Discuss Switch fuse for tt submain in the UK Electrical Forum area at ElectriciansForums.net

Bellendian

-
Arms
Reaction score
311
Hi,

My solution in this scenario has always been to get a Lewden switch fuse unit, and replace the 100A main switch with a wylex s-type RCD to achieve earth fault protection.
With this new requirement in the 18th, am I no longer going to be able to do this?
If not, does anyone know of an off the peg solution?

Cheers
 
I understand your thinking, but lets look again at the question, Switch fuse for a TT submain? Based on your question I would say any 2 pole if single phase or 3 pole if 3 phase, would you like to re submit your question?
 
I understand your thinking, but lets look again at the question, Switch fuse for a TT submain? Based on your question I would say any 2 pole if single phase or 3 pole if 3 phase, would you like to re submit your question?
Wouldn't that be a four pole for three phase?
 
Wouldn't that be a four pole for three phase?
No never be able to split the Neutral on three phase lol, an example, if a 4 pole contactor fails, and it has been known, you co
Wouldn't that be a four pole for three phase?
If it has a Neutral yes, many machines have not though
 
No never be able to split the Neutral on three phase lol, an example, if a 4 pole contactor fails, and it has been known, you co

If it has a Neutral yes, many machines have not though
As this is for a distribution circuit on a TT system then four pole would comply whereas a three pole wouldn't as we should isolate all live conductors on a TT system.

Ideally all machines should be shut down and all loads should be removed before disconnecting the supply however I would guess this is domestic so a bit of a mute point.

Haven't seen many decent size machines in a domestic setting unless she's been single for a while...
 
I think the OP is talking about installing the Lewden RCD into a Wylex enclosure.
Which would mean the type testing would be invalid and the unit would no longer comply with the required standard.
 
I think the OP is talking about installing the Lewden RCD into a Wylex enclosure.
Which would mean the type testing would be invalid and the unit would no longer comply with the required standard.

Na hes on about fitting a lewden off the shelf switch fuse and putting a wylex typeS rcd in it.... Which he doesnt need to do as lewden make a typeS rcd, perhaps he just didnt know
 
Yep spot on suffolk. Just got to persuade wholesalers to stock the Lewden RCD now. Should do, there are loads of TT supplies round here so its not like I'm the only one thats going to need it...
Cheers
 

Reply to Switch fuse for tt submain in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
758
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock