Discuss Suggestions for better RCD discrimination in the UK Electrical Forum area at ElectriciansForums.net

Good point from @7029 dave about having a fused-switch instead of taking off the CU, more space needed but better selectivity with downstream MCB/RCBO and if the fuse is 63A for 100A DNO (or 50A for 80A, etc) then it should be selective upstream as well.
 
Good point from @7029 dave about having a fused-switch instead of taking off the CU, more space needed but better selectivity with downstream MCB/RCBO and if the fuse is 63A for 100A DNO (or 50A for 80A, etc) then it should be selective upstream as well.
Yup IMO with what the OP has described, having a genuine sub main is better, a sub circuit off the main dB is asking for trouble.
 
Last edited:
Yup IMO with what the OP has described, having a genuine sub main is better, a sub circuit off the main dB is asking for trouble.
Am in total agreement..... had I only been there 20 years ago........
 
I would expect there is some way to run some SWA across the house, or maybe around it, and join to existing SWA so the RCD at source is not needed for "additional protection" forcing 30mA and the issues above.

Given the lengths mentioned above you might still want a delay RCD for fault protection if end of sub-man Zs is not low enough for the OCPD alone (especially if you go D-curve MCB to buy a tiny bit more fault selectivity).
Sadly there isn't! And just for extra giggles the T&E to SWA joint is buried underneath an ornate patio (or assumed to be, anyway). There's also no way in hell that the client would sanction an overhead catenary (it would need to be about 30m long and involve installing masts for extra height!).

I think quite possibly this may just be a bum deal and the customer has to accept the odd nuisance trip,
 
Sadly there isn't! And just for extra giggles the T&E to SWA joint is buried underneath an ornate patio (or assumed to be, anyway). There's also no way in hell that the client would sanction an overhead catenary (it would need to be about 30m long and involve installing masts for extra height!).

I think quite possibly this may just be a bum deal and the customer has to accept the odd nuisance trip,
I know not compliant, but I would be debating as to fitting 100ma s type at the source depending on if the loss of supply could result in an accident.
 
I know not compliant, but I would be debating as to fitting 100ma s type at the source depending on if the loss of supply could result in an accident.
So here’s a thing…. I need to get my head into the brown book and scour the regs but off the top of my head my recollection is that the requirement for cables in walls is simply 30mA, nothing said about S types at all??
 
Nobody makes a type S 30mA RCD as @mainline points out it would not meet disconnection times.

You have two issues for selectivity:
  • One is when there is a 'hard fault' and so you need some delay to allow the downstream RCD to clear irrespective of the magnitude of the fault current.
  • The other is for a 'soft fault' where the imbalance is small and rises slowly, or indeed is simply there all of the time due to accumulation of appliance leak currents, etc. For that you need a difference in trip threshold so again the downstream one always goes first.
So if designed you have no other choice then to go 100mA selective for upstream and then, to meet regulations, it has to be installed so accidental cable penetration is very unlikely. Yes, I know the BBC have some guidance limiting temporary supply RCDs to 100mA / 200ms max as it gives you some protection against a fatal shock, but that is not meeting the BS regs.

If you can clamp the sub-main and check the leakage you might find it is hovering in the 10-15mA region in which case it is not going to be cured by anything other then a change of upstream RCD to a higher current and all of the other implications of that. On the other hand, if it is normally below 10mA and the issue is the odd spike incident (like my oven that trips the RCBO a couple of times a year on switching off) then it might just be worth looking at ones of these:
They claim to be less prone to false triggering while still meeting the overall low frequency trip current and times. Here is the FAQ comparing the A-SI type they call it with the normal type A:
 
Last edited:
Nobody makes a type S 30mA RCD as @mainline points out it would not meet disconnection times.

You have two issues for selectivity:
  • One is when there is a 'hard fault' and so you need some delay to allow the downstream RCD to clear irrespective of the magnitude of the fault current.
  • The other is for a 'soft fault' where the imbalance is small and rises slowly, or indeed is simply there all of the time due to accumulation of appliance leak currents, etc. For that you need a difference in trip threshold so again the downstream one always goes first.
So if designed you have no other choice then to go 100mA selective for upstream and then, to meet regulations, it has to be installed so accidental cable penetration is very unlikely. Yes, I know the BBC have some guidance limiting temporary supply RCDs to 100mA / 200ms max as it gives you some protection against a fatal shock, but that is not meeting the BS regs.

If you can clamp the sub-main and check the leakage you might find it is hovering in the 10-15mA region in which case it is not going to be cured by anything other then a change of upstream RCD to a higher current and all of the other implications of that. On the other hand, if it is normally below 10mA and the issue is the odd spike incident (like my oven that trips the RCBO a couple of times a year on switching off) then it might just be worth looking at ones of these:
They claim to be less prone to false triggering while still meeting the overall low frequency trip current and times. Here is the FAQ comparing the A-SI type they call it with the normal type A:
So, here's a thing. Not conventional for a domestic, and not cheap, but an adjustable RCD could in theory be set for bang-on 300mS @ 30mA / 40mS @ 150mA and be compliant, basically relying on the downstream devices being inherently faster (which we all know they typically are, by a significant margin).
 
So, here's a thing. Not conventional for a domestic, and not cheap, but an adjustable RCD could in theory be set for bang-on 300mS @ 30mA / 40mS @ 150mA and be compliant, basically relying on the downstream devices being inherently faster (which we all know they typically are, by a significant margin).
Yes - if the "adjustable" bit is continuous and not a set of pre-determined steps.

Last time I priced an adjustable RCD (actually separate Hager HR520 EL relay, sense toroid, and actuator to trip the Hager 125A 3P MCBs) it all totalled around £840 inc VAT at "trade" price.
 

Reply to Suggestions for better RCD discrimination in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Replies
5
Views
877
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi all Now being upfront I am not a sparks. I am about to have some work done by a friend (certified) and as he is doing me a favour I want to as...
Replies
5
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
857
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock