Hi and thanks in advance.
I have been called to a job to look at a faulty starter for a swimming pool.
The starter apparently has never worked and swimming company has agreed to pay for it to be fixed ( there electrician has had 2 goes already).
The starter is supposed to be wired so that if there is a power cut the pump automatically restarts, also it is controlled by a 240v timer which also turns on 2 uv lights.
The starter at the moment never turns off by the timer and the reason for this I noticed straight away is that starter is a 415coil being controlled by a 240v timer.
The main trouble I've got is does anybody know if there is a starter with 240v coil and n/c contractor so after power cut it automatically restarts. Existing starter is Schneider LM35P714.Thanks again.
 
Hi and thanks in advance.
I have been called to a job to look at a faulty starter for a swimming pool.
The starter apparently has never worked and swimming company has agreed to pay for it to be fixed ( there electrician has had 2 goes already).
The starter is supposed to be wired so that if there is a power cut the pump automatically restarts, also it is controlled by a 240v timer which also turns on 2 uv lights.
The starter at the moment never turns off by the timer and the reason for this I noticed straight away is that starter is a 415coil being controlled by a 240v timer.
The main trouble I've got is does anybody know if there is a starter with 240v coil and n/c contractor so after power cut it automatically restarts. Existing starter is Schneider LM35P714.Thanks again.
Nothing wrong with a 240v control circuit controlling a 415v starter coil, you could control the starter with whatever voltage you want.
The 240v timer could be switching some contacts which form part of the 415v coil circuit, check that you have volts at the coil when you are supposed to, or it could be fail safe whereby the 414v coil is de-energised when the timer is in operation, if that is the case check that the coil loose voltage at that point.
 
Last edited:
Before this thread gallops off , could you carefully and with a some more description set out the conditions for which the starter contacts are to be closed and opened? In the form:

The starter is to close/open if or when:

1. The timer demands 'close' or 'open';
2.....
3.....
4.....
 
Sorry can you explain! How can 240v pull in a 415v coil on the contactor. I have experience with contactors, but not a great deal with motor starters. Also can you explain why pump is constantly running, appears to be N/C as timer isn't switching the starter, however didn't test across the contactor, [aern't starters n/o contactors] Thank you
 
I have been told the timer controlls starter to pump and uv lights so if they are away on holiday and have power cut the pool doesn't go go green.
The timer controlls the uv lights however doesn't affect the starter, it is just running 24/7. I was presuming the contactor would be N/C and timer would open it so if there is a power cut the motor automatically restarts when power comes back on. I could rewire differently if anyone has any ideas. Thanks
 
Sorry can you explain! How can 240v pull in a 415v coil on the contactor. I have experience with contactors, but not a great deal with motor starters. Also can you explain why pump is constantly running, appears to be N/C as timer isn't switching the starter, however didn't test across the contactor, [aern't starters n/o contactors] Thank you
The 240v control circuit, and the coil arrangement are, or could be two separate circuits, the coil is fed from 1 phase to whatever devices are in the system, and returns via the coil via another phase, the 240 v timer could be operating a set of contacts in one of these devices. You can even operate the coil from a DC source to eliminate chatter on the magnetic faces of the contactor, your choices are almost limitless, could be the timer is faulty, but check out the control circuit, are there any sump pumps, limit switches etc involved? before spending cash on something that is OK. Sounds like from post 5 that the 415v coil should loose it's voltage when the timer operates, when you ask why the motor is running constantly.
 
Gradually coming back to me after some years, in the place I worked, the reason why the 415v coil was / was switched from another source was a safety issue. The powers that be sensibly imo didn't like the idea of a 415v control circuit, dodging about all over the shop, so in many cases we used a 240v, 12v, 24v or a DC source for the control circuit.
Imagine if you can the 3 phases to the starter and a supply from say L1 via a fuse, mcb wired through the overloads etc of the starter, then the coil back to the say L2 hence a 415 v coil would be needed.
Within that control circuit there could be other factors that are needed to switch the motor on and off examples sump pumps, limit switches etc, and in your case a timer, don't want to run 415 to these units for safety reasons so the designers have used 240v as a control source. Sorry for the ramble, it's difficult to explain in writing, I believe that this description can go a long way in explaining to someone, who may not have had very much experience of Motor control circuits, the limitless avenues you can take when wiring remote control stations using lower voltages, ( by remote I mean some distance from the actual machine) hope this helps, take some pain killers with you because some electricians, even experienced ones, just can't get their heads around this method, it just clicked with me when I first came across it many moons ago.
 
No at the moment it runs 24/7 and they don't want it to. They just want it all to automatically restart after power cut to stop pool going green. Thanks
 
No at the moment it runs 24/7 and they don't want it to. They just want it all to automatically restart after power cut to stop pool going green. Thanks
Sounds bizarre as the circulating pump should be running to keep the water clean and maybe off at night only.
 
Just to clarify, what's the supply to this pool equipment? Single or three phase?
Just to clarify, what's the supply to this pool equipment? Single or three phase?
I would imagine it's 3 phase as his initial post mentioned the coil voltage as 415v that's not to say the pump is though.
 
Sorry , just got in from work..
I live in Worcestershire for anybody who would like too know.
I installed all the supplies for pool last September ready for the pool guys (see 1st picture). I got called back last week to see if I could sort why circulating pump isn't turning off as pool electricians had had no success.
They have wired as in my crude diagram.
Also I have downloaded picture of there starter (3 phase in and out L from time clock to A2 and N from timeclock to 96 on overload).
What I believe they want to happen is for pump and uv lights to go of at night, however if there is a power cut they want it all to automatically restart. Thanks
 
Pool plant room.

20170510_100927_HDR.jpg
 

Reply to Swimming Pool Starter Help! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'd like to find a timer switch, in a style that looks alright next to decora light switches, to control a bathroom fan. The bathroom fan...
Replies
1
Views
909
Hi, I hope that someone here might be able to put my mind at rest. I have an engineering mind and a reasonable understanding of electical work...
Replies
13
Views
2K
Hi all looking for some helpful advice I'm an Aussie so go easy on me, I have a good mechanical engineering head but first time plumbing and...
Replies
32
Views
2K
Need some help please. Got a brain teaser for my first post. My pool pump motor cratered over 4th of July. It was working fine and started to...
Replies
13
Views
2K
Hi there Complete novice electrical wise. I am refurbishing an old 1950s Injection Moulding machine and looking to replace the Power Timer...
Replies
55
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock