I thought I'd mention a 3 phase fault I had recently for the benefit of a lot of guys on here who are learning or are not familiar with working on 3 phase systems.
See if you can work out the fault. ( if you know it please give the guys a chance to try and work it out first.......ta).

The factory where I work has its own 500kva transformer.
Built in the early 60's this supplied both the factory and the remote office block.
I recently had the DNO run a 3 phase/N SWA cable into the office block so I now have 2 separate supplies.
I then installed a 3 phase board and ran several single phase sub mains to various c/units around the office block.
From the main board I then ran a 3 phase 'dedicated supply' to the server room for the IT dept ( this is the only 3 phase board in the building apart from the incomer).

I was called to the IT dept because the main server had 'crashed'. UPS had kicked in but lots of things not working.
Main thing I noticed on my way there was ALL the power and lighting in the offices was still on.

Anyway...........work this out if you can:)
Testing the 3 phase D/B in the server room gave me these results.

L1-N = 230v.
L2-N =230v.
L3-N =230v.
L1-E = 230v.
L2-E = 230v.
L3-E = 230v.
N-E = 0v.
L1-L2 = 432v.
L1-L3 = 432v.
L2-L3 = 0v.

What fault could cause this, bearing in mind, ALL power and lighting was still on !

I'll wait and see if there's much interest before giving any clues if their needed but I'm sure many have come across this problem on here just thought it would be good to share with others that haven't.
 
2013-02-10T22-55-02_0.jpg
Found this in my mates bathroom ceiling.
The cieling is a flat roof with approx 100m space above the plasterboard , which is also PACKED with insulation.
 
was it one phase blown and then back feeds through the neutrals indicting a phase present when testing all phases to earth?
Apologies in advance if this has been brought up earlier but I'm not trolling through god knows how many previous posts:)
I thought I'd mention a 3 phase fault I had recently for the benefit of a lot of guys on here who are learning or are not familiar with working on 3 phase systems.
See if you can work out the fault. ( if you know it please give the guys a chance to try and work it out first.......ta).

The factory where I work has its own 500kva transformer.
Built in the early 60's this supplied both the factory and the remote office block.
I recently had the DNO run a 3 phase/N SWA cable into the office block so I now have 2 separate supplies.
I then installed a 3 phase board and ran several single phase sub mains to various c/units around the office block.
From the main board I then ran a 3 phase 'dedicated supply' to the server room for the IT dept ( this is the only 3 phase board in the building apart from the incomer).

I was called to the IT dept because the main server had 'crashed'. UPS had kicked in but lots of things not working.
Main thing I noticed on my way there was ALL the power and lighting in the offices was still on.

Anyway...........work this out if you can:)
Testing the 3 phase D/B in the server room gave me these results.

L1-N = 230v.
L2-N =230v.
L3-N =230v.
L1-E = 230v.
L2-E = 230v.
L3-E = 230v.
N-E = 0v.
L1-L2 = 432v.
L1-L3 = 432v.
L2-L3 = 0v.

What fault could cause this, bearing in mind, ALL power and lighting was still on !

I'll wait and see if there's much interest before giving any clues if their needed but I'm sure many have come across this problem on here just thought it would be good to share with others that haven't.
 
Re: Tell us about your faults !

My main fault is I get angry with stupid thick customers when they ask questions like how much is it going to cost and how long is it going to take ;)
 
Come on alan dood.....need to know now ....
us thicko's that add extra sockets for grannies extra heater are dumbfounded ...lol

ok.

You were close originally mate so here's one last clue to see if you can fathom it out.
Always better if you work it out yourself:)

The fault caused me to lose a phase.........call it L3.........but all my single phases were testing 230v and non of my circuit breakers on site were tripped?
Twas a head scratcher for a few minutes lol

ok anyone know what the fault was here's your big chance lol
 
Last edited by a moderator:
nope ...still lost :-9

ok mate no interest elsewhere so here goes........one for your fault archives.

The new 3 phase/N feed into my office block was taken from a joint in the street outside which also feeds street lighting/pump house down the road etc etc.

Turns out the cable/joint/termination ( downstream from us) developed an earth fault on L3/blue phase/grey phase whatever you want to call it:).

This earth fault blew the main fuse in their substation but the heat from the blast ( at the location of the fault) 'welded' L2 and L3 together at the same time clearing the earth fault..........if you get my drift ! lol

This meant L1 was still ok and fused.
L2 was still ok and fused.
L3 was now fused to L2 and being fed through L2 back to my main D/B giving me good tests on all single phases.

Moral of the story........if their is one lol
You can have good tests but still be in a fault situation.

Subsidence seemingly causes this problem on underground cables sometimes but not sure how often..........new one on me that's for sure.

Clear as mud mate:)
 
ok mate no interest elsewhere so here goes........one for your fault archives.

The new 3 phase/N feed into my office block was taken from a joint in the street outside which also feeds street lighting/pump house down the road etc etc.

Turns out the cable/joint/termination ( downstream from us) developed an earth fault on L3/blue phase/grey phase whatever you want to call it:).

This earth fault blew the main fuse in their substation but the heat from the blast ( at the location of the fault) 'welded' L2 and L3 together at the same time clearing the earth fault..........if you get my drift ! lol

This meant L1 was still ok and fused.
L2 was still ok and fused.
L3 was now fused to L2 and being fed through L2 back to my main D/B giving me good tests on all single phases.

Moral of the story........if their is one lol
You can have good tests but still be in a fault situation.

Subsidence seemingly causes this problem on underground cables sometimes but not sure how often..........new one on me that's for sure.

Clear as mud mate:)

To be fair that is what I was trying to say that is way you showed 0 volts as they was same phase
 
To be fair that is what I was trying to say that is way you showed 0 volts as they was same phase
quote_icon.png
Originally Posted by Elrick
Are L2 and L3 the same phase



Meaning?
How could this be?



You certainly did mate I was just asking if you knew what fault could have caused it though and the clue was that non of 'my' breakers had tripped.
 
Last edited by a moderator:
Old cable joints cause similar faults, quite common once they are in 30+years.

Hi Rob,
I've seen a few 'strange' faults in my time and for a few moments this one had me bamboozled to say the least.
Then training kicked in...........think easy/think logically.
So I walked down to the main incomer and my new dazzling meter showed L3 was lost lol. (on the incoming side I hasten to add).
Fault finding at it's best.... quick phone call and someone elses problem:)
 
To be fair that is what I was trying to say that is way you showed 0 volts as they was same phase
quote_icon.png
Originally Posted by Elrick
Are L2 and L3 the same phase



Meaning?
How could this be?



You certainly did mate I was just asking if you knew what fault could have caused it though and the clue was that non of 'my' breakers had tripped.

I wouldn't of guessed what it was never came across this one before thanks for sharing got my grey matter going. What tester did you use to confirm it.

Thanks
 
I wouldn't of guessed what it was never came across this one before thanks for sharing got my grey matter going. What tester did you use to confirm it.

Hi mate.
It might help a few to 'show-off' with their fault finding skills if they come across it in the future lol
It was a bit tongue in cheek about mine because our 3 phase meter has 'phase indication' on it and it showed L3 was missing:)
Confirmed it with my Fluke 1653 on the main incomer.
Local DNO guy was blowing 500amp fuses trying to clear the fault ffs !!!
 
Here's a good one: two two-core SWA's of differing csa's and a length of flex feeding some outside lights, connected with connector blocks, and made 'safe' (ish) by covering with silicone sealant, and buried between zero and three inches across a gravel drive! The doubled-back earth wire of the flex is taped to the swa plastic sheath, but the swa's armours are touching, so sort of achieving earth continuity. :D

Oh yes, protected by a 50A MCB. And as far as I can find (so far) no earthing to the installation whatsoever - definitely not PME in the 1930's cast iron head, and no conductor in the board that could end in an earth stake, unless the stake is connected to one of the final circuits somewhere.

DSC06295.jpg
 
Last edited by a moderator:
Same house as above: noticed that every time you shut the front door the lights flicker. Found why, they are using these p1ssy little electronic 5 amp fuses in both lighting circuits which are considerably smaller than their correct BS1361 equivalents.

DSC06301.jpg
 
IMG_1566.jpg

New twin RCD board install, replacing wylex rewireable one.
Energised the board.. trip.
Id tested the whole house prior to the job with not too many faults...
However, it'd had lots of work done to it over the last 20 years.
The main culprit was one of the RFCs. However, there were other circuits which seemed to add to the problem.
Took the RFC in question, split into 2 radials to narrow the fault. Identified the half causing the problem and split that down even more.
Eventually found this in a socket, spurred off the ring. The little nick in the wire was just touching the earth terminal of the socket. Snipped it out and re terminated.. hey presto everything fine..
The annoying thing is it didnt show out on IR test, even when testing just that spur from the other side.
The only explanation I can give is that it must have been a fraction away from the contact, but when energised it was close enough to jump the gap..!!
3 hours of hunting... but got there in the end.
 
Today’s little adventure!

If you have ever wondered how many wires you can squeeze down a 20mm coupling and into a surface mounted double socket box then wonder no more. It’s 12x 2.5mm singles and 1x 2.5mm twin and earth cable. If I had not seen it for myself I wouldn’t have believed it.

Needless to say it’s no longer like that now!
 
Got a pic Kam? sounds like a right squeeze!

Someone took a ring of the ring to another nearby socket and then for good measure added a feed for an extractor fan as well. Unfortunately forgot to take a picture but it took me ages to strip it out. The T&E had a twist in it as it came through the bush. But that is the most 2.5’s I have seen down a 20mm hole. Once saw 23x 1.5mm singles down a 25mm galv. conduit with two 90* bends. But that was a long time ago and it’s still there and working.
 
Customer asked me to look at why a downlight wasn't working. Removed it to change transformer and was astounded to find a 13a plug-in transformer pack into a socket (with no backbox) terminated on the end of the lighting circuit in the ceiling!

Amazed.

20130212_152959_zpse5c08ccf.jpg
 
called to a job where socket in kitchen was not working, i asked client if he has juction box underneath and he said no, i told him there must be junction box under there, anyway long story short, found a junction box with wire bitten by a rat or mouse who probably died, rotted and decomposed.
 
called to a job where socket in kitchen was not working, i asked client if he has juction box underneath and he said no, i told him there must be junction box under there, anyway long story short, found a junction box with wire bitten by a rat or mouse who probably died, rotted and decomposed.
so the socket stopped working when a rat bit the cable did it?
 
eh? so you get called out because of a non functioning socket ,have no sign of the mysterious rodent and end up replacing the consumer unit? :dizzy2:
 
Re: Tell us about your faults !

wall heater.jpg

This is why you don't get builders who are not competent to do your wiring as they leave exposed wiring on a bathroom heater !!!
 
Was a bit puzzled looking into this morning's consumer unit, as there were the same number of green/yellows as there were MCB's. In other words no bonding or main earth conductor. No earth stake to be found, or a cable that could go to a hidden one, and its definitely not this new-fangled PME thing. Soooo, get my spanky new tester out and run a PFC, which turns out worryingly low. Zero amps, in fact! So we seem to have no earth whatsoever. Yikes! Being a conscientious sort of chap I think I'll ignore it and pretend I haven't noticed. ;)
 
I hope your joking?

Also pme isn't new it's been around for years.
No, absolutely no joke about there being no earthing and zero amps PEFC. We are talking to the DNO about (hopefully) PME'ing it, as being an area of solid Guernsey granite an earth stake could be tricky.

Edit: Oh, I think you meant joking about leaving it. Even I'm not that rough!
 

Reply to Tell us about your faults! in the Australia area at ElectriciansForums.net

Similar Threads

I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock