Discuss Sub panel.wiring question in the UK Electrical Forum area at ElectriciansForums.net

Terp393

DIY
Reaction score
0
Hello I am wiring up a 100amp sub panel in my shop the run is about 230 feet so I was advised by the supply house to use 1/0 aluminum, I was told that the breakers at the main panel at the house would not accept the 1/0 aluminum, what would be the proper way to connect the wires I have seen like step down pins that could be used but not 100% sure if they would pass inspection thanks
 
Hello I am wiring up a 100amp sub panel in my shop the run is about 230 feet so I was advised by the supply house to use 1/0 aluminum, I was told that the breakers at the main panel at the house would not accept the 1/0 aluminum, what would be the proper way to connect the wires I have seen like step down pins that could be used but not 100% sure if they would pass inspection thanks
If you are referring to 100 amps for the panel I would use four # 3 copper wires and install a main lug only sub panel. The wire will cost a little bit more but it’s half the size of copper. Remember that all buildings or shop in your case has to be GFCI protected
 

Reply to Sub panel.wiring question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am adding a 60 AMP subpanel for a detached garage/workshop with a 200 foot underground conduit run from the main panel to the sub panel...
Replies
3
Views
894
I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
862
Hi, I am burying wire from the outside meter panel to the new 100amp sub panel inside a garage. The run is 20' long. Is 2-2-2 Aluminum URD Cable...
Replies
0
Views
780
The seller is saying they will not upgrade the electric and it is normal to have 100 amps. However the inspector is stating it may trip often and...
Replies
4
Views
820
At long last my wife is getting her new kitchen and the contractor will be running 10 or so new circuits from a new sub panel. The sub panel...
Replies
1
Views
819

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock