Discuss Testing 110 Tx in the UK Electrical Forum area at ElectriciansForums.net

i=p/u

-
Arms
Reaction score
801
Anyone test these before and is there anything you know that I don't.

from what I see 110v transformer is supplied from 16A protective device which is a sub main circuit ,Then the 2 x 55v lines are protected by 16A fuses


Q. Do I just cables upto primary side?
 
If it is SELV CT-E remember to test for continuity from centre-tap to earth, and ensure it is earthed when you IR test the primary to earth, in order to prove the insulation of the windings as well as the circuit.
 
As far as I know you test the primary side as submains and then has 2 circuits each at 55v to Earth . 16A fuse testing each line.


wheres the neutral Lol


Ps is there anyway of knowing what overloads are set at on a vsd
 
If it is SELV CT-E remember to test for continuity from centre-tap to earth, and ensure it is earthed when you IR test the primary to earth, in order to prove the insulation of the windings as well as the circuit.

Reduced Low Voltage (RLV) isn't SELV. It exceeds Extra-low voltage.
 
As far as I know you test the primary side as submains and then has 2 circuits each at 55v to Earth . 16A fuse testing each line.


wheres the neutral Lol


Ps is there anyway of knowing what overloads are set at on a vsd

I think it will be a final circuit feeding it rather than a distribution circuit.
 
both lines should be fused on secondary side so we put in as 2 circuits....

i see some dont have the fuses and apparently have thermal cut out
 

Reply to Testing 110 Tx in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
845
Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock