Sure thing, what I meant was that is that one doesn't want 400V coils and control circuits even within a panel, because 400V is harder to switch with small relays and control devices.
Discuss Swimming Pool Starter Help! in the UK Electrical Forum area at ElectriciansForums.net
Sure thing, what I meant was that is that one doesn't want 400V coils and control circuits even within a panel, because 400V is harder to switch with small relays and control devices.
What is operating the 400Volt coil, are dry contacts on the 230 timer, somehow integrated into the 400 Volt control circuit, dangerous and I believe does not comply to BS 7671, cant give you the reg number if there is one, it was/is something in the back of my mind that is reminding me. Imagine the problems of a 230 V timer with NO/NC dry contacts, with a possible 400V sitting on them, not nice.On a lot of contactors there is a switch that sets the contactor to stay off in the event of a power failure or restart automatically.
Not sure how 230v will operate the 400v coil though!
Also the UV’s must turn off if the pump stops. They will burn out otherwise.
Where abouts are you?
Do you know the reg number Rob out of interest?Once external controls are introduced. Anything above a 230v control circuit is currently forbidden. It's not just preference, it's regulations.
Thanks Rob Will take a lookSection 9 BS60204
Still come across plenty control panels with 400v control circuits but anything controlling remotely with 400v is definitely a no no.Section 9 also covers this. Any more than 2 control devices and it needs a dedicated isolating transformer or psu.
Can't get much in the way of a control system with that. Hence the only 400v control you really see now a days is the dol in a box with a stop and start button. Even then these usually aren't wired control. Simply pushing the contactor in manually, then hitting the trip on the OL to stop.
Still come across plenty control panels with 400v control circuits but anything controlling remotely with 400v is definitely a no no.
Are you suggesting that you fit a device that will trip in the event of a fault, only to reset it's self before the fault has been identified and rectified, seems to defeat the point of a Safety device don't you think?Why not a self resetting RCBO?
Thanks for that RichSelf resetting RCBOs monitor the circuit and will only reset if the fault has cleared quickly, they are intended to avoid the nuisance of short duration intermittent faults. If the fault is significant then the RCBO will not reset.
I'm thinking now that 240v was operating the contactor and caused it eventually to weld closed due to arcing.