  1. Dontwanttobeelectrocuted
    Offline

    Dontwanttobeelectrocuted New EF Member

    Location:
    Birmingham
    EFE3168C-6CF8-41AE-B53A-504DC2072645.jpeg Hi All, I want to start by saying thanks to the experts on here that give advice. It’s been really helpful looking over past posts. That said, I haven’t quite seen this issue before so I wanted to ask. I am about to buy a new house, and one of the things that has been flagged as an issue is that the electrical supply and the meter are installed under a sink (see photo). I’ve never encountered this before, and frankly seems insane. The circuit box is well above the sink, at about eye level and is a modern (but plastic) unit. The WC in question is under a stair and on an outside wall. I am 99% sure that the supply and meter need to be moved, as the sink can’t go anywhere else. Does anyone have an idea what it will cost to put them outside or any other general advice? Apologies for the low quality photo.
     
  2. buzzlightyear
    Online

    buzzlightyear please let me back in to the prison cell. Electrician's Arms

    Location:
    star command
    Welcome , i would be better if the meter is put out side after you purchased the property you would need to ask the DNO could it, it will come at a cost.
     
  3. Dontwanttobeelectrocuted
    Offline

    Dontwanttobeelectrocuted New EF Member

    Location:
    Birmingham
    Thanks, is there a specific regulation that forbids this? I’ve been doing my best to find this information but can’t quite seem to find it.
     
  4. ackbarthestar
    Offline

    ackbarthestar Forum Mentor

    Location:
    A Zoo near YOU
    Umm, I'm pretty sure that the supply intake and meter would not have been installed with that sink in its present position.
    However, if the sink cannot be moved because of internal decoration then the meter should be moved quite easily through to the outside. You'll need to check the prices to do the work from your local DNO.
     
  5. Dontwanttobeelectrocuted
    Offline

    Dontwanttobeelectrocuted New EF Member

    Location:
    Birmingham
    I am pretty sure the sink came afterwards, it was an under-stair conversion by the homeowner as best I can tell. Any idea of ballpark pricing on that kind of work? The wall in question would be 1-2 M and towards the road.
     
  6. Vortigern
    Offline

    Vortigern Regular EF Member

    Location:
    England
    Business Name:
    F.H. Electrical
    Go on line and look at your DNO prices which are put up on their site. I guess 1k plus a new CU £400 assuming no remedial works. Anything for £100 to £300 remedial works So maybe about 2k ish.
    Bet you're thinking hang on maybe I could move the sink now?:cool:
     
    • Like Like x 1
  7. Baddegg
    Online

    Baddegg Still simmering Ken, not boiled yet buddy x Electrician's Arms

    Location:
    Portsmouth
    If you are lucky op they used to move meters outside for free down here.....but the smartish meter revolution might have stopped em doing it now...worth a check though
     
    • Optimistic Optimistic x 1
  8. Taylortwocities
    Offline

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    I guess that you are in WPD area?

    There is an indicative cost table at Western Power Distribution - Basic pricing tool - https://www.westernpower.co.uk/connections-landing/guide-prices/basic-pricing-tool

    It says that "on average" that sort of thing is just shy of a grand. but of course it could be a lot more, or a lot less.
    On that page there is a quotation request link.
    Western Power Distribution - Apply for a new connection or modification to an existing connection - https://www.westernpower.co.uk/connections-landing/apply-for-a-new-connection-or-modification-to-an-existing-connection
    You'll need the MPAN number of the installation, and you wont know that, as you don't live there!
    Note that they would need to visit the site, evaluate the work and provide a quotation. They will only do this for the existing householder.
    Also it takes time.

    If you are keen on the house, take a punt and ask for a thou off the asking price. If you are in a hurry, or like certainty, then go find a different house.
     
  9. Pete999
    Offline

    Pete999 Forum Mentor

    Location:
    Northampton
    Business Name:
    None
    DNO have their own rega as far as I am aware
     
  10. SparkyChick
    Online

    SparkyChick Making a banana smoothy for my fave gorilla Staff Member Moderator

    Location:
    South Wales
    Business Name:
    SparkyChick
    I've recently had a client obtain a free (I believe) service head move due to the fact his meter box was old, tatty and a little the worse for wear after years of snails using it as a home. WPD are my local DNO.

    He enquired about having the service head moved and the guy who came out to survey the job wangled it as the equipment was not in a satisfactory condition. It wasn't a massive move mind you but it was still done for free as a maintenance activity.

    In your case, the service head appears to be an old cast iron type, which could benefit safety wise from being replaced with a modern plastic one.
     
    • Like Like x 1
  11. Rpa07
    Offline

    Rpa07 4000 posts - only 54195 behind Telectrix! Electrician's Arms

    Location:
    Bristol
    Business Name:
    Ebenezer electrical
    You may be able to carefully enclose it using Perspex panels with a bit of inventiveness.
    There are sockets under sinks all over the land. Sinks and wastes do not leak water if they work properly and with a Perspex sheet between will let you see any leaks and divert it anyway.
    Just a thought.
     
    • Agree Agree x 3
    • Like Like x 2
  12. telectrix
    Online

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    look on the bright side. a bit of soapy water in the meter might slow it down. near to me there is a whole estate with CUs fitted under kitchen sinks as when built. not heard of any problems (apart from me and some other sparks refusing to upgrade them ).
     
    • Funny Funny x 1
  13. Dontwanttobeelectrocuted
    Offline

    Dontwanttobeelectrocuted New EF Member

    Location:
    Birmingham
    Thanks for all the helpful tips. Good idea SparkyChick about the DNO maybe doing it as a safety upgrade. I will definitely follow that up.

    I agree that sinks shouldn’t leak, but I’ve got 3 kids under 9 and frankly they can’t be trusted.
     
    • Funny Funny x 1
  14. Gavin John Hyde
    Offline

    Gavin John Hyde Electrician's Arms

    Location:
    Somerset
    Business Name:
    Sulis Electrical Services Ltd
    Must have had one of the better meter fitters that day, as around here at the moment one outfit who have the meter fitting contracts find slightest thing or speck of paint on the cut out they report it to WPD who then have to come out and change it so mr smart meter man can fit a new meter. its causing a backlog now and WPD are not happy. they have to do it as part of the governments smart meter drive. i learned that if they attend and report cut out then it stills counts as a successful job visit for the meter man as he has complied with health and safety...
    Now you cant move the cutout yourself but I am aware of an electrician in the area around here who used to move the meters himself, seal fairy would come visit and somehow decide to move things and get the screwdrivers out!!! dont condone it but i am sure a lot of it goes on out there.
     