Not normally required, battery backup on fire alarm should deal with Loss of supply due to fire for long enough to do its job.
 
I agree with @Lister1987 in as much as if it were installed today the supply should be a dedicated circuit in fire resistant cabling. (Section 25 of BS5389)
But plenty of things were allowed on fire alarms back in the day including this, and 4 core for detectors and sounders, and detector circuits/call points were even allowed to be regular T+E once. I believe 2002 was the significant year for the regs tightening up.

The thing is, I don't think this is codable on an EICR as anything other than a note.
After all, it isn't electrically unsafe and in any case as I understand things BS5389 isn't retrospective either.
Is there any justification within BS7671 for coding it?
 
You could use 560.10 but as you say, it complied at time of install, was it ever modified after install? Just got visions of the system being done to 2 versions of 5839.
I'd compile a list of required actions to bring it to current code, advise it was likely to code when installed, discharge the duty of care and leave it to the client to decide what to do.
 
the fact that the fire alarm is fed in SWA is irrelevant to your EICR as long as the SWA complies with BS7671. i.e it'ssuitable for the load; it is installed in accordance with BS7671 (glanded properly etc.). Your EICR has no relationship to BS5839.
 
the fact that the fire alarm is fed in SWA is irrelevant to your EICR as long as the SWA complies with BS7671. i.e it'ssuitable for the load; it is installed in accordance with BS7671 (glanded properly etc.). Your EICR has no relationship to BS5839.
BS7671 makes reference to supplies for safety systems hence it is relevant.
 

Reply to SWA feeding fire panel in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good evening! Don’t have a huge deal of experience with fire alarms but having to work on a conventional system at the minute with various...
Replies
8
Views
620
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
749
Hi, my friend is having a floating shelf with a electric fire, and I’m between minds where to put the socket, I was gonna put the socket behind...
Replies
3
Views
660
Hi, I'm completely rewiring a 9 bed 3 storey HMO in Jan, The fire detection required is just some linked lithium detectors in the...
Replies
7
Views
733
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock