Discuss Submain Supply 100a 100mA in the UK Electrical Forum area at ElectriciansForums.net

T

Tom Christopher

Installing a 25mm 3core swa to feed an exisitng consumer unit due to the SEB moving the supply.

Planning to use a 100A 100mA time delayed rcd to feed the split load rcd board.

Sound ok?
 
Why a 100mA S type rcd upfront?
Is it a TT system?
Will the dual rcd board accommodate a 25mm into the earth bar?
Will there be a switch fuse isolator fitted If the supply is over 3 meters from the cut out?
 
Why would it need that? Nothing in BS7671 about it, and the DNO may not specify it.
433.3.1 item (iii)
A device for Overload protection need not be provided at the origin of an installation where the distributor provided an overload device and agrees it affords overload protection to the part of the installation between the origin and main distribution point where further overload protection is provided.
The general consensus is that the DNO will allow 3 meters and no more for their cut out fuse to protect the tails.
Also 434.3
 
433.3.1 item (iii)
A device for Overload protection need not be provided at the origin of an installation where the distributor provided an overload device and agrees it affords overload protection to the part of the installation between the origin and main distribution point where further overload protection is provided.
The general consensus is that the DNO will allow 3 meters and no more for their cut out fuse to protect the tails.
So as I say its speculation if its needed, nothing to say in this instance that the DNO require it fitting.
 
My understanding is that the DNO will not generally allow their fuse to be used to protect any part of a consumer’s installation.
The 3m stipulation relates to the BS7671 requirement that overload protection must be provided within 3m of a reduction in the CCC of a conductor.
 
This is northern powers requirements anyway
1388B8A2-0046-4E6C-88C4-944582FF8636.png
 
Why a 100mA S type rcd upfront?
Is it a TT system?
Will the dual rcd board accommodate a 25mm into the earth bar?
Will there be a switch fuse isolator fitted If the supply is over 3 meters from the cut out?

PME

Yes dual board will take a 25mm

SWA will be made off into a metal enclosure with the 100a 100ma time delayed rcd. This will be mounted next to the main supply, so tails less than 3m

SWA will be above the plaster board so wont it need rcd protection?

I thought time delay to save both RCD trippings if there is a fault?
 
My understanding is that the DNO will not generally allow their fuse to be used to protect any part of a consumer’s installation.
The 3m stipulation relates to the BS7671 requirement that overload protection must be provided within 3m of a reduction in the CCC of a conductor.
Tho that is a regulation in the context you describe that has Nothing to do with the DNO tails
Read 433.3.1 and 434.3 or not
 
PME

Yes dual board will take a 25mm

SWA will be made off into a metal enclosure with the 100a 100ma time delayed rcd. This will be mounted next to the main supply, so tails less than 3m

SWA will be above the plaster board so wont it need rcd protection?

I thought time delay to save both RCD trippings if there is a fault?

There is no need for RCD protection for those reasons if using earthed SWA. If it did, then you RCD you selected would not have been suitable anyway.
 
We can only confirm if this is okay if you let loose what the earthing system is.
 
Last edited:

Reply to Submain Supply 100a 100mA in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
878
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock