Discuss Terminating SWA into Hager CU in the UK Electrical Forum area at ElectriciansForums.net

Either drill a round hole in another place, there Is plenty of room on those units, or use an adaptable box under the db for the gland and run the cores through that to your db.
 
Good suggestions. Just feels wrong to be having to drill my own holes into the CU. Can't understand why Hager wouldn't include knockouts for SWA given how common the setup is in the UK?

Why does it feel wrong, its a basic task for an electrician.

Hager are fully aware that any competent electrician is capable of drilling whatever holes they need, that is why they have an option with no knockouts.
 
I used to have a qmax cutter that did inch square holes, it got pinched with a load of other kit a good few years ago. Not seen any since!
Edit
I stand corrected!!
 
They make 3 different types of their db 1 with round knock outs 1 with square and 1 with none! I personally prefer the blank one and make the holes exactly where I want them, but most wholesalers seem to keep the square ko version for some reason!
I hate the square ones. I get the RK versions instead where possible. My preference too is for the units without knockouts but it's an uphill struggle to get anyone to stock them.
 
Is it only me that favours the rectangular knockouts then ?
Why do you like that option, for rear entry of many cable with a grommet strip?

I would assume that most would want round hole knock-outs, at least for the top/sides/bottom so glands to seal & support tails and T&E could be used.
[automerge]1595922426[/automerge]
I used to have a qmax cutter that did inch square holes, it got pinched with a load of other kit a good few years ago. Not seen any since!
I got some recently from here:

They stock a few square ones but in the past the likes of RS had a big range for things like IEC sockets, etc. Always a bit expensive compared to the round ones, alas!
 
Why do you like that option, for rear entry of many cable with a grommet strip?

I would assume that most would want round hole knock-outs, at least for the top/sides/bottom so glands to seal & support tails and T&E could be used.

Mostly so I can butt up a 50x100 trunking above or below for final circuit entry. Tails can go up or down through the designated rectangle with a purpose made grommet. They are then secured inside the unit with the tails clamp.
I hardly ever use SWA to supply domestic boards.
 

Reply to Terminating SWA into Hager CU in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys After bit of advice please as we don't do much data normally, tend to sub it out. Had garden building this week which we'd run in SWA...
Replies
9
Views
372
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
Afternoon everyone.. During some testing I have found an IR reading of 0.01MΩ between N-E. This is on a length of SWA buried underground from the...
Replies
17
Views
3K
Hi guys, Can I ask you a DIY question? I'm refurbing a detached garage and adding a garden building. Garage currently has a submain supplied by...
Replies
1
Views
809
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
754

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock