Discuss Summer House Submain in the UK Electrical Forum area at ElectriciansForums.net

Gakure

-
Reaction score
19
Evening, may I pick you brain guys?
I have wired a summer house about 30m away from the main board. I have used 32A at DB1 (not RCD protect) and 6mm² 3core SWA, where I have connected both black and sheath (sleeved) at both end as CPC. In the Summer house I have used shed consumer unit 1xRCD and 2 useable mcbs.
I test Ze and PFC at DB1. I then move to test the shed DB2 RCD, Ring final and light circuit.
I am wondering
1. if I use Zs at the DB2 as Ze while filling the cert or do I use Ze and PFC from DB1?
2. I have added a 32A mcb at DB1, do I test the whole DB1 or Ze and PFC from there are enough?
What are your thought guys?
Regards
 
Ze and PFC are done at source, Ze only occurs at source assuming you have not TT'd DB2. There is no need to test all circuits from DB1, just your new circuit.
 
Usually on the top of the test results section page of the cert there is a box for zs and ipf reading at origin of your remote 2way cu, but this is only on the last test results page, its always worth measuring these values as part of your testing imo
 
Usually on the top of the test results section page of the cert there is a box for zs and ipf reading at origin of your remote 2way cu, but this is only on the last test results page, its always worth measuring these values as part of your testing imo
Thanks guys, just to clarify, am looking at the test sheet part 10, I can see PFC bit and a column of Zs measure near the end of RHS.
I am wondering am missing the Zs box
 

Reply to Summer House Submain in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
I have a client on a Superdeal tariff from SSE, the Superdeal Meter has 3 sets of tails coming out of it feeding 3 DBs: (i) DB1 - the main board...
Replies
4
Views
2K
Hi, I have completed a EIC for a garage DB2 with five final circuits (no problem there i think). But for the distribution circuit from house DB1...
Replies
1
Views
1K
Hi all, I recently moved to an older property that had a run down garage. We had this removed and a summer house put up in its place. The old...
Replies
0
Views
831
Hi guys, Can I ask you a DIY question? I'm refurbing a detached garage and adding a garden building. Garage currently has a submain supplied by...
Replies
1
Views
820

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock