hi guys new to this so sorry if revisiting old stuff.

I need to run a sub main 200M from the service head to a log cabin
Super eco all LED etc, so 40A 9Kw max demand

if i use the cable calculators i get 185mm cable
we all know power networks cover huge distance with 35mm cable on 100A supply

I intend to use 2 core 25mm SWA bonding/earth the Armour at the origin then through a
60A double pole breaker terminating in an insulated enclosure with a 40A double pole breaker
then into a 17th board on a TT system

Your thoughts welcome on how i justify what i intend
any suggestions welcome

The fact that I'm part "P" & NICEIC means I'M authorized not that I'm any good
 
According to my calculation 70mm swa will give you a volt drop of 5.5 v at the cabin @40a.
25mm will result in a volt drop of around 15v @40a. Wont comply with the 3% requirement for lighting will it?

How have you arrived at your maximum demand?
 
we all know power networks cover huge distance with 35mm cable on 100A supply

Think you'll find that the 35mm cable you are talking about are the short Tee's off the main distribution cable to service heads supplying domestic and small commercial properties. The smallest DNO distribution cables that i've personally seen, have been 4 core 95mm...

200 metres is a hell of a long distance. When sizing sub main cable you may want to think about using a parallel cabled sub main, could well work out cheaper too!! Hmm, ...Unless of course you start adding in a derating grouping factor into the equation!! lol!!
 
Last edited by a moderator:
I will refrain from stating the obvious regarding your apathetic approach to the job and your obvious lack of knowledge, but I will say this and only this;

The voltage drop on a 25mm cable over 200m with a 40A demand will be a non issue if you are able to check the exact voltage tolerance of every single item of equipment to be installed and it can cope with less than the nominal (200-260V for example). Is this likely to be the case? No. But unless you do something, your install won't comply with the regs. I'd start with diversity!
 
200m of 35mm, I hope you are getting it delivered as that's a fair amount of cable.

Excuse my if ignorance but will this not need joining too as its quite long, can you get a 200m length of that?
 
200m of 35mm, I hope you are getting it delivered as that's a fair amount of cable.

Excuse my if ignorance but will this not need joining too as its quite long, can you get a 200m length of that?

Yeah you can but you aint lifting that drum by hand, will be very,very heavy

Spec for 4c 35mm 200m is 500kg cable weight!!!

Drum will add a bit as well
 
Last edited:
the first thing to say is that i took the job over and the supply was to come from a closer house
BUT that house has a 60A supply a hot tub and a 9.5Kw power shower and it is tenanted, the farm owner has an 80A supply to a barn 200m away. the DNO have quoted 105,000 to put in a new 100A supply,
Max demand
i have now decided to wire the dish washer and the washing machine through a 2 way switch so the cannot be used together.
wash machine 3 kw
40 of the 65 dimmerble led down lighters 400W
5 kw of everything else (boiler audio visual kettle and microwave)
as all of the lighting is dimmerble and therfore quite happy to run at reduced voltage
so i can use the 5% as a genral circuit
also the mesured voltage is 237@the service head
 
Think you'll find that the 35mm cable you are talking about are the short Tee's off the main distribution cable to service heads supplying domestic and small commercial properties. The smallest DNO distribution cables that i've personally seen, have been 4 core 95mm...

200 metres is a hell of a long distance. When sizing sub main cable you may want to think about using a parallel cabled sub main, could well work out cheaper too!! Hmm, ...Unless of course you start adding in a derating grouping factor into the equation!! lol!!

Agreed - App 10-2 'apply grouping factors only when it's not too pricey'!

Just kidding Eng - really not going there again lol ;)
 
Just ask wholesalers, they will ring there suppliers and get it delivered to site.

If not there are places online that will


Trouble is, he hasn't got a clue as yet, as to what size cable to order!!

No problem having in-line joints in a cable(s), standard practice on longer runs. So long as the cable and joints and have been accurately position marked on a appropriate drawing.... Oh, and that the joints have been made off correctly obviously...lol!!
 
round the 200 when the night stores kick in im just making the point DNO have difrent ruels to us


Yes the DNO's do have different rules, unfortunately you have to comply with BS7671!!

Depending on the cable size, supplying your house, i'd be very much surprised if you are seeing 200 Volts after 650 metres. And even if it were 200 V, i'd be complaining like hell to the local DNO!! lol!!
 

Reply to sub main to outbuilding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I am a homeowner and have a solar project coming up. I intend to install a 9kw solar system but I am not sure if I have to upgrade my main...
Replies
2
Views
951
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
0
Views
603
Hello everyone, I hope you are doing well. Several years ago I purchased an older 1971 home (aluminum wiring that has since been fixed with al/cu...
Replies
5
Views
1K
Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Replies
0
Views
780
Was wondering if the gurus can critique and/or provide recommendations on my plan to install two sub-panels in a (50'x100') 5,000 sq ft steel...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock