Discuss SWA For meter tails? in the UK Electrical Forum area at ElectriciansForums.net

Think of peak times morning evenings when most load will be consumed should only be short periods when applying diversity,
a bs88-3 (new bs number for 1361) will take 190a for half hour fig 3A1 bs1761
/QUOTE]
Thanks for that. Fig 3A1(page 319) is most illuminating. Few discussions of diversity refer directly to this time factor and its clearly very relevant.
 
Think of peak times morning evenings when most load will be consumed should only be short periods when applying diversity,
a bs88-3 (new bs number for 1361) will take 190a for half hour fig 3A1 bs1761
Thanks for that. Fig 3A1(page 319) is most illuminating. Few discussions of diversity refer directly to this time factor and its clearly very relevant.
 
Last edited:
PPP

Post pictures please
TailsfromMeterBox (Large).jpg

TailRoute (Large).jpg
 
That is a bit of a lash up, what you want is a bit of swa cable :rolleyes:

Could the tails be routed out the back of the meter box, then surface inside in some plastic trunking?
 
If it's SWA why would I use surface trunking? The problem I'm facing really, is once it reaches the porch getting it through the brickwork and wooden beam to the void. Ironically the supply to the meter appears to originate from somewhere under the concrete floor inside the porch, but moving the meter inside isn't really an option.
 
If it's SWA why would I use surface trunking? The problem I'm facing really, is once it reaches the porch getting it through the brickwork and wooden beam to the void. Ironically the supply to the meter appears to originate from somewhere under the concrete floor inside the porch, but moving the meter inside isn't really an option.

Trunking looks a little nicer than cleated SWA.

To get through the brickwork and wood drill a hole.

It’s not really ironic, it’s just probably been moved outside from it’s original location inside.
 
Really ? Please refer to previous comments of concern suggesting you get an electrician in.
I am involving another electrician... As mentioned previously. Existing tails are in plastic conduit embedded in the wall. This is more like passing through the wall in conduit as does the DNO supply.
If you have feedback on the method based on standards, please refer.
 

Reply to SWA For meter tails? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
409
On a new build site how/ why are people getting away with installing meter tails over 3metres in length and behind dot and dabbed walls with no...
Replies
7
Views
2K
Just wanted to know which people use. My case. Client converting attached garage into new rooms. Consumer Unit has to move to accomodate this...
Replies
7
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
751
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock