Discuss Testing an Uninterruptible Power Supply in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Reaction score
15
Hi,
I'm looking for some advice on the results I got from testing a 1000VA UPS in use in a small business. With the permission of the owner I had switched-off and disconnected the PC it was intended to protect.

Firstly, it passed all tests except the differential leakage test. Is it normal for these devices to leak current via the protective conductor?

Secondly, I got a noticeable shock when I removed the mains plug from the socket and inadvertently touched the pins. Is there a legitimate explanation for this?

Thanks in advance.
 
Not sure about the leakage, but the shock may be a result of the rectified mains smoothing capacitors in a switch mode power supply. Should have discharge resistors but if you unplug and touch fast enough they might not have discharged to a safe voltage.
 
Sounds like a switched mode power supply and a bridge rectifier set up. You will get leakage to earth and a belt from the pins sounds like capacitor discharge.

Be very careful testing these type of items as they don't like insulation resistance tests, refer to the manufacturers guidance for testing.

Also I would recommend testing the batteries to ensure they will do their job when required, they need load testing as a shagged battery may well show good voltage but have no capacity for any load.
 

Reply to Testing an Uninterruptible Power Supply in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
465
Hello, I am currently DIY upgrading a caravan with my girlfriend but need some advice. The (very old) 230VAC to 13.8VDC power supply broke down...
Replies
5
Views
1K
I found myself needing to do some emergency plumbing at home this evening. I've got a small guest flat on my property which has been empty for...
Replies
1
Views
458
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Hello, I’ve got an issue driving me crazy and can’t get anyone to figure it out as it’s not their issue. We had a new extension, single rear...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock