OK, got an extention lead thats shot (not mine) With only a Fluke 1651 NOT a pat tester I have 96 volts between CPC and phase yet an IR test shows >500 M ohms. ? How would you test?
Kind Regards
David
 
Hi

OK, got an extention lead thats shot (not mine) With only a Fluke 1651 NOT a pat tester I have 96 volts between CPC and phase yet an IR test shows >500 M ohms. ? How would you test?
Kind Regards
David
Err, what do you mean by you have 96V between CPC and phase? Under what circumstances?
 
Thanks for the reply TQ ..Under the circumstance that I have an earth fault that I can only find by reading between phase and cpc when pluged into mains OR using a little plug martindale in tester that I only keep for use as a final functional tester. I cant get a fault by IR tests but they must be a breakdown.
 
if there's no continuity between the extension lead conductors, then the fault is probably in the installation you are plugging the lead into.
Perhaps there is something else plugged into the circuit that is providing the 96V between line and earth.
 
Hi Spin, no brought home too and tested on our home supply - same problem. Voltage before lead 241 with lead 126 and between cpc and phase around 95. Its not a problem, the lead looks knackered and its not mine. I just thought that a simple IR test would show breakdown. Otherwise how would you tell?
Regards, David
 
So just by plugging into the mains you are getting a PD between Line/Earth on the lead (with no load) and the socket is fine before hand. Is it moulded at each end?

You'll need to be VERY careful when handling it when plugged in of course ;)

Is it worth spending any time on it, or is this just an education exercise? Check the flex for any external damage first, either brittle outer insulation (sign of over heating) or cuts/nicks. Then it's down to checking the terminations in the plug/socket ends.
 
Thanks again for your reply TQ. Oh yes, purely for educational reasons. I did examine the lead and it has been overloaded at some point in the past. Here is the thing ... customer decided they could not wait for the dishwasher and machine to be connected (im doing a new RFC for the kitchen, new CU and upgrade on the bonding) so ran their old lead from outside the kitchen to these two appliances. I happened to touch the DW and the sink and the potential difference gave me a belt. I know the bonding is good, I know the circuit they ran from is good and tested so after testing all again checked their extention lead and it was shot. (brought home and tested here too - same result) But I'm frustrated that a simple IR test did NOT show a fault 500v gave me >500 Mohms - only the following showed it was faulty:
1. voltage between the lines and CPC
2. Condition of the lead (bumpy)
and 3. a cruddy littly socket tester.

I am going to take the plug and socket off and try direct on the wire when I get back.
Kind Regards, David
 
Last edited:

Reply to Testing an Extention lead in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Long shot but thought I’d try, have a lighting circuit that trips the RCD as soon as the neutral touches the neutral bar for said RCD. Bypass that...
Replies
6
Views
2K
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
Hi Hope anyone can help Can someone give me advice on how to connect up a 3 phase to 13amp adaptor lead for carrying out PAT testing on 3...
Replies
17
Views
2K
I did a VLF and IR test on my 33kv cable and IR resulted between 80 to 100Mega Ohms on all the phases and VLF between 0.270 to 0.470mA is the cable ok
Replies
0
Views
680
Regarding 3 phase IR tests for initial verification, I'm wondering how people actually do it efficiently. GN3 says to IR test between all phase...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock