason. Its assumed 5mA per pc on design (can't find the spec ATM). What reasons does it require RCD protection in your design ?
 
just seen the T&E bit. Is this a school ? can you use T&E in the place ? would not have thought so. Personally i would go for the swa with the additional core with armouring for possible high currents.
You can still get some old federal (not all) types, I had to on a couple of jobs last year. Don't see you have an option other than changing to a standard mcb. sorry for all the questions, i missed your original post about it all.
I agrre about the ebay route, I will look back during the week where i got mine from when i'm back in the office.
Stick a photo up as i may even have one in the stores your welcome to it if it helps.
 
needsaparks
You right about the T&E issue, however it will be run in metal trunking above a suspended ceiling and the 8way cu will be in a small office adjacent to the suite.
 
Yes I thought it would be, possibly low smoke even, its just that you will have a sub-board supply with possibly high currents running on the earth so how do you intend on addressing this if your using T&E.?
My guess is the pc suite is surface trunking or dado compartment, thats how most do them. sounds like just adding additional circuits to split it up would be the sensible answer on more rcbo's.
 
Thanks needasparks.
Just been on to the doncaster website as i was unsure of the csa of the cpc of the 10mm T&E and as it comes out at 4mm. My plan will be to running an additional 6mm cpc.



Edit
Sorry for the late response but i could not reply posts till today
 
Last edited by a moderator:
We had a drum of about 70m of T&E so couldn't justify the £200 spend on singles. As for the trunking, there is plenty space as it is 100mm x 100mm and about 20% full.
 
We had a drum of about 70m of T&E so couldn't justify the £200 spend on singles. As for the trunking, there is plenty space as it is 100mm x 100mm and about 20% full.

Save your T&E for another job and use singles on this installation. Your already having to supply a separate single CPC conductor, so bite the bullet and do things properly by using the right installation cable....
 

Reply to Sub main board question in the Canada area at ElectriciansForums.net

Similar Threads

Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Now that SPD's must be fitted regardless, how does this stand from a sub-main perspective? Went to look at a job and they want a supply to a pre...
Replies
3
Views
2K
hi thank you for help in advance have a potential pv installation for a garage roof that is some 60m from the main house (main incomer in the...
Replies
9
Views
2K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
891
I have an older Crouse Hinds board with a 200A service. Due to recent rehab on the house, I found I have the need to install a sub panel. I...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock