installing a sub main to 5 x new flats but the service heads and meters will be about 50meters away
Ive worked out the design current to 74 amps due to it being electric heating and immersion ect (no gas)
The cable are to be brought in same duct and around 30c temp.
I worked out that 25mm will do the job but will leave with a voltdrop of 0.5volts for lighting so decided 35mm would be what was need.
I was going to install switch fuses after the meters and run swa into the flat but I was after some advice on what to do about connecting the swa into the consumer unit, I was thinking of a metal box in the service hatch which is running behide all the flats then mounting the consumer unit on the directly opposite side and bringing the cores straight into the cu to avoid any joints.
Will it be ok to use 35mm 2 core and get the earth from the swa the reason I wondering is I need to earth bond the water as it copper pipe and i thought it would be ok to use the swa for the main earth and bonding back to the MET but the guy i working with seems to think we cant use swa armouring if its for bonding and either we need 3 core or to run a separate 16mm earth for bonding
Any advise given i will be very greatful.
Many Thanks
Jimmyb
Ive worked out the design current to 74 amps due to it being electric heating and immersion ect (no gas)
The cable are to be brought in same duct and around 30c temp.
I worked out that 25mm will do the job but will leave with a voltdrop of 0.5volts for lighting so decided 35mm would be what was need.
I was going to install switch fuses after the meters and run swa into the flat but I was after some advice on what to do about connecting the swa into the consumer unit, I was thinking of a metal box in the service hatch which is running behide all the flats then mounting the consumer unit on the directly opposite side and bringing the cores straight into the cu to avoid any joints.
Will it be ok to use 35mm 2 core and get the earth from the swa the reason I wondering is I need to earth bond the water as it copper pipe and i thought it would be ok to use the swa for the main earth and bonding back to the MET but the guy i working with seems to think we cant use swa armouring if its for bonding and either we need 3 core or to run a separate 16mm earth for bonding
Any advise given i will be very greatful.
Many Thanks
Jimmyb