Discuss Testing block of flats in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

s6stu

-
Reaction score
1
Hello,

Couple of questions, firstly does each flat require it's own dedicated earth to the main incoming on the ground floor of the property, zs readings are fine with the 10mm 3 core SWA that has been used. (never certed a block of flats before, jus wanted to be 100%)

And, there is a heater in the bathroom that only has it's own pullcord isolator, does this require an FCU outside of the zones?

Thanks in advance
 
I would assume,that one of the cores in the SWA is being used as an earth/bonding conductor?
If so, a separate earth is not required.
How is the heater fed, is it spured off of a circuit, or is it on it's own circuit?
If it's on it's own circuit, then an FCU is not strictly neccessary.
 

Reply to Testing block of flats in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
805
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
851
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
This isn't very electrical, but never mind! I'm adding an extractor fan to a bathroom in a 4th floor flat. The builder has helpfully cored a hole...
Replies
20
Views
2K
Hi, this is a repost of the initial in diy as the only potential diy aspect is the prep ahead of a qualified person attending, this is hopefully...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock