Could somebody please clarify the difference between tables 4.1.2a & b. It appears to me that the difference is in types of circuit breakers - B or C depending upon max test loop impedance. Is this correct and which measurement do they mean by test loop impedance?
 
basically, a type C requires double the Amps of a type B to trip within the specified times, so the max. Zs is halved.
 
A circuit breaker will disconnect within 0.1 sec whenever the fault current is equal or greater than the upper limit of their instantaneous tripping band.
For Type B devices this is 5 × In.
For Type C devices this is 10 × In.
The magnitude of the fault current is dictated by the impedance of the fault path which can be measured by an earth fault loop impedance tester. The lower the impedance the higher the fault current and as Type C devices require higher current for any given time the maximum required Zs is lower.
 
Could somebody please clarify the difference between tables 4.1.2a & b. It appears to me that the difference is in types of circuit breakers - B or C depending upon max test loop impedance. Is this correct and which measurement do they mean by test loop impedance?

Why are you asking the question? College work?
 

Reply to Table 4.1.2a/b in Electricians Guide in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Replies
4
Views
740
Hi , Could someone answer the following for me? i don't have reg book handy and when i google i'm getting mixed answers. 1. maximum...
Replies
2
Views
434
OLDBOY
O
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
1K
Hi, I am currently studying to become an electrician and keep seeing this question (normally different values) and I am not sure how to work this...
Replies
14
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock