Hi Guys and Gals
i want to suspend swa between two buildings about 20 feet apart at high level and will find it difficult to attach a catenary wire. i was wondering if anyone knows the name of kit the electricity board use and also where to get them. it appears that it is bolted to each building and looks like a spring which is wrapped around the cable to take the strain.
 
There are three methods for suspending cables, as far as I'm aware.
One is to use a catenary wire, and then attach the cable to this wire.
Another is to use a cable, that incorporates a catenary wire (not sure if this is still available).
Finally there is just suspend the cable (normally hard drawn copper).
All methods will require a similar method for attaching the cable or support system to each support point.
 
The prefered method for me would be a cable ladder spanning the two buildings it allows for future expansions, if you choose a catenary ensure the swa isn't prone to swinging in the wind as it will damage the cable as its not in its design to repeatedly flex, ive seen a few cases of this where the cable shorted out between the catenary and its first fixing point on the building.
 
The spring you are refering to is called a preform or wrap. It is cable size specific and should not be used on SWA directly as it will strain the cable if not supported along its length. If you can ft a bolt each end why can you not fit eye bolts and a catenery. you could always attach the swa to the catenery on the ground and pull up at each end if you are concerened about reaching to fix midspan.
 
The spring you are refering to is called a preform or wrap. It is cable size specific and should not be used on SWA directly as it will strain the cable if not supported along its length. If you can ft a bolt each end why can you not fit eye bolts and a catenery. you could always attach the swa to the catenery on the ground and pull up at each end if you are concerened about reaching to fix midspan.
Much better idea than attempting to slide the ties along using a long stick.
 

Reply to suspending swa between two buildings in the Australia area at ElectriciansForums.net

Similar Threads

Hi I have been in the electrical contracting industry all my working life 40 years and became a member of the NICEIC in 2006. During this time I...
Replies
17
Views
2K
Was wondering if the gurus can critique and/or provide recommendations on my plan to install two sub-panels in a (50'x100') 5,000 sq ft steel...
Replies
2
Views
1K
We recently had a thread or two about some cables that were almost certainly tinned copper, but people continued to suspect they were aluminium...
Replies
7
Views
3K
I had a job last week that needed a data logger on a sewerage pump station to monitor the running times during bad rainfall. I have a Hioki PQA /...
Replies
22
Views
4K
Former Sponsor TM
F
B
Prefix - I've tried to post this in automotive, but it would not let me. This may be because I have not been recently active. Apologies if this is...
Replies
3
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock