In the past where it was required to several cables I fitted a copper bar across the lot, down the side of the board to the earth bolt and a link to the earth bar.
Discuss SWA cables - fly leading armour as cpc?? in the Industrial Electricians' Talk area at ElectriciansForums.net
i always take 3/4 strands of steel into the cpc connection aswell, what if the gland gets loosened off and some doughnut doesnt put it back on correctly?
How do you manage to do that elsparko? just curiousi always take 3/4 strands of steel into the cpc connection aswell, what if the gland gets loosened off and some doughnut doesnt put it back on correctly?
Yes agree Bob, with respect "elsparko" not really something I would ever do. Don't think that would comply with the Regulations. On a par with snipping a few strands from a conductor to get in into the terminal. IMO.How are you doing that and following manufacturers instructions in using the glands?
Also i'm reading that as 3 to 4 stands rather than 3 quarters. In which case, will do nothing anyway.
Aside from this, have you ever seen a properly terminated SWA gland just loosen on it's own?
If I saw this practice on one of my jobs I'm afraid I would insist on having it remade.
Yes agree Bob, with respect "elsparko" not really something I would ever do. Don't think that would comply with the Regulations.
i dont do this on outside glands for this very reason, but standard glands its always been a force of habit, monkey see monkey doIt's a poor way of doing it an unfortunately as you've now no longer got evenly applied pressure all the way round the gland seat, it's actually more likely to come loose with vibration.
It would compromise the IP rating of certain glands also.
Agree with Bob again, you have been taught the cowboy way I'm afraid, I would use PIRANHA locknuts as the locking ring for the gland an take a cpc from the connection on that locknut, beats having banjos or frying pans as you refer to them littering up the enclosure a far better and neater way of doing the job IMO.Sounds about right for a farm.
No you shouldn't be doing it, the glands aren't designed that way. As for a reg, I can't remember the number but it's something along the line of "suitable electrical and mechanical termination"
@elsparko
I would stop this practice asap, regardless of who taught you this or what field of electrics they worked in, this is poor to bad practice, I would also question the quality of their working practices given they felt this was an acceptable method.
The glands are manufactured to certain tolerances and the SWA has to also be to similar tolerances so that the glands are more or less universal to the given size on their packets thus will fit what it says.
The glands rely on a full use of the strands to maintain an even grip all round, taking a number of strands away and routing them direct to the earth will give a poorer glanding termination and the remaining steel strands you have secured will not satisfy the reg's, under fault conditions the gland or strands brought through could fail and/or see damage done to the cable.
Your R1 + R2 tests and ELI do not show all issues and when 1000+ amps flow under fault conditions your gland should be fitted as per manufacturers instruction as the regs require you do.
If you secure and tighten your gland correctly it should not come loose, if due to environmental conditions you suspect the glands could loosen then serrated washes should be fitted, there is also the case that the installation requires regular inspection and this should pull up on any glanding issues.
In my experience of 30+ years I have never seen a gland come loose that was fitted correctly and suitably done to account for environmental conditions so I do not see this practice serves any purpose, the only glands I find loose etc are down to poor termination practices of which I would put your method as one.
https://www.google.co.uk/search?q=p...x-b&gfe_rd=cr&dcr=0&ei=WNl5WrSMNamn8weSkoGIAQwell i stand to be corrected and glad to have it pointed out, at the macallans site we used a really thick brass locknut that had screws on the side for terminating crimps to, nobody was bothered about me taking a few strands into the earth terminal aswell though
my first boss we only used what came in the gland pack
yeah thats the ones we used at macallanshttps://www.google.co.uk/search?q=p...x-b&gfe_rd=cr&dcr=0&ei=WNl5WrSMNamn8weSkoGIAQ
Here you go PIRANHNA nuts just the ticket for SWA why the gland makers don't utilise them in their gland packs I don't know
If the armour is used as the CPC then you have no option other than to fly lead. I like the piranha nuts personally.
i should add that it still has a frying pan and flying lead, aswell as the 3 or 4 strands, and a dedicated cpc.
worst case scenario i still want there to be some earthing to the steel wire