Discuss Tails inside consumer unit bare copper, not terminated correctly - C1 or C2 ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Unless the barriers and front cover are off, or the copper is out and exposed going into the tails gland I'd C2 myself, purely because it drives the requirement to fix, that said a few seconds to chop and re-terminate and no code at all, depends how you see it.
 
If you C1 exposed copper then potentially every pendant would be a C1

At worst a poorly stripped conductor leaving too much bare wire showing is a C2 as an untrained person fiddling inside the enclosuer could touch the bare wires. Which then questions why is an untrained person fiddling with the wiring in the first place

For me C1 should only be used for really serious things like a bare wire exposed so anyone can touch it. If that wire is inside a box then its much less of an issue
 
He’s not waiting for an answer. WE are waiting for a photo.

There are various degrees of “bare copper showing” that determines whether a C3, 2 or 1
Funny you say that , I worked with a sparks who every time he made off tails he stripped way too much insulation and often left about an inch of bare copper wire poking out the terminal...
Did my head in but he was about 15 years my senior and had done it this way for donkeys years so wasn't going to change his ways...
He is exact same on sockets , switches and JBs he would trim off way to much insulation leaving a solid inch or more of bare wire
 
If it’s just a few mm showing at the terminals, then that’s C3. Improvement.
It’s more likely someone can touch the terminal screw with a fingertip if they really tried.

If bare copper can be accidentally brushed against, when not trying…. That’s C2. As another fault needs to make it a C1…. Such as no front panel, or missing blanks from the front panel.

A C1 would be live copper floating about in free air, likely to be accidentally touched.
 
If you start coding bits of bare copper within the consumer unit where do you stop, do you end up coding sockets and switches that are showing a bit of copper or how about the brown junction boxes with their exposed brass terminals once the lid is off and all generally need a tool to access the areas of concern, it then begs the question should ceiling roses have a key / tool removable cover instead of the current twist off cover because it is too easy to access live terminals
I would suspect there are more items posing a greater danger than this on most installations, it seems now that some doing EICR's don't feel they have completed it correctly unless they hit that pinacle of a C1 on the report, but a few C2's can usually be a substiute for the upset
 

Reply to Tails inside consumer unit bare copper, not terminated correctly - C1 or C2 ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I'm getting conflicting stories about this, I wonder if someone could put this to bed once and for all. I'm replacing a consumer unit in the...
Replies
15
Views
4K
Hi guys, I hope you're all doing ok in this heat!! I have recently carried out an EICR on a domestic property where it failed miserably. The...
Replies
6
Views
6K
...and why would I want to do that ? Well, I'm faced with a real botch job of a consumer unit. Essentially this is a "new" consumer unit only put...
Replies
21
Views
9K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
It's been asked a thousand times I know, but nothing quite matches what I have to work with. Ok, it's a 1950's ish house, 2 bed terrace, so very...
Replies
11
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock