Discuss test rig with fault causing fault elsewhere in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
:confused5: I have been asked to wire up a couple of CU on plug tops on a display for tenants to show how to go about basic fault finding before they send for a call out .
I used 2 wylex boards , one with dual rcd and one with none .
I put a neutral earth fault but that resulted in the plug top supply tripping out before the show CU tripped , so i changed the fault to live earth and still it tripped out the plug top supply .
any ideas on how to contain the fault to my test unit . I knew i should have paid more attention in college about discrimination .
 
Separate the incoming supply from the portable CU test box(es) with a 230V/230V isolation transformer (similar to the more familiar 230v/110V yellow site transformer).
 
Last edited by a moderator:
.......or take a genny with you :walkman:

Pleeeeese don't apply a neutral - earth fault to anything that's plugged into a generator. Many small generators have split windings and with a neutral-earth fault you'll either make the chassis of the generator live (assuming it's not connected to an earth spike) or you blow the hell out of the windings.

I'd suggest rather go with Markiesparkie's isolating transformer idea.
 
Pleeeeese don't apply a neutral - earth fault to anything that's plugged into a generator. Many small generators have split windings and with a neutral-earth fault you'll either make the chassis of the generator live (assuming it's not connected to an earth spike) or you blow the hell out of the windings.

Sorry Marv, was a joke I promise!
 
No probs, especially in the general public forums I thought it was best to clarify in case it was taken as a serious suggestion.
 
To be honest I'd use a 12v battery or 12v pool light transformer and fit some indicator LED's but I'm not sure if the RCD would trip to a leakage fault with an ELV supply.
 
I would see if you can use the transformer from a shaver socket, its cheap and cheerful and wont weigh you down. Do remember that you will only be able to run a very small load, but as you said its a test rig so no need for massive capabilities.
 
Why can't the housing association/council just send people round when tenants have problems. This will encourage idiots to think "Well doing that was perfectly safe so this will be too"
It'll end in tears mark my words :)
 
Basic fault finding should not be encouraged to any incompetent persons let alone a housing association or whoever wanting test rigs made up. All the tennents need to know is how to reset a mcb, RCD or rcbo. If it holds fine if not lift the phone. These people should not be encouraged by anything more.
 
It would seem that some people have got the wrong impression about what the aim of this test rig is about , to clarify , basically want to show the first steps , and the only ones necessary for tenants to put their supply back on in the case of say a lamp causing the rcd to trip out , thats it , no tools involved little brainpower required .
 
You don't need a live rig with faults incorporated to show them that. A simple set of written instructions would do the job.
 

Reply to test rig with fault causing fault elsewhere in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
475
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
872
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock