Discuss Supplementary equipotential bonding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
0
Could I have some clarification on this issue ,

the tight customer does not want a new CU ,

so the only option is supp bonding the bathroom , from what I've read is link the hot and cold copper pipes and the rad and that's it . Bs7671 does not require a link from the supp bond to a cpc on an accessory , so long as the main water is bonded back to the MET . Is this the correct way to interpret it ?
 
Supplementary bonding should join together all accessible exposed and extraneous conductive parts in the location.
This would include the cpcs for any electrical circuits, otherwise it is pretty pointless.
The main bonding is also required to be in place.
 
Surely if your main water is bonded back to the met , then , in theory all copper pipe work from there on is directly connected to the met ,provided there are no plastic joints . So to save looking for plastic joints connecting to a cpc terminal is ensuring continuity ?
 
question has been asked. what work are you proposing. 9/10 you'll have to fit RCD protection anyway. if customer won't pay, walk.
 
so. if there's no supp. bonding and no RCD it's a code C2. then it's down to the owner to get it fixed or not.
 
so the only option is supp bonding the bathroom
No.

from what I've read is link the hot and cold copper pipes and the rad and that's it
No.

Bs7671 does not require a link from the supp bond to a cpc on an accessory
But the circuit may require it.

so long as the main water is bonded back to the MET
MPB must be in place regardless.

Is this the correct way to interpret it ?
No.

You must determine by testing whether the parts are extraneous and then if supplementary bonding is required.

Is supplementary bonding not required and that is why there is none?
 
I must admit this subject is the one that throws me the most!! I have just purchased guidance note 8 and am itching to get into it and it should answer some of these questions.... I hope!

Perhaps make the same purchase Jon?
 
No.


No.


But the circuit may require it.


MPB must be in place regardless.


No.

You must determine by testing whether the parts are extraneous and then if supplementary bonding is required.

Is supplementary bonding not required and that is why there is none?

When confirming if the pipework in the location is extraneous or not and there is a protective main bond to the incoming metal water service do you need to disconnect this before performing a test between the M.E.T and pipework within the location?
 

Reply to Supplementary equipotential bonding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

No waffling, going to get straight to the point. Main water on the exterior of the building in plastic. Changes to copper inside the building...
Replies
24
Views
882
In my bathroom there is supplementary bonding of the bath, bath pipework, and basin pipework before it goes into trunking and exits unconnected in...
Replies
6
Views
412
So I know why it is done, where it is done and how it’s done, but I’m yet to see a scenario where there is shock danger in a typical bathroom in a...
Replies
32
Views
1K
Curious about supplementary bonding, I have these two 4mm Cables loose and not connected to anything in my parents house. I presume they are for...
Replies
9
Views
2K
Just had my design project handed back to me from my last block and I got everything right apart from one question Q9 I would take a photo but...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock